Old 08-24-2010, 10:13 PM   #1
installing ground rod
I ran wire from my house to a new shed that will have a 100 amp breaker box in it, do I need to install a ground rod? If so how do I do it?
rlaurent79 is offline   Reply With Quote
Old 08-24-2010, 10:14 PM   #2
Inspector/Instructor
codeone's Avatar
Yes., Large Hammer.
codeone is offline   Reply With Quote
Old 08-24-2010, 10:16 PM   #3
codeone's Avatar
The current codes require 4 wire to be run to the sub panel and drive ground rod(s) at he seperate structure. The key being driven ground rods.
Old 08-24-2010, 10:19 PM   #4
" Euro " electrician
frenchelectrican's Avatar
Oui you will have to drive two ground rods on detached buildings there is no extempts on that at all on subpanels set up.
And you have to keep the netural and ground seperated at subpanel { make sure you do not use the bonding screw at all !! }
Merci.
Marc
Old 08-24-2010, 10:30 PM   #5
codeone's Avatar
Merci.
Marc
Thanks Marc,
Very important part!
Old 08-25-2010, 12:55 AM   #6
What is the bonding screw?
Old 08-25-2010, 01:25 AM   #7
Rewards Points: 1,016
Bonding screw ties the nuetral and ground bars together in a panel - in a subpanel you do not tie them together because there should be only one neutral path in the system (in the main panel).
2 grounds rods - I drive them with a hammer drill.
Old 08-25-2010, 07:43 AM   #8
I=E/R
a7ecorsair's Avatar
Panels contain two bars, one for connecting the white grounded conductor (Neutral) and the other for connecting the bare grounding conductor.
In a sub-panel, these two bars cannot be connected but in a main panel they are. The panel case has to be bonded (grounded) too, so depending on how your panel is set up will determine what has to be done.
I will use an example that I'm currently working with. It is a GE Power Mark panel.
This panel comes with the two bars installed and mounted in stand-offs; they are not fastened directly to the case. These two bars are also connected together with a removable link.
To use this as a main panel, I only have to install a screw, the bonding screw, to connect the panel to the ground bar so the case is grounded.
To use this as a sub-panel, I have to remove the link that connects the two bars. One bar will then be connected as the neutral, and the other the ground bar. The panel case is bonded to the ground bar with the bonding screw and all the ground wires have to be connected to this bar.
All the white wires have to be connected to the neutral bar.
a7ecorsair is offline   Reply With Quote
Old 08-25-2010, 01:17 PM   #9
DIY'er
jamiedolan's Avatar
Rewards Points: 1,024
Funny, my video is the top you tube result for driving grounding rod
Use a helper if you can to hold the rod still and hope you done have rocks in your soil that are as bad as mine.
Jamie
jamiedolan is offline   Reply With Quote
installing new dedicated circuit - neutral bus full 7green Electrical 12 05-03-2011 02:32 PM
sub panel ground and neutral daddyrabbit Electrical 3 01-29-2010 07:49 AM
Installing timer switch, no ground wire in switch box diydan Electrical 2 05-25-2009 08:51 PM
Grounding VS Bonding BillyD Electrical 24 06-22-2008 01:14 PM
Older home -- Open Ground issues, please help Toyz Electrical 1 06-15-2008 09:41 AM