02-04-2009, 12:43 AM
#31
UAW SKILLED TRADES
Installing Service In Shed.
Bob
Look at this diagram this would be a general diagram of a cooking range as an example. Load one needs a neutral for the light at 120 volts. Load 2 is your heating elements at 240 volts...no neutral is needed just 2 hots wires L1 and L2. Look at the two breakers as a double pole breaker connected to opposite legs in your electrical panel.. If I test either L1 or L2 to neutral I get 120 volts. If I test L1 to L2 I get 240 volts. In your case black and white are L1 and L2. black is connected to one terminal of the breaker and white to the other terminal.
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
02-04-2009, 01:01 AM
#32
Originally Posted by Scuba_Dave
Yeah, I just didn't explain it right
But as I understand it I could draw 29.9999a  on each leg without a problem = equal almost 60a at 120v
I know that most people might not balance the load that way
But I use a meter to setup my Christmas display electric
All the Christmas geeks calc in 120v power available
It's just the way I calculate it - since my Christmas display takes 80a @ 120v
And I don't kick out the 60a breaker
So to say I will kick out the breaker the minute I exceed 60a is not quite true. Saying if either leg exceeds 60a is (in my case I have a 60a 240v panel)
FWIW, My holiday light display made it up to about 110-115 amps on a double pole 60 amp breaker with out tripping. Of course that was after I fully balanced the loads out between the legs on 3 panels! Tripped the main breaker a couple times while I was in the process of metering and balancing loads. Clamp meter is definitely your best friend when you are running holiday light displays this big. FYI it was around 37,000 lights.
Just would like to add, the neutral in this setup saw little to almost no current on the sub panel for the lights as it was balanced fairly well. It had to be otherwise i'd be pulling too much on one leg and trip the breaker!
Reason: added last part
02-04-2009, 01:05 AM
#33
i know that you need to have a neutral, so you can get 120vac to run the clock, timer, etc... on an electric stove, so how does it differ for the heater i spoke of?....bob
The heater circuit will measure 120V to ground on each leg and 240V between legs. The heating element uses only the 240volts, it doesn't use the 120V legs individually.
120V circuit = one pole breaker, one hot wire to send the power to the light in "pulses", sixty times a second, and one neutral wire to send it back.
240V circuit = two 120V legs. "A" phase sends power to the heater and it returns on "B" phase, then it flip flops, 60 times a second (alternating current) The electrons are not flowing out of the two legs at the same time, they are alternating back and forth.
120/240 circuit has two hots which can provide for the 240 equipment, and a neutral which provides the return path for the 120V circuits. The 120 stuff would function using the ground as a return path but it is dangerous and not allowed (in most cases)
02-04-2009, 02:07 PM
#34
ok, STUBBIE, thanks for the diagram, it helped alot. i knew how to dio it in my head, but couldnt get it right sometimes, seeing it on paper, so to speak, made it clear. so i need to run two hots from a double poll breaker in the main house panel to the lugs in the sub panel to get 240vac at the sub? what size double poll breaker and wire do i use? i also need to run a neutral and ground from the ground/neutral buss (both on same buss) to the sub, with the neutral going to the neutral buss, and ground to the ground buss. then snap in my branch circuit breakers and wire them in. do i need a main breaker in the sub panel too? i hope i got this right this time! im alittle thick headed sometimes!...bob
02-04-2009, 02:22 PM
#35
Breaker protects the wire. #10 = 30 amp, #8 = 50 amp
Some say yes because it is a separate building. Some say only if there are more than six breakers.
02-04-2009, 03:07 PM
#36
Licensed Electrical Cont.
Originally Posted by 220/221
#8 = 50 amp
Only for conductors in conduit. NM cable would be #8 = 40 amps.
You need a means of disconnect regardless. Doesn't matter if it is six breakers or one main.
One main assures you will always have a main shut-off. With six breakers it is too easy for someone to throw in some twins.
02-04-2009, 05:39 PM
#37
Trying not to confuse the guy.  At this point, this isn't an NM installation.
I agree. Others will argue the point.
02-04-2009, 06:07 PM
#38
There was talk of UF. It may still be a possibility.
I can't see how:
225.31 Disconnecting Means.
Means shall be provided for disconnecting all ungrounded conductors that supply or pass through the building or structure.
02-04-2009, 06:28 PM
#39
Another horrible idea
Underground conduit belong in wire. Even the POCOs here figured that out in the 80's when they had to start going back thru all the neighborhoods replacing parts and pieces. The still use dirct burial triplex but they now pull it thro conduit. Wiring doesn't last forever in most cases, especially underground.
Is #8 UF also 40 amp?
02-04-2009, 06:39 PM
#40
Electrician
340.80
02-04-2009, 06:42 PM
#41
hi,
in the beginning i was going to use uf, but now im going with seperate conductors with ground. i realize that u use #10 for 30amp breaker. i ran new wires from the fuse box (pull type fuse assembly) to the central air conditioning compressor outside the house, which is 240vac, and used #10 wire cause it was on 30amp fuses. the reason i asked about the size of the wire and breaker needed is that someone mentioned a while back, that due to the distance (approximately 150ft) that i may need a heavier gadge wire compensate for voltage drop. its no big deal to put in a main breaker at the sub,right? so i might as well do that and be safe...bob
02-04-2009, 06:51 PM
#42
To stay code compliant, buy a panel that has a main installed in it. It will likely be a 100 amp main.
The main breaker must be fastened (screwed) to the panel. Until a few years ago we could just backfeed a breaker plugged into the bus. Someone decided that that wasn't safe. I don't agree.
02-05-2009, 01:03 AM
#43
UAW SKILLED TRADES
I wish someone could tell me how we got to a 100 amp sub panel with a 30 amp demand load.......  He would probably be fine with a multiwire branch circuit getting two 20 amp circuits out to the shed. At most I would install a 2 space 60 amp sub-panel. He could have 4 ... 120 volt circuits. I'd run #8s
with a #10 ground and protect with a 40 amp breaker. He could use the 6 disconnect rule most likely as from my experience most inspectors allow it. If not he could use a simple ac pullout disconnect configured as service equipment ahead of the 60 amp sub.
Stubbie
02-05-2009, 01:40 AM
#44
I am sure my suggestion is help you.. i think Figure that No. 10-2 with ground wire will provide about 30 amps on a 220/240-volt circuit, No. 8-2 with ground wire will provide about 40 amps on a 220/240-volt circuit, and No. 6-2 with ground about 50 amps on a 220/240-volt circuit.
02-05-2009, 02:23 PM
#45
Hey....it happens
Trying to stay simple and code compliant can sometimes snowball. I haven't seen a 30 or 60 amp main breakered panel.
Although adding a pullout to the system would be legal, it would look like a moron installed it and I doubt it would save any real money. I'm a rebel. I'd back feed a breaker and not lose a minutes sleep.
| Thread Tools |
Search this Thread |
| Display Modes |
Linear Mode