Old 07-16-2012, 06:39 PM   #1
Live and let live
Installing Conditioning disconnect
I am installing an Air Conditioner 60 amp disconnect on the side of the house and running it up and into the attic in conduit and then over approximately 50 feet and down to a 50 amp feeder breaker with no conduit. What is the correct way to wire this.
I would like to make one unbroken wire run.
rrodgers is offline   Reply With Quote
Old 07-16-2012, 06:45 PM   #2
E2 Electrician
stickboy1375's Avatar
You would have to use UF type wire, but seriously. what ton AC unit do you have, 50 amp feeder is ridiculously high... Do you have the unit on site? What does the nameplate actually require? MAX Breaker, and MIN Amperage is what you are looking for.
Old 07-16-2012, 06:54 PM   #3
Live and let live
I am going to have a 4 ton unit installed and it seems pretty high to me too. I am going by what the installers requirements are. I do not have the equipment on site, it will be installed in a few weeks. It will be an American Standard and from the specs i found, minimum amps are 28 and protection required 50 amp.
Old 07-16-2012, 06:57 PM   #4
E2 Electrician
I figure 7-8 amps per ton, but that's usually on the high end.... can you wait till the unit is in place before wiring? Im guessing no on this...
Some installers don't know how to size a AC unit, Im guessing you could easily run #10 wire and be safe.... but you should ask for the model number or the actual nameplate to save yourself some money in wire...
And don't be scared to install a larger size breaker than wire size you ran... just follow the name plate.
The Following User Says Thank You to stickboy1375 For This Useful Post:
rrodgers (07-16-2012)
Old 07-16-2012, 07:00 PM   #5
Semi-Pro Electro-Geek
I assume the 50A rating is the MAXIMUM overcurrent protection, not a minimum requirement. Since the rated current is 28A, you can use #10 wire and any breaker from 30-50A. 30A may trip on startup. 40A would probably do fine. 50A is overkill, but allowed. Your wire size only needs to match the rated current (28A) not the breaker rating.
mpoulton is offline   Reply With Quote
Old 07-16-2012, 07:07 PM   #6
E2 Electrician
The reason you can use a much larger breaker on AC systems is because the over current protection is actually built into the hermetically sealed motor, so in essence, the breaker you install is only providing ground fault and short circuit protection, this way the motor will start with its high current start up.
Yoyizit (07-16-2012)
Old 07-16-2012, 07:19 PM   #7
Live and let live
So UF 8/3 with a 10AWG ground is the best choice for this job?
Old 07-16-2012, 07:22 PM   #8
It was a dark and stormy
Yoyizit's Avatar
Yeah, at a COP of 3.4 and @240v this would be 4.3 A/ton.
Old 07-16-2012, 07:26 PM   #9
E2 Electrician
You certainly won't have an issue running #8 UF, that's for sure.
Old 07-16-2012, 07:28 PM   #10
E2 Electrician
Yes, but you have to figure in 125%, and with my numbers, I'm confident on running a wire and not being undersized with equipment unseen.
Old 07-16-2012, 07:31 PM   #11
Live and let live
Thanks a million, I have a call in now to the tech to get the nameplate data.
Old 07-16-2012, 07:35 PM   #12
E2 Electrician
Lets us know the actual nameplate, you want the MINIMUM circuit ampacity, and the MAXIMUM breaker size.... these numbers are the important ones.
Old 07-16-2012, 09:07 PM   #13
Electrical Contractor
kbsparky's Avatar
Nope. You are planning to install an oversized cable, with a neutral conductor that will not be needed. #8/3 uf cable is a large, flat assembly and will be unwieldy when trying to install it. It's also very expensive and a waste of money and resources.
All you need is a #10/2 cable for this equipment. The minimum circuit ampacity rating already allows for the 125% requirements of the NEC.
-KB
Old 07-16-2012, 09:19 PM   #14
E2 Electrician
We don't know the actual nameplate, Im not so sure I would say #10 is sufficient, but probably is... and I completely missed the 8-3, not 8-2 part.
Old 07-16-2012, 09:44 PM   #15
kbsparky's Avatar
We don't know the actual nameplate...
From the OP:
... from the specs i found, minimum amps are 28 and protection required 50 amp.
Taking this at face value, #10 is quite sufficient for the load ...
-KB
Tags
attic wiring, thhn
Air Cond Unit disconnect switch? rcassidy Electrical 4 04-16-2012 06:07 PM
Installing new doors, floors, and trim. toobhed Windows and Doors 5 03-16-2012 03:21 PM
furnace and air conditioning package price MichaelV HVAC 3 12-02-2008 09:19 AM
Main disconnect box before service panel Cellomangler Electrical 4 02-04-2008 08:43 AM
fused disconnect and/or GFCI ? pchiz Electrical 8 12-21-2007 11:02 AM