Kitchen GFCI With 12/3 Feed - Electrical - DIY Chatroom Home Improvement Forum
Old 10-22-2010, 08:45 PM   #1
Kitchen GFCI with 12/3 feed
I would like to wire up 2 kitchen counter receptacles that need to be GFCI protected. Will the following wiring method be up to code?
2 - 20A T slot GFCI receptacles.
2 - separate boxes (about 3' from each other)
12/3 wire feeding 1st receptacle
12/2 wire feeding 2nd receptacle off pigtails with neutral and red wire.
2 - 20 breakers, side by side but not tied together.
zapped is offline   Reply With Quote
Old 10-22-2010, 09:03 PM   #2
Rewards Points: 1,440
All okay except:
... The breakers. You need a double wide double breaker (double pole) with the handles tied together.
Old 10-22-2010, 09:05 PM   #3
Rewards Points: 324
handel ties required.you are aware it needs to be a 240v ckt?
oleguy74 is offline   Reply With Quote
Old 10-22-2010, 09:06 PM   #4
Be sure the breaker is positioned in the panel so you measure 240 volts across the two hot terminals.
Old 10-22-2010, 10:11 PM   #5
Are you sure the handles have to be tied? I thought that as long as the 2 hot wires are not terminated in the same box you can use separate breakers? Obviously each hot will be on opposite bus bars for a balanced load.
Old 10-22-2010, 10:16 PM   #6
Rewards Points: 324
code says handel ties.210.4(b).
Old 10-22-2010, 10:45 PM   #7
" Euro " electrician
frenchelectrican's Avatar
Ya in USA or Canada ?? there is diffrence on code to deal with it.
Merci,
Marc
Old 10-22-2010, 10:59 PM   #8
Rewards Points: 324
usa.is this guy in canada?
Old 10-22-2010, 11:02 PM   #9
Hey Oléguy., I will give you a 50/50 split I have a feeling the OP is from Canada due the T-slots recetpale on kitchen circuits which I know not very often used in USA side.
Merci.
Marc
Old 10-22-2010, 11:03 PM   #10
joed's Avatar
Rewards Points: 11,966
You need to post your location. Your rules sound like you might be in Canada. Separate breakers are allowed if you are in Ontario.
The Following User Says Thank You to joed For This Useful Post:
frenchelectrican (10-22-2010)
Old 10-22-2010, 11:08 PM   #11
Yes, I'm from Ontario, Canada.
After more searching I discovered that the 12/3 feed does NOT have to be on a double pole receptacle or have the handles tied.
The 2 single 20 breakers have to be positioned such that there would be 240V between the red and black. The neutral wire in the first receptacle must have a pigtail to allow removal of the receptacle without interrupting the circuit downstream.
This doesn't apply to split receptacles and if both duplex receptacle were in a gang box you may have an issue.
Old 10-22-2010, 11:13 PM   #12
Maybe so but with split receptales IIRC they have to be on 15 amp circuits but Joed will confirm the excat details and make sure you have RCD protection 1 meter from sink but how far out I will let Joed confirm this part due you are in near his area so he will give you a stright answer.
Merci.
Marc
Old 10-22-2010, 11:39 PM   #13
Rewards Points: 324
Merci.
Marc
t-slots 20 amp recps,is all i use on kit ckts.that goes for the gfci outlets too.some aeras that i work in require them for kit ckts.
Old 10-23-2010, 12:05 AM   #14
It's actually not 1m from sink. GFCI receptacles are required for all receptacles within 1.5m (59") of sink, bathtub or washbasin. (Ontario Rules)
They way they keep expanding the GFCI zone, your neighbour will have to protect his plugs from YOUR sink!
Old 10-23-2010, 12:45 AM   #15
jlhaslip's Avatar
Rewards Points: 922
Don't you split the receptacles so that the top and bottom are on different circuits?
Originally Posted by Bud Cline View Post
Go ahead and apply for a variance, those guys at City Hall can use a good laugh.
jlhaslip is offline   Reply With Quote
GFCI Stumper ksqrdks Electrical 2 04-03-2010 07:24 AM
20 amp GFCI breaker pops when pool pump is turned on. jagrunner Electrical 11 03-19-2010 05:31 PM
GFCI between porch receptacles Thurman Electrical 4 08-19-2009 01:40 PM
GFCI plugs in kitchen DeterminedMom Electrical 10 04-23-2009 11:42 PM
Gfci Circuit howard.wheaton Electrical 10 01-29-2009 06:14 PM