Installing Nema Locking Plug Outlet. Need Advice. - Electrical - DIY Chatroom Home Improvement Forum
Old 10-17-2008, 03:08 PM   #1
installing nema locking plug outlet. need advice.
i have to pull wire and install a receptical for a vaccum heat press in my shop.
these are the requirements: 4-wire, single phase NEMA L14-20 plug 230 VAC, 15 Amps -
and here's a link to the actual equipment: http://www.bhphotovideo.com/c/produc...specifications
i was an assistant electrician for a year, but i'm a novice. what supplies do i need? i figure i need a double 230 breaker..don't know what wire...and a L14-20 outlet.
can anyone help me get started?
andy
SPIT is offline   Reply With Quote
Old 10-17-2008, 03:21 PM   #2
DIY'r
ScottR's Avatar
You would need 12-3 wire/cable, a double pole 20A breaker, and as you said, an L14-20 receptacle, and a box for it. Plus any cable clamps, etc needed for your type of cable/conduit.
If this is going in a residential shop, you can probably use NM cable -- commercial you'd probably need to run MC cable or conduit.
I'm an amateur, BTW -- there are plenty of really knowledgeable pro electricians on this site, so you might want to wait to hear from one of them too before you go shopping.
ScottR is offline   Reply With Quote
Old 10-17-2008, 03:21 PM   #3
Electrician's Helper
Pudge565's Avatar
Rewards Points: 150
Send a message via AIM to Pudge565
If it is straight 220, 230, 240 whichever you want to call it you only need 2 wire with ground. Since it is only 15 amps you only need 14 gauge wire but I would go with 12 wire on a 20 amp breaker just to be safe.
Pudge565 is offline   Reply With Quote
Old 10-17-2008, 03:26 PM   #4
DIY'r
ScottR's Avatar
Originally Posted by bhpphotovideo.com
Requirements: 4-wire, single phase NEMA L14-20 plug 230 VAC, 15 Amps
According to the requirements on the site, it's 4-wire. So 2 hots, neutral, and a ground. The electronics may require 120V. (Hence 12-3 cable).
Old 10-17-2008, 04:35 PM   #5
Read the details. It call for a four wire plug, so you know it's a four wire run. How about 12 gauge on a 15A breaker?
jerryh3 is offline   Reply With Quote
Old 10-17-2008, 04:38 PM   #6
DIY'r
ScottR's Avatar
Not sure if this will be running for >3 hours.. If it's a continuous load it would have to be on an OCPD rated for 125% of load, therefore 20A breaker... no?
Old 10-17-2008, 04:58 PM   #7
If you put it that way, then yes. The requirements are written funny. It says it's a 15A load, but requires a 15A circuit. If this thing is meant to run continuously, then it should be spec'ed to a 20A circuit.
Old 10-17-2008, 05:53 PM   #8
it will run continuously for most applications for just a few minutes. i don't think any more than 10minutes. i want to use the vaccum press eventually for rubber vaccuum clamp sheeting for wood veneering which could require leaving it on overnight.
Old 10-17-2008, 06:24 PM   #9
Electrician
SD515's Avatar
Rewards Points: 504
NEMA L14-20=20 amp receptacle. The specs call for a 15A circuit, but the receptacle is rated 20A. I'd run 12 AWG on a 2P-20A brkr. Also note that the specs say " ** International (export) model electrical specifications"...so are these specs for the U.S. or outside the U.S.??
Kyle
Old 10-17-2008, 06:31 PM   #10
so is the 4 wire pretty common...can i find it in a role of the flex conduit?
Old 10-17-2008, 06:39 PM   #11
Electrician
SD515's Avatar
Rewards Points: 504
If you mean 12/3 w/gnd MC cable, yes, it's common. Commonaly a 25 foot roll is the smallest you'll find on a shelf in a big-box store, but not always. Some may sell it by the foot also.
Kyle
Old 10-17-2008, 08:59 PM   #12
DIY'r
ScottR's Avatar
I think that ** refers to where it says 3-wire.
Originally Posted by Website
230 VAC, 15 Amps; Requirements: 4-wire, single phase NEMA L14-20 plug 230 VAC, 15 Amps - **3-wire
Old 10-18-2008, 02:11 AM   #13
When you run romex down a wall exposed, it must be protected by conduit. Be sure to use proper bushings if you do. (This is a short run down a wall, no romex in conduit in other situations)
rgsgww is offline   Reply With Quote
Old 10-18-2008, 05:21 AM   #14
Licensed Electrician
Scott is right on the money here (although it should be a 12/3 with ground cable) . A continuous load is considered to be 3+ hours and should not load the circuit to more than 80% of it's ampacity: on a 20 amp circuit that would be 16 amps. This is to prevent the build-up of heat in the circuit during the extended duration. If you're unsure of whether it will be a continuous load or not, I would err on the side of safety and wire it as a continuous load.
Tuckahoe Sparkplug is offline   Reply With Quote
Old 10-18-2008, 04:39 PM   #15
Electrician
SD515's Avatar
Rewards Points: 504
I think you're right Scott...my bad.
Kyle
Wiring a new outlet advice kennykenny Electrical 19 08-29-2008 10:54 AM
Installing dryer outlet in laundry room ManMythLegend Electrical 11 07-13-2008 10:36 AM
Is it a hazard to plug a surge protector into an ungrounded GFI outlet? CuriousWithQuestions Electrical 7 02-01-2008 09:04 PM
Help on installing a 220v outlet BobRankin Electrical 24 10-23-2007 05:32 PM
European 220V outlet "Schuko" estophile Electrical 6 08-27-2005 08:45 AM