Junction Boxes - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 06-07-2013, 10:22 PM   #16
Rewards Points: 156
Also,do dining room outlets have to remain dedicated ?.
Can you junction off them ?
On the 12guage 20 amp circuit I had 6 outlets and added 5 .
Thanks for the input!
hidden 1 is offline   Reply With Quote
Old 06-08-2013, 05:40 AM   #17
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
13 outlets per 20 amp circuit .... ie ...180va per duplex outlet = 2340 va/2340watts ..
20 amp circuit is 2400 watts >>>>120v x 20amps ( ohms law )
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 06-08-2013, 08:47 AM   #18
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
There is no limit to the number of receptacles on a SABC.
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
stickboy1375 (06-08-2013)
Old 06-08-2013, 09:39 AM   #19
Rewards Points: 516
what did that circuit supply ????
Old 06-08-2013, 10:29 AM   #20
Resi EC
Rewards Points: 252
Originally Posted by Philly Master View Post
if you are adding circuits ... 13 for 20 amp
220.14(I)
220.14 (J) is for dwelling units
Gac66610 is offline   Reply With Quote
Old 06-08-2013, 10:48 AM   #21
Rewards Points: 516
did u actually read that section ??? to see what it is reffering too ??? all the code referenced ???
Old 06-08-2013, 11:34 AM   #22
Resi EC
Rewards Points: 252
220.14 (I) Recepticale outlets. Except as covered in 220.14(J) and (K), recepticale outlets shall be calulated at not less than 180 volt-amperes for each single or for each multiple recepticle on one yoke. ..........
(J) dwelling occupancies
(k) banks and office buildings
what am I missing?
The Following User Says Thank You to Gac66610 For This Useful Post:
MTN REMODEL LLC (06-08-2013)
Old 06-08-2013, 01:46 PM   #23
Rewards Points: 516
220.14 Other Loads All Occupancies. In all occupancies, the minimum load for each outlet for general-use receptacles and outlets not used for general illumination shall not be less than that calculated in 220.14(A) through (L), the loads shown being based on nominal branch-circuit voltages.
I assumed junction box here in this thread to mean outlets ..LOL
220.14(I)
I stated "if you are adding circuits" .. so they would not have been in the original load calulations ...
what am I missing?[/QUOTE]
What point are u trying to make ....since 220.14 starts out saying All occupency's?????
Old 06-08-2013, 02:39 PM   #24
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
I'm not wasting my time arguing with you, but i'll tell you that you are simply wrong again, you can have as many receptacles on a circuit as you want in residential.
The Following 3 Users Say Thank You to stickboy1375 For This Useful Post:
electures (06-08-2013), Jim Port (06-09-2013), MTN REMODEL LLC (06-08-2013)
Old 06-08-2013, 03:12 PM   #25
Rewards Points: 516
We choose not to do it that way ...just to save a buck......you may do as you wish ....
Old 06-08-2013, 03:14 PM   #26
E2 Electrician
Lol, you're spending someone else's money, people don't generally like that fact when you do it for your own this is better mentality.
Old 06-08-2013, 03:35 PM   #27
Resi EC
Rewards Points: 252
I never said I'll do the entire house, normally 8 to 10 openings to a circuit.
My inspectors tell me I "over wire a house".
And yes I have read the articles ....... without skipping the first sentence of 220.14(I)
It may be a local ammendment that requires you to use the 180va per receptacle, even in residential.
Old 06-08-2013, 06:45 PM   #28
Rewards Points: 516
I think we at least agree on that ..lol
Old 06-08-2013, 06:57 PM   #29
Rewards Points: 516
Using the "minimum" calculations on some houses we do.....2500 sq. ft. useable ..would equal 7500 watts ... 4 20 amp circuits .....
Now also we put for argument sake 50 6" cans in, so that would be in excess of 3000 watts ...
Remember it is a minimum guideline ... I see lots of people do all kinda stuff ....so here recommending to a DIY .. I would rather er on the side of better not minimum...just like we do with our customers...
Yes I will be in school next fri .. For CEU .....
Old 06-08-2013, 08:45 PM   #30
Rewards Points: 156
Back to original question...yes it has dining recepticles and a fridge on it .before fridge and outlets its junctioned again to bedroom outlets..is a 70s home also..
Is it required to be on dedicated circuit in dining room 20amp?
Is difference between ceiling and attic for junction boxes? Mallethead Electrical 13 05-06-2013 09:20 PM
grounding metal junction boxes simanco Electrical 3 07-27-2012 06:22 PM
Attic - Replacing electrical - Positioning, how many boxes, checking understandings darlingm Electrical 12 12-05-2011 12:17 AM
Number of junction boxes on a branch circuit j_sun Electrical 5 07-13-2011 10:37 AM
Junction boxes for garage T8 fixtures mazeroth Electrical 13 01-25-2010 10:52 PM