Old 08-13-2012, 09:34 PM   #16
Rewards Points: 6,652
BTW, how many amps is the main breaker panel, what was the load calculation that was done before this dream of running a NOC in your house, stated as to the load already. Add to that another 46 amps, you are talking a nice electric bill.
Most homes on average will use anywhere from 4 to 6 amps daily, depending on the size of the home, what the occupants are doing. Average load per hour can range anywhere from 7 to 36 depending on what a person or family is doing (ie watching multiple tvs, home theater on, dryer running, microwave heating up popcorn, or food, dishwasher running, clothes washer, electric stove, etc., hvac).
Before you move a server farm into this house, I would personally like to see posted what your load calculation is on what the current home's main panel was built to handle, due to I doubt that unless it is a 200 amp panel, that it may be able the extra load.
Old 08-13-2012, 09:36 PM   #17
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Most homes on average will use anywhere from 38 to 74 amps daily, depending on the size of the home, what the occupants are doing. Average load per hour can range anywhere from 12 to 26 depending on what a person or family is doing (ie watching multiple tvs, home theater on, dryer running, microwave heating up popcorn, or food, dishwasher running, clothes washer, electric stove, etc., hvac).
Seriously?
Old 08-13-2012, 09:40 PM   #18
Originally Posted by stickboy1375 View Post
Im going with way lower. but just for giggles, intstall the kill a watt meter and see what you are actually dealing with... You could install (3) 20 amp circuits, or (4) 15 amp circuits, both will give you the same amount of wattage, but may better balance the load out.
You are right!
I just checked group 3 with the KILL A WATT and it comes in at 6.6AMP. The HP power calculator had it higher at around 12AMP
Maybe I can get away with just two 20AMP outlets. I will test the other two groups with the KILL A WATT to see what the real world AMP usage is.
Group 3 is:
Top Fan
Switch
Router
Monitor / Keyboard
DL 360 G5
ML 370 G4
HD & Tape backup unit
APC UPS
Mellow is offline   Reply With Quote
Old 08-13-2012, 09:53 PM   #19
It is a 200AMP service (Square D) with one blank slot that I am planing to install double (skiny) 20AMP breakers in. The hot water heater and clothes dryer is gas. There is no central air only a few window units. Some of the breakers go to stuff like the RV outlet that never gets used and add no load. I dout it strongly that I am close to the 200amp capacity.
Old 08-13-2012, 09:54 PM   #20
E2 Electrician
you woundn't be able to afford your electric bill if you were even close to 100 amps... lol... The NEC overkills service requirements.
Old 08-13-2012, 09:59 PM   #21
Then I must be near a 100amp use because I cannot afford it
Yes I see the NEC is a bit heavy handed, probably start up amp usage. I do have the ability to bring the rack up slowly one server at a time to keep the start up load "normal"
Thanks for you help Stickboy!
Old 08-13-2012, 10:04 PM   #22
E2 Electrician
I cant afford mine either, mine is around $330 a month, but I have a lot of items.
Old 08-13-2012, 10:28 PM   #23
OK Group 1 tested. I also brought over one server from group 2 to balance the load better.
Group 2:
4x DL360 G4
1x DL360 G4p
Total amp usage after start up is 10AMP
The HP power calculator has this at 18.5 (with the extra server)
I wonder if the AMP's will go up significantly when the servers start rendering? I will do that test tomorrow.
So between group 1 and group 3 I am at 16.6AMP that would be fine on one 20AMP breaker so I think I will easily be able to do it with just 2x dedicated 20AMP circuits and not three as originally thought.
Group 3 is:
4x DL360 G4p
I will test it next but I expect it to only be around 8AMP's.
Old 08-13-2012, 10:30 PM   #24
E2 Electrician
Group 2:
4x DL360 G4
1x DL360 G4p
Group 3 is:
4x DL360 G4p
Correct, they will rise a bit during heavy usage, but dont expect much more...
Old 08-14-2012, 12:49 AM   #25
If you're going to cool the room with A/C, which you should, watch your humidity levels. If the humity gets too low in the room, electrostatic discharge becomes a risk and you might accidentally damage some of the components of your servers.
gookinp07 is offline   Reply With Quote
The Following User Says Thank You to gookinp07 For This Useful Post:
Mellow (08-14-2012)
Old 08-14-2012, 01:01 AM   #26
Thanks for the tip.
I will keep an eye on it. The APC UPS has two external sensors that monitor both temperature and humidity. I placed one in the room and the other in the rack.
Old 08-14-2012, 01:05 AM   #27
JOATMON
ddawg16's Avatar
Rewards Points: 1,116
I got tired of waiting for the HP page to load.....
If your using the power requirements based on the wattage if the power supply...then the esitmate is always going to be a lot higher than actual.
I noticed you made a reference to UPS.....did you factor in the losses from the UPS?
Something to consider....up your UPS to one that runs off 240Vac....APC makes models specifically made for things like servers....once you make this jump, you can get all sorts of power....
Old 08-14-2012, 01:27 AM   #28
This is my UPS: http://www.apc.com/resource/include/...=documentation
I only keep the two main servers (exchange / DHCP / file ) on it and naturally the backup, switch and router. It will keep all that up for about 12min. The other servers are not mission critical (just render machines) so no UPS for them.
Adding 2 outlets in the middle of a series of outlets - wiring question Evan55 Electrical 7 06-14-2012 10:43 AM
New Home: 2 Prong Outlets & K&T Wiring (Maybe) weekley14 Electrical 4 05-29-2012 08:56 AM
DNS Server Question SPS-1 PC Repairs & Upgrades 5 01-21-2012 12:49 PM
Installing GFI outlets tsperry Electrical 1 04-27-2011 12:25 PM
Need to rewire outlets and lights..HELP suboveryde Electrical 1 11-02-2010 07:19 PM