Kitchen remodel, how many circuits (20 amp) and to what is common today? Was planning on one for fridge, dishwasher and disposal. Two for outlets on counter tops. One for microwave and igniters for gas stove. Overhead pendant lights on same circuit as dining room light.
Russell is offline   Reply With Quote
Old 07-04-2011, 08:07 PM   #2
Master Electrician
Rewards Points: 3,874
1. Refrigerator 15 or 20 amp.
2. Dishwasher combined with disposal 20 amp.
3.Microwave combined with ignitor 20 amp.
4. Two(2) 20 amp small appliance branch circuits for countertops.
brric is online now   Reply With Quote
Old 07-04-2011, 08:15 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
Agreed.
Suggest balancing the countertop receptacles. Don’t do what they did in my house. Put 1 cntr-top recpt on one circuit, 7 on the other.
Kyle
Old 07-04-2011, 08:42 PM   #4
Rewards Points: 6,652
I have the following:
1 15a for dining & kitchen lights (3 fixtures)
1 20a for baseboard wall outlets for Kitchen & Dining area (6 outlets)
1 15a for Dispoall
1 20a for outlet for Countertop Microwave (GFCI outlet)
1 20a for 2 countertop outlets (GFCI).
Old 07-05-2011, 12:55 AM   #5
" Euro " electrician
frenchelectrican's Avatar
Tyically 4 or more circuit is common with the kitchen area but for small kitchen or bare bone set up 2 circuits { per NEC codé minuim requirement }
My kitchen in Wisconsin have 7 circuits including a 240 volt circuit for tea kettle { just don't start discuss on this part so leave it out }
In France it typically 3 or more circuit depending on size.
Merci,
Marc
Old 07-05-2011, 04:12 AM   #6
Rewards Points: 1,192
If you can, put in plenty.
bobelectric is offline   Reply With Quote
Old 07-06-2011, 07:23 PM   #7
Thanks for the great answers. Will get busy this weekend to get ready for elec, plumbing and gas inspections.
Old 07-09-2011, 12:13 AM   #8
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
Without knowing electrical specs for disposal and D/W, run dedicated circuit for each. Check D/W installation instructions for electrical requirements. Avoid putting disposal and D/W on same circuit. Disposal is a motor.
Dedicated 15 or 20a circuit to frig and M/W. Built-in M/W's do not require GFI protection. Frig does not require GFI either. At least 2 20 amp small appliance circuits to counter top receptacles. All counter top receptacles require GFI protection. No lighting on 20a small appliance branch circuits.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
Old 07-30-2011, 10:53 PM   #9
DIYer
Rewards Points: 262
I am finishing up the wiring in my kitchen remodel and I have a question about this same setup specifically about the last statement regarding adding lights to a small appliance circuit...
I have all of the circuits in place as suggested above. I need to add two pairs of over-bar pendant lights over the bars I'm adding to the kitchen. One pair switched on each of two opposite walls. It seems dumb to add these to the 15A lighting circuit which already has 7 recessed lights, a ceiling fan/light combo, dining room chandelier, plus three outlets in the adjacent family room (end table lamps). I've done the math and even with all the lights on, I'm still okay. The 20A small appliance circuit will power a toaster and a blender a few times per month. Most likely these two appliances will never run at the same time. It just seems silly to have this appliance circuit that is so underutilized.
I have a third 20A circuit (GFCI protected via receptacle) in the kitchen that has two receptacles. Only thing connected will be a 1600W microwave. Can I (should I) put these two sets of switched lights on this circuit instead of the lighting circuit?
mystic_cobra is offline   Reply With Quote
Old 07-31-2011, 08:46 AM   #10
Electrician
SD515's Avatar
Rewards Points: 504
Lighting is not allowed on the small appliance branch circuits. Doesn’t matter how many you have, or how ‘under-utilized’ there are. SABC’s for kitchens can only supply receptacles, and only in the kitchen, dining rooms, pantrys, etc. associated with that kitchen. No other outlets are allowed on them (a receptacle is not an outlet).
Kyle
Old 07-31-2011, 08:50 AM   #11
DIYer
Rewards Points: 262
Thanks for the reply. Now I'm confused. I thought an outlet was the same thing as a receptacle. What's the difference?
receptacle?
outlet?
Old 07-31-2011, 09:16 AM   #12
Electrician
SD515's Avatar
Rewards Points: 504
2008 NEC definitions:
Outlet: A point on the wiring system at which current is taken to supply utilization equipment. Layman’s terms: A point where electricity can be tapped to supply equipment. Junction boxes, switch boxes, light boxes, etc. An outlet box does not necessarily need to have a device installed in/on it.
Receptacle: A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke. Layman’s terms: A device that a cord cap can be plugged into to receive power.
Kyle
Old 07-31-2011, 09:36 AM   #13
DIYer
Rewards Points: 262
Ok, so would it be correct to say, "an outlet is a box in a circuit where a receptacle or switch may be installed".
Would that be correct?
So, what properties define a kitchen SABC. Is it any circuit with receptacles above a kitchen counter? Any circuit with receptacles in a kitchen?
Old 07-31-2011, 09:40 AM   #14
It can only be in the Kitchen & Dining area. Basically where food is prepared & eaten in the home. Of course, most people eat in their living rooms, home offices, outside also. This circuit can not feed other rooms in the home (ie hallway, basement, bedroom, living room, etc.).
Old 07-31-2011, 09:43 AM   #15
Electrician
SD515's Avatar
Rewards Points: 504
receptacle?
Above is a picture of one type of receptacle
outlet?
This is a picture of a receptacle with its cover plate installed. The outlet is what the receptacle is mounted in.
Kyle
The Following User Says Thank You to SD515 For This Useful Post:
jkk (04-20-2016)
Split receptacles, double pole breakers and multiple circuits in a junction box. morganhammer Electrical 6 04-05-2011 04:38 PM
Yet another Kitchen Sub-panel Post...Sorry tpagel Electrical 4 03-19-2011 09:54 PM
short circuit. reset the breaker, but no power bp91708 Electrical 10 03-18-2011 10:07 AM
Kitchen reno, any better suggestions? mgarfield Remodeling 7 01-20-2010 03:37 PM
Kitchen remodel frank551 Electrical 2 11-15-2005 07:13 PM