-   -   Installing a recessed light (http://www.diychatroom.com/f18/installing-recessed-light-31834/)
y_wren 11-13-2008 11:05 PM
Is it okay to replace a light on a 12 awg circuit (20 amp breaker) with a recessed light that is marked 14 awg through branch circuit conductors (on the can). If not, can you explain why.
jamiedolan 11-13-2008 11:26 PM
Does it have pig tails that are 14 gage or are the terminals are it marked that it only accepts 14 gage?
Jamie
y_wren 11-13-2008 11:51 PM
Hi,
On the under side of the recessed can is states 'Max. of (4) NO. 14 AWG thought branch circuit conductors 2 in and 2 out suitable for at least 75 degree premitted in junction box.'
Gigs 11-14-2008 04:55 AM
That sounds like a physical fill limit, not anything to do with ampacity.
rgsgww 11-14-2008 08:10 AM
Where will this can be located in the circuit?
y_wren 11-14-2008 09:50 AM
Hi,
The light is in the middle of run. I have not removed the old light yet, but it is also connected to a 3-way switch. So depending on how this way done, it is possible to have 2 - 12-3 coming from the switch and 1 -12-2 leaving which would exceed the capacity of box. (but I might can do a work around if it'sonly a capacity issue).
InPhase277 11-14-2008 10:47 AM
Yes, the 14 gauge limit is the volume capacity of the junction box attached to it. I doubt that the 3-way wiring passes through the lights. If the box is limited to four 14-2's, that seems to indicate a volume of 18 cubic inches or so, not counting the wires to the fixture. This would indicate a maximum of three 12-2's in the box.