Install Of New Switch Box Next To Old - Electrical - DIY Chatroom Home Improvement Forum
Old 01-03-2012, 01:21 PM   #1
Install of new switch box next to old
Hi All,
New to this forum. Looking for advice on whether I have made big mistake. Installing LED undercabinet lighting in kitchen. Installed a switched outlet off of a under utilized outlet circuit. I installed the box for the switch right next to the existing outlet which I had tapped into. Everything went fine except when I went to install the faceplate and realized that 2 gang does not mean 2 boxes next to each other. So now there is 3/8 inch mis match to fit the plate over both the outlet and the switch.
Is this major mistake? Any options for non-standard faceplate dimensions?
Thank you for any help.
cmuzzy is offline   Reply With Quote
Old 01-03-2012, 01:23 PM   #2
Licensed electrician
Rewards Points: 1,892
The bigger mistake is adding the lighting to the small appliance branch circuit. This is prohibited be the electrical code.
cmuzzy (01-03-2012)
Old 01-03-2012, 02:11 PM   #3
Julius793's Avatar
Yes a violation but here is what I would do take both boxes out put in a double gang box and then try to find a big plate to hopefully cover the extra space.
Electricity will kill you if you give it a chance
Julius793 is offline   Reply With Quote
Old 01-03-2012, 06:11 PM   #4
So covering up a big hole allows the poster to ignore the code issue?
Old 01-03-2012, 06:22 PM   #5
Rewards Points: 582
lets try it again WHAT YOUR ABOUT TO DO IS AGAINST CODE......
The Following User Says Thank You to ben's plumbing For This Useful Post:
Jim Port (01-03-2012)
Old 01-03-2012, 10:01 PM   #6
Thanks for feedback. Sorry for basic question - is code violation because kitchen counter top outlets can not have any lights on them? I am trying to understand code. This is the 3rd circuit for outlets along the counter top. Is code to have 2 with no lighting? This third circuit has refrigerator outlet and one other unused outlet. Fridge is 6.5A full load and LED lighting will be less than 1A so I don't think a load problem but I do not want to violate code. There is an outlet on another circuit out of kitchen on the other side of the wall which I think I could tie into.
Old 01-04-2012, 01:26 AM   #7
Julius793's Avatar
Yes nothing but receptacles even it there are more circuits than required by code. Still I wouldn't worry because it's not dangerous or anything.
Old 01-04-2012, 01:58 AM   #8
Not a Noob or Boob
The work around is a switched outlet, plugging the under cabinet lighting into it. I usually run an outlet into a cabinet that is switched and use it for the lighting. Perfectly legal and to code.
Rob1975 is offline   Reply With Quote
Old 01-04-2012, 07:06 AM   #9
If the receptacles did not serve the countertop this would be an option. It sounds to me the OP has tapped a circuit serving the countertop and it still would be prohibited.
OP, here is the code:
(B) Small Appliances.
(1) Receptacle Outlets Served.
In the kitchen, pantry, breakfast room, dining room, or
similar area of a dwellingunit, the two or more 20-ampere
small-appliance branchcircuits required by 210.11(C)(1) shall
serve all wall and floor receptacle outlets covered by 210.52(A),
all countertop outlets covered by 210.52(C), and receptacle outlets for
refrigeration equipment.
Exception No. 1: In addition to the required receptacles
specified by 210.52, switched receptacles supplied from a
general-purpose branch circuit as defined in 210.70(A)(1),
Exception No. 1, shall be permitted.
Exception No. 2: The receptacle outlet for refrigeration
equipment shall be permitted to be supplied from an individual
branch circuit rated 15 amperes or greater.
(2) No Other Outlets.
The two or more small-appliance
branch circuits specified in 210.52(B)(1) shall have no other outlets.
Exception No. 1: A receptacle installed solely for the electrical
supply to and support of an electric clock in any of
the rooms specified in 210.52(B)(1).
Exception No. 2: Receptacles installed to provide power
for supplemental equipment and lighting on gas-fired ranges,
ovens, or counter-mounted cooking units.
cmuzzy (02-02-2012)
Old 01-04-2012, 09:43 AM   #10
Not a Noob or Boob
breakfast room, dining room, or similar area of a dwelling
unit, the two or more 20-ampere small-appliance branch
circuits required by 210.11(C)(1) shall serve all wall and
fl
oor receptacle outlets covered by 210.52(A), all countertop
[ROP 2206]
speci
other outlets.
the rooms speci
fired
ranges, ovens, or counter-mounted cooking units.
Sorry, I wasn't specific enough. Forget I am not on CT. You would need a circuit that is not servicing the counter top. Thanks Jim!
The Following User Says Thank You to Rob1975 For This Useful Post:
cmuzzy (02-02-2012)
how to install a photoelectric switch DougManNC Electrical 12 06-10-2011 05:58 PM
3-way light with a twist Jeepsail Electrical 14 05-18-2010 01:24 AM
Trying to install Leviton In-Wall LCD timer switch Proulx06 Electrical 36 11-05-2009 10:15 PM
What switch to install between panel and 220 volt heater Rogers Guitar Electrical 4 01-21-2009 06:08 PM