Old 10-23-2012, 05:47 PM   #16
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Originally Posted by Glennsparky View Post
Yes, shut off the main breaker. Do you have a volt meter to confirm the power's off in that box?
Dont you think the fuses are the main? The reason I ask, is because we wouldn't be running the GEC to this point if it in fact was not.
Old 10-23-2012, 05:48 PM   #17
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
If this is your main disconnect (which it appears it is) you will have to have to POCO come out and pull the meter. You will not be able to turn off power to this disco. The line side will remain live.
The Following 3 Users Say Thank You to k_buz For This Useful Post:
Glennsparky (10-23-2012), jrclen (10-25-2012), stickboy1375 (10-23-2012)
Old 10-23-2012, 05:54 PM   #18
Electrician
Rewards Points: 150
Yeah, it looks like a main to me too. But Lemkie said there was another main. So I thought it was worth a shot.
Glennsparky is offline   Reply With Quote
Old 10-23-2012, 05:56 PM   #19
E2 Electrician
The GEC would be run to that disconnect then. just so everyone is on the same page.
Old 10-23-2012, 05:59 PM   #20
Rewards Points: 242
The main box is also a great place to look for more grounding electrode conductors.
Thanks for the help I really appreciate it. I do have a volt meter to confirm that the power's off.
This is the main fuse panel for the whole house. Are you saying there should be more grounding conductors?
Lemkie is offline   Reply With Quote
Old 10-23-2012, 06:02 PM   #21
Rewards Points: 242
Just to clarify this is the one and only panel for the house. The wires in the picture are the main power wires coming from the street. I realize these stay live if the main breaker is switched off. What I didn't know if it the main breaker being off was enough to move the ground wire
Old 10-23-2012, 06:03 PM   #22
Electrician
Rewards Points: 150
The current code calls for more. I don't know what was legal when this was built. Whatever you have may be grandfathered in.
Old 10-23-2012, 06:05 PM   #23
E2 Electrician
Basically you should have two ground rods to supplement the water pipe GEC....
Old 10-23-2012, 06:05 PM   #24
Rewards Points: 242
Based on my research I am short a ground which I understand. I mainly was wondering if the one I have now is ok or not, and whether or not it could easily be moved.
Old 10-23-2012, 06:08 PM   #25
E2 Electrician
First off, the wires they used are not sized properly, what I would do, is buy the correct size wire, buy a lay in lug for the bonding bushing, because you dont have enough lugs in the disconnect to just hit the bonding bushing by itself, exit the disconnect and land the wire on the water pipe entering the building, if you have city water, hit both sides of the water meter... If you so feel desired, you can come off the water pipe with a #6 cu. and hit two ground rods outside.
Old 10-23-2012, 06:08 PM   #26
Electrician
Rewards Points: 150
I would do it. Standing on rubber. With only one hand near the panel at any time.
Old 10-23-2012, 06:16 PM   #27
Rewards Points: 242
I have city water but there isn't a meter so I was planning on hitting it about a foot after it enters the house.
Can this be done with the main wires live? Is there any benefit to shutting the main breaker? Thanks!
Old 10-23-2012, 06:16 PM   #28
Rewards Points: 242
Ya I'm not so sure about this with the way you're describing it.... I really want to come out of this shock free....
Old 10-23-2012, 06:17 PM   #29
E2 Electrician
My personal opinion, no, you should hire someone and have the Power Company shut off the power.
Old 10-23-2012, 06:22 PM   #30
k_buz's Avatar
Seriously? This is what you recommend to an amateur?
The Following User Says Thank You to k_buz For This Useful Post:
jbfan (10-25-2012)
new sub panel BlueBSH Electrical 11 01-22-2012 09:28 AM
New detached garage with sub and ground, house has no ground at panel italie Electrical 9 09-12-2011 03:43 PM
Service panel ground downunder Electrical 13 05-13-2011 05:46 PM
Ground rod or not? brotherman Electrical 30 07-15-2008 05:58 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 12:33 PM