Inter-connected smoke detectors
I want to replace my existing 15 year old smoke detectors. I have 4 detector that are 120 volt with 9V battery backup; they are not interconnected. The existing smokes are wired to 3 different circuits: 2 on a 20 amp circuit that feeds lights & receptacles in the dining room, one each on 15 amp bedroom lighting circuits.
I want to interconnect the new smokes. Here is a reference to the FireX smokes I want to use.
http://www.sentrydetectors.com/firex/manual/4618.pdf
I am aware that usually interconnected smokes use 3 wire cable and use the red wire to make the interconnection. I would prefer not to have to rewire the four locations.
The manual listed above indicates the interconnection can be made using 18 gauge wiring so I think the interconnection signalling is low voltage. I would like to run a single strand of #14 THWN between the existing boxes to make the interconnection. The FireX manual cautions that if different circuits are used to power the smokes, the neutrals originate from the same phase. This will require I rearrange one of the circuits at the breaker panel but is a minor issue.
My question is: Is my plan to run a single THWN wire (no conduit) between the smokes a code compliant method?
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 06-16-2011, 08:34 PM   #2
Rewards Points: 330
has to be in conduit or cable.single wires can't be run like that.
oleguy74 is offline   Reply With Quote
Old 06-16-2011, 08:54 PM   #3
Electrician
SD515's Avatar
Rewards Points: 504
I don’t think so. Fire alarm systems can have some different rules than the norm, but the typical household smoke alarm is not considered to be fire alarm equipment, therefore the special rules of fire alarms don’t apply. Which means the general rules of branch circuits would apply, and those rules wouldn’t allow it.
Also, this is the wording from the firex link you posted….
Connect smoke alarms to a single AC branch circuit. If local codes do not permit, be sure the neutral wire is common to both phases.
I read that to say that the phases share the neutral….an MWBC.
Kyle
Old 06-23-2011, 03:04 PM   #4
A "Handy Husband"
rjniles's Avatar
OP here rehashing an old question.
I hooked up one of the detectors I am planning on using (see original post) with a cord and plug for testing. I used the test button to set off the alarm and used a meter to test the signal on the red wire from the detector. I get 9 VDC.
Does this make any difference to my original thought to use a single #14 THWN wire to interconnect the smokes (without cable or conduit)?
Old 06-23-2011, 04:00 PM   #5
Lic Electrical Inspector
electures's Avatar
Rewards Points: 1,108
All conductors of a circuit shall be contained in the same cable or conduit. You have to run 14/3.
300.3 Conductors.
(A) Single Conductors.
Single conductors specified in Table 310.13(A) shall only be installed where part of a recognized wiring method of Chapter 3. Exception: Individual conductors shall be permitted where installed as separate overhead conductors in accordance with 225.6.
(B) Conductors of the Same Circuit.
All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, trench, cable, or cord, unless otherwise permitted in accordance with 300.3(B)(1) through (B)(4).
All responses based on the 2011 NEC.
If you live in New Jersey click here. All other states click here.
Please check with local, county and state officials as laws may vary.
Sizing motors here. Online motor calculator here. Online calculators here.
electures is offline   Reply With Quote
The Following User Says Thank You to electures For This Useful Post:
rjniles (06-23-2011)
Old 06-23-2011, 06:58 PM   #6
Rewards Points: 1,016
When I did my whole house remodel a couple years ago, I installed battery powered wirelessly communicated smoke alarms. Works well, easy install. Might be an option to consider if allowed in your locale.
____________
Vince
The Following User Says Thank You to vsheetz For This Useful Post:
Old 06-23-2011, 08:17 PM   #7
A "Handy Husband"
rjniles's Avatar
I looked at those but they were a little to rich for my blood $$$)
Old 06-23-2011, 10:30 PM   #8
Depending on the situation by the time you subtract out wiring costs, the delta is not that much.
____________
Vince
Hard wired smoke detectors Gabriel24 Electrical 4 12-01-2010 08:02 AM
Smoke Detectors on Different Circuits Mililani Electrical 13 10-17-2010 06:35 PM
Tying in new 120v smoke detectors in an addition to existing ones... matthewschrag Electrical 1 08-20-2010 10:43 AM
Wiring Smoke Detectors - Has to be straight run? WaldenL Electrical 15 08-30-2009 09:22 AM
Smoke Detectors / CO Detector Bocolo Electrical 9 02-17-2009 05:12 AM