Jumping From Main Panel To Sub-panel - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 09-23-2008, 08:20 AM   #16
Rewards Points: 506
Send a message via AIM to theatretch85
If you look at the ebay listing I posted, it shows the item that you should be looking for, only in a 2 pole variety (the 3 pole would work, but no need to buy 6 of them). This would be the better solution than "splicing" into existing wires. It would essentially be the same thing as splicing the wires, only your making a better tap connection.
Like 220/221 said, you would have to run 3/0 copper from these lugs to your garage. Your existing 125amp sub panel would have to be replaced with a 200 amp panel and it must have a main breaker installed at the new 200 amp panel. This would serve as your disconnect for the garage building. Or you could put in a new 200 amp panel at the garage, and connect the existing 125 amp panel to the new panel as a sub panel. Though it would just be better to replace it with a single panel.
theatretch85 is offline   Reply With Quote
Old 09-23-2008, 12:58 PM   #17
If I can I would like to keep my costs down and keep the current 125A sub-panel and add another 125A panel in the garage and a 125A breaker in the main.
Can I run 2 feeders in the same conduit?
Thanks,
teamjnz
teamjnz is offline   Reply With Quote
Old 09-23-2008, 02:34 PM   #18
Rewards Points: 78
Since we have clarified that the garage is attached to the house and considered one structure, how does art 225.30 apply? Art 225.30 only addresses "More than one building or other structure".
So a circuit for a spa, "for example" that is fed from a service panel feeding a disconnect within the same structure would be a violation?
Old 09-23-2008, 04:56 PM   #19
Electrician
Originally Posted by teamjnz View Post
The garage is attached and as for 2 feeders into 1 structure, I passed my electrical inspection with both feeder and 2 sub-panels. My power company will not bring a 3phase line into a residential building.
Not everyone knows what they are doing. I really dont know what else to tell you.
Can I run 2 feeder threw the same conduit to power 2 different sub-panels? If I remember correctly someone told me awhile ago that you can't. This is the main reason why I was thinking about splicing into the main feeder to the breaker bus. If I can get a 2pole 200A breaker this would solve my problem.
Thanks,
teamjnz
Your house should only have 1 feeder, its bad enough it has two already, and the garage is missing the required disconnect, I bet the house panel does not have one either... Just curious, Did you hire someone to wire the house?
chris75 is offline   Reply With Quote
Old 09-24-2008, 01:03 PM   #20
Yes the 200A house sub-panel has a disconnect in it. The 125A sub-panel has a disconnect too but it is not in the garage, it is in the main panel. Since it has a disconnect the county inspector signed it off, if it was unsafe he won't have.
I am not a contractor and I did wired the house.
Is it safe to run 2 feeders in 1 conduit?
teamjnz
Old 09-24-2008, 04:32 PM   #21
Electrician
It applies because the combo meter/main is a pedestal service, and that itself is a separate structure, if that meter was attached to the building everything would be fine, but its not. so here is the problem, Everything leaving that meter/panel is in fact a feeder and article 225 applies to all those feeders.
Here are the violations I see already existing,
House has two feeders, violation of 225.30.
225.31, no disconnect located for the garage panel.
225.34, garage and house disconnects are not grouped together.
the list goes on.... The OP needs to call an electrician and see what options are available to him, I cant he his entire setup, so I cant really help at this point.
Old 09-24-2008, 04:34 PM   #22
Electrician
teamjnz
Or he was uneducated?
Old 09-24-2008, 04:36 PM   #23
Electrician
Not at all, 225 would not apply in that situation.
Old 09-25-2008, 10:58 AM   #24
Rewards Points: 78
Chris, So the keyword is pedestal? I could not understand your point until you mentioned pedestal twice. Why is a pedestal service considered a structure?
I understand now what you meant. Thanks for sticking with the thread as I have learned something today.........John
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 08:40 PM
Replace main panel or use subpanel? MasterofNone Electrical 8 02-12-2008 01:24 AM
turn main panel into a sub panel? tikicarver Electrical 2 01-24-2008 08:37 AM
Replace main panel? And lots of other ?s Bcoleman6 Electrical 13 01-22-2008 10:40 AM
main lug vs main breaker for sub panel diyll Electrical 1 01-17-2008 09:18 PM