-   -   Installing a ceramic kiln (http://www.diychatroom.com/f18/installing-ceramic-kiln-179201/)
jahertz 05-10-2013 05:20 AM
2 Attachment(s)
Attachment 70628
Attachment 70629
Hello, I am trying to find some information to help me install a ceramic kiln. The above images are the information plate and plug for the Evenheat kiln.
I understand that there needs to be a 240v breaker installed (I have room for it on the panel and I have replaced breakers in the past). I have read that I have to have kiln be 80% of the Amperage rating of said breaker. So I would need a 60A rated breaker.
Now I what I am having trouble with is finding an outlet/receptacle that 1) matches the factory plug. 2) matches the 240v 60A
Please illuminate me with the solution that I'm sure is right in front of me.
kbsparky 05-10-2013 05:26 AM
That's a typical welder plug on the kiln. It's rated at 50 Amps, 240 Volts.
NEMA 6-50.
You can readily get a receptacle that matches it at most electrical suppliers. Some home-horror stores may also have these in stock.
You can feed it with #8 THHN conductors installed in conduit, or #6/2 romex cable.
You don't need anything larger than a 50 Amp breaker.
Speedy Petey 05-10-2013 06:03 AM
Sorry KB, I disagree.
I do a lot of kilns, and IMO this unit requires hard wiring with a local disconnect since 60A devices are basically non-existent locally and stupidly expensive.
http://www.amazon.com/Leviton-9460-R.../dp/B00271GXA6
https://www.platt.com/platt-electric...px?zpid=161882
It is a continuous load over 50A so a 50A circuit and receptacle are not appropriate. 6/2NM is just slightly under the limit for ampacity, but I would not worry about it.
Someone just put that welder cable on it because it was easy. That does not make it appropriate.
usair 05-10-2013 06:20 AM
what makes you think the cord was added and not factory installed?
md2lgyk 05-10-2013 06:36 AM
Have you tried to find an instruction manual for this kiln? Must be a big one; my wife has a small one that needs only a 30A breaker.
usair 05-10-2013 06:58 AM
The photo shows 45 amp on the rating plate.
md2lgyk 05-10-2013 07:08 AM
Yes, I saw that. By "big" I meant physical size.
r_marcinko 05-10-2013 08:00 AM
I'm a tile manufacturer and have over 25 electric kilns. Have that kiln hard wired and forget the plug. Over time the plastic around those prongs WILL melt.
mpoulton 05-10-2013 01:32 PM
I second the recommendation to hard-wire this kiln. I have one slightly larger than that, and I just moved it to my new house. Will be wiring it this weekend. The kiln will draw full rated power for many hours continuously, and in a hot environment. The 80% derating factor really needs to be applied, and kilns tend to melt plugs even when they don't exceed the ratings. I'd use #6 wire in flexible conduit and be done with it.
Speedy Petey 05-10-2013 02:07 PM
Kiln's do not typically come with a cord attached, especially medium to bigger ones like this.
Speedy Petey 05-10-2013 02:08 PM
The instructions will say to wire it according to local and national codes.
usair 05-10-2013 04:07 PM
I just ran a circuit for an Evolution 2318 that came with a nema 6-50p and it s draw was 37A.
mpoulton 05-10-2013 04:09 PM
We all stand corrected!
http://evenheat-kiln.com/ceramic/rmseries/rm2-2329/
That's the current model of this kiln - the only difference appears to be updated controls. This kiln comes with that cord, and is intended to be plugged into a NEMA 6-50R receptacle, presumably on a 50A breaker since that's the largest allowed for the receptacle. I'd still take the cord off and hard-wire it, but using the cord would be perfectly acceptable.
Speedy Petey 05-10-2013 04:25 PM
37 x 125% = 46.25
Speedy Petey 05-10-2013 04:26 PM
I guess so huh?
It amazes me how a presumably listed product can be so blatantly non-code-complaint. :icon_rolleyes: