-   -   Just want to know if I'm correct... (http://www.diychatroom.com/f18/just-want-know-if-im-correct-186708/)
Carnifex 09-08-2013 09:28 PM
I work at a church and we are getting a new high output printer. It requires 208/240. The building is run with 3 phase. I was wondering if I am correct in thinking that a double pole 20 breaker with two hots and a ground(earth) is all that needs to be run. I am not doing the work, just wondering if i'm correct. If i am correct, is it also possible to pick up the ground from a passing outlet? Thanks for your know hows!!!
Speedy Petey 09-08-2013 09:34 PM
If you can pick up a ground from another receptacle is iffy. Depends on the wire size among other things. WHY would you need to consider this if you have having a circuit run? The ground will be run with the circuit.
Carnifex 09-09-2013 12:49 AM
Gahh. I just wanted to know if it was safe. I know who is going to do the wiring and i don't like his work. I know he is going to cut corners to save money(because saving money is more important than doing it right and safely...) and i would prefer to not to die because of shoddy electric work. Thanks for the reply :)
dmxtothemax 09-09-2013 04:28 AM
We cant say for sure if it is safe !
There are many other factors to consider,
Which you have not told us about.
So the safest way is to run the proper size and type
of wire to the panel and tie into the ground bar there.
Also regulations change from place to place.
Speedy Petey 09-09-2013 05:59 AM
This is a freakin' church! If the guys is not qualified/certified then he should not be doing it.
Depending on where the circuit is run it may also need to have redundant grounding since a church by definition is a place of assembly. The wiring rules are much more stringent.
busman 09-09-2013 06:44 AM
Pete,
Could you point me to the redundant ground requirement? Is it new? We are still on the 2008 code.
Thanks,
Mark
md2lgyk 09-09-2013 08:16 AM
Is the person who'll be doing the work a licensed electrician?? If not, I would find someone who is. Preferably someone with 3-phase experience.
Speedy Petey 09-09-2013 03:14 PM
Originally Posted by busman (Post 1239711)
Pete,
Thanks,
Mark
Sorry, my mistake. I was headed out the door this AM.
I was thinking Health Care Facility wiring. That requires redundant grounding.
Places of Assembly require conduit or a wiring method with an insulated ground, such as MC cable.
Still, it sounds like the OP needs to get himself a real electrician.
electures 09-10-2013 06:50 AM
Also keep in mind that all conductors of a circuit shall be in the same cable, conduit or raceway. The ground has to be run with the circuit conductors.
Carnifex 09-10-2013 06:42 PM
Hmmm, well the work is being done tonight. The one whos doing is a licensed electrician. Just not a very good one. I will look at it tomorrow and if it looks like something is amiss i will call someone else that i know who does his work correctly. Thanks for all the replies.
Carnifex 09-11-2013 03:34 PM
Update
Black white and green solid mc run in a commercial building wired with 3 phase? Is that even code approved?
jbfan 09-11-2013 04:23 PM
Originally Posted by Carnifex (Post 1240734)
Update
If he is only using the black and white as hots, and does not need a neutral, it is fine.
Speedy Petey 09-11-2013 05:12 PM
Update
Like JBfan says, if it is for single phase 240v or 120V it is fine. Just because the building has 3-phase does not mean all wiring and circuits are 3-phase.
It's good that he's at least using MC cable.
Carnifex 09-11-2013 05:50 PM
Ok. So the white can be used as a hot. Good to know. The device doesnt need the neutral so just run the black and white to a 240v breaker and the correct style of outlet. Ok makes sense now lol. As you can tell i know next to nothing about commercial/3 phase wiring. I hope to be accepted into a commercial apprenticeship within the next year so I'm sure i'll be learning all this in much greater detail, but I'm impatient and wanted to understand now, so thanks for putting up with my ignorance :)
itsnotrequired 09-12-2013 02:06 PM
Per NEC 200.7, any white-insulated conductor that is not being used as a grounded conductor (neutral) needs to have colored tape or paint or similar at the breaker and receptacle terminals. this is to avoid confusing it with other white conductors in the wiring system that are being used as neutrals.