Just To Double Check (subpanel) - Electrical - DIY Chatroom Home Improvement Forum
Old 11-24-2012, 10:59 AM   #1
just to double check (subpanel)
Have 200 amp service. Installing a subpanel in attached garage. Distance is 35 feet. 17 feet in attic. 60 amp breaker in main box. 100 amp breaker in subpanel(used as disconnect). Running 6-3 romex. Seperate ground and neutral. No ground rod at subpanel. Sound OK? thanks
jhsatt667 is offline   Reply With Quote
Old 11-24-2012, 11:40 AM   #2
Sounds kosher to me
mterry is offline   Reply With Quote
Old 11-24-2012, 05:02 PM   #3
TTW
TTW's Avatar
Looks good to me 6-3 romex - w G should be good up to 80 amps.
TTW is offline   Reply With Quote
Old 11-24-2012, 05:06 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Nope, only good to 55 Amps. Depending on what you are installing in the sub panel, use a 50A breaker.
Old 11-24-2012, 05:32 PM   #5
TTW
TTW's Avatar
55 amps by table 310.15(B)(16) in raceway cable or earth
80 amps by table 310.15(B)(17) free air
I think I used the wrong table. I stand corrected, thank you.
Old 11-24-2012, 06:01 PM   #6
Electrical Contractor
jbfan's Avatar
Rewards Points: 530
Romex is limited to the 60 degree column
jbfan is online now   Reply With Quote
Old 11-24-2012, 06:44 PM   #7
Engineer
Rewards Points: 161
In addition to replacing the 60 amp with a 50 amp, this leads to an interesting question. Can a 100 amp breaker be used in the sub as a disco when the feeder breaker (and wire) is not 100 amp?
diystephen is offline   Reply With Quote
Old 11-24-2012, 06:48 PM   #8
jbfan's Avatar
Rewards Points: 530
Not a problem, and you can use the 60 amp breaker, because there is not a 55 amp breaker.
Old 11-24-2012, 07:13 PM   #9
Engineer
Rewards Points: 161
Thanks for the info, I've always matched the subpanel breaker to the feeder breaker (when they wanted a sub disco.) Do you happen to know the code reference on that one?
Old 11-24-2012, 07:18 PM   #10
jbfan's Avatar
Rewards Points: 530
Somewhere in the office, and football is on.
As long as the wire feeding the panel is properly protected, you can have any size breaker in the panel.
The Following User Says Thank You to jbfan For This Useful Post:
diystephen (11-24-2012)
Old 11-24-2012, 08:11 PM   #11
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
240.4(b) 2008 NEC
408.36 2008 NEC
The Following 2 Users Say Thank You to Stubbie For This Useful Post:
diystephen (11-24-2012), jbfan (11-24-2012)
Wiring a sub panel to another sub panel Uncle Wayne Electrical 25 02-08-2011 09:50 AM
Please double check my tstat wiring firedogut HVAC 1 10-14-2009 04:47 AM
Subpanel for now, convert to 2nd main panel later? abmiller67 Electrical 2 08-27-2009 01:44 PM
Reverse Polarity at the Subpanel adm060306 Electrical 14 07-09-2007 12:58 PM
Subpanel to Shed - Check my plan NateHanson Electrical 9 04-26-2007 09:56 PM