Old 11-18-2012, 07:25 AM   #16
Rewards Points: 1,542
You would not need that many wire nuts in the breaker panel.
For each critical circuit, a pair of wires comes from the transfer switch unit into the panel, one attached directly to the panel breaker for that circuit and the other wire nutted to the circuit conductor that was just taken off of that breaker. If the wires from the transfer switch unit are not long enough then go ahead and mount a junction box just outside the panel to splice on extensions, or, you could replace the wires coming out of the transfer switch unit with new longer wires.
If you take some of the branch circuit cables out of the panel and attach them to the junction box then individual neutrals must continue on into the panel. One ground wire, sized for the largest branch circuit moved to the junction box, connects the new ground bus in the junction box to the ground bus in the panel.
The Following User Says Thank You to AllanJ For This Useful Post:
DanS26 (11-19-2012)
Old 11-18-2012, 07:38 AM   #17
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,974
Originally Posted by tylernt View Post
Once I learned what an interlock was and what it did, I can't imagine why anyone would bother with a piddly little transfer switch.
Especially for a 10kW permanent generator!
Standby automatic generators, like the OP has, REQUIRE piddly little transfer switches.
Old 11-19-2012, 12:59 PM   #18
Rewards Points: 411
Thanks everyone for your advice, especially AllanJ for his advice on the grounding.
Dan
DanS26 is offline   Reply With Quote
Old 12-30-2012, 08:31 PM   #19
Rewards Points: 411
Just wanted to update this thread with the progress on the Junction Box project. I obtained a 8x8x4 Carlon junction box and mounted 22 pass through blocks rated for 30 amps each at 600V. Also mounted a ground bar as required. As you can see I numbered the circuits. Only 1 and 3 are 30 amp, the rest are either 15 or 20 amp.
I mounted the box, which now is ready to make the transition of the critical circuits from the main distribution panel. 11 circuits will be transferred.
Thanks for everyone for your helpful comments.
Old 12-30-2012, 08:37 PM   #20
Special User
Rewards Points: 1,230
Is combustible material like wood allowed in a JB?
The above post is for entertainment purposes only. Its contents may, and probably will, lead to legal liability and damage or loss of property, life, or limb. Use at your own risk.
tylernt is offline   Reply With Quote
Old 12-30-2012, 08:40 PM   #21
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Each one of those metal romex connectors need a bond/ground bushing.
Edit: The ground going to the panel needs to be a #10 minimum.
Old 12-30-2012, 09:21 PM   #22
Rewards Points: 411
If the metal romex connectors are removed then the circuits need to be stapled or secured at least eight inches from the box. Correct? No other strain relief is needed.
The ground is #10.
Old 12-30-2012, 09:27 PM   #23
Rewards Points: 411
I'm willing to remove the wood, but give me a code reference.
Thanks.
Old 12-30-2012, 09:27 PM   #24
Rewards Points: 506
Originally Posted by stickboy1375
I think its a shame you have a 10 kw generator and are only getting 12 circuits out of it...
My house has 2 - 240V circuits which feed a heater rated at 15kw total...the only heat source. Seems to me that 12 circuits from 10kw is doing pretty good.
jlmran is offline   Reply With Quote
Old 12-30-2012, 09:33 PM   #25
" Euro " electrician
frenchelectrican's Avatar
How far is that 8X8 box to the transfer switch or breaker box ?
Merci,
Marc
Old 12-30-2012, 09:35 PM   #26
Rewards Points: 411
Merci,
Marc
Less than four feet, but far enough that I cannot wire the transfer switch directly without a junction box.
Old 12-30-2012, 09:37 PM   #27
k_buz's Avatar
Incorrect. That is for plastic device boxes. They do make plastic snap in romex connectors.
As for the wood mounting, I think that would fail as well. There is no specific code, but I'd be willing to bet the approved method to mount the terminal blocks are on a metal rail that would mounted to the box with screws. Maybe they make a plastic rail for this application so you don't have to bond the mounting rail.
Old 12-30-2012, 09:39 PM   #28
Less than four feet.
Quatre pieds? ( Four feet ? )
Are you aware with conductor derating ?
Merci,
Marc
Old 12-30-2012, 09:39 PM   #29
k_buz's Avatar
If it is more than two feet, you haven't derated the wires. Those #12's are now rated at 10A (assuming 20 conductors in the raceway).
Old 12-30-2012, 09:46 PM   #30
Here the NEC verison of derating listing.,
This will give you a straight answer on that.
Merci,
Marc
The Following User Says Thank You to frenchelectrican For This Useful Post:
k_buz (12-30-2012)
Generator Manual Transfer Switch BJohnston Electrical 1 11-06-2012 03:33 PM
Bypassing transfer switch in RV to backfeed panel chadmw7 Electrical 5 07-28-2012 03:06 PM
Installing a Reliance 31406CRK transfer switch LeeB18509 Electrical 2 03-17-2012 01:22 PM
Generator Transfer Switch Trouble wgramer Electrical 23 11-12-2011 07:23 PM
Custom wiring a generator to a transfer switch robojoe_fl Electrical 4 06-08-2011 12:36 AM