New house and garage. Garage has 1 switch, 1 light bulb and 2 outlets. Is there anyway I can run my 12-2 from a spare breaker in the main box out to the garage and into a new breaker box?? How would I hook the 12-2 into the new box in the garage??
Thanx for all helpful replies guys n gals!!!
JSJ is offline   Reply With Quote
Old 04-02-2013, 12:40 PM   #2
Electrical Contractor
jbfan's Avatar
Rewards Points: 534
Attached or detached?
jbfan is online now   Reply With Quote
Old 04-02-2013, 12:48 PM   #3
JSJ
Detached
Old 04-02-2013, 12:54 PM   #4
JSJ
To go into a little more detail, the previous owner ran overhead wires from a back door light to the garage. Flip the back porch light on and you get power in the garage!!! Not sure what all is on that circuit, but it comes from the laundry room area. Would rather run a whole new circuit out there from a spare breaker in the main box in the house.
Old 04-02-2013, 12:58 PM   #5
Rewards Points: 2,516
Do you mean a junction box in the garage or an actual breaker panel?
hammerlane is offline   Reply With Quote
Old 04-02-2013, 01:07 PM   #6
JSJ
an actual breaker box. so basically if it tripped it would trip in the garage and not all the way up in the house.
Old 04-02-2013, 01:14 PM   #7
Rewards Points: 214
it would have to be a sub panel. Best left for the pros due to your limited knowledge of not even knowing a sub panel would be needed.
rosem637 is offline   Reply With Quote
Old 04-02-2013, 01:27 PM   #8
JSJ
a sub panel would be wired in from the main in-feed lines going to the main box, right?? I just want to know if I can wire from an actual circuit breaker in the main box to feed a whole new breaker box.
Old 04-02-2013, 01:46 PM   #9
Rewards Points: 150
The main "in-feed lines" feed the main box only. A subpanel would be fed off a breaker in the main box. I wouldn't run 20A... I'd go 30A / 10ga to a subpanel in a garage. But I agree w the others... if you're going to do this, you really should start w a lot of reading as you sound pretty new to wiring. There are lots of things to be concerned with. What kind of cable to bury. How deep. How to transition from buried to the structure. Do you need a ground rod at a detached garage. Whether or not to bond the neutral. Get a book on the subject and start reading. Pull a permit. It won't cost much and they'll check the important stuff for you. If you do your homework ahead of time and come ready w good questions, most inspectors are happy to answer them.
SquishyBall is offline   Reply With Quote
The Following User Says Thank You to SquishyBall For This Useful Post:
JSJ (04-02-2013)
Old 04-02-2013, 02:01 PM   #10
JSJ
so basically I can run a 30A 2pole breaker in my main, run 12-3 wire, wired black and red hot from main breaker to feed sub panel, common from main common bus to common bus in new breaker box, and run a ground from new panel common bus to an earth ground.
Old 04-02-2013, 02:09 PM   #11
Rewards Points: 150
If you run a 30A 2 pole breaker then you need at least 10-3 wire, not 12-3.
But the grounding question is one for your locality (or the pros out here). I don't know if 10-3 plus ground tying the ground to the main box ground is appropriate or Earth ground instead. I've only installed a sub within a dwelling, in which case the ground comes from the main box as well.
JSJ (04-02-2013)
Old 04-02-2013, 02:30 PM   #12
JSJ
10-3, gotcha!!!
I wont run grnd from main box out to the garage, but earth ground my com bus in my new box.
Old 04-02-2013, 02:47 PM   #13
seansy59's Avatar
Rewards Points: 258
10-3, gotcha!!!
Lets see if you really want to do this:
You must run a ground wire from your main panel. In your case, 4 separate wires. Hot 1, Hot 2, neutral, and ground.
You need at least 1 8ft ground rod fed with #6 solid or stranded wire. Some areas require 2 located 6ft apart, especially if you have water/or gas running to your garage from the house.
Make sure ground bar and neutral bar are separate in the sub panel! They CANNOT be tied together.
Running Methods:
You need 4 10 gauge THWN/THHN wires in conduit, at least 18" deep. Protect by 30a DP breaker.
Or you can run 10/3 (with ground) UF cable 24" deep, and sleeve it with conduit where it goes above ground. Protected by 30a DP breaker.
You cannot run more than 1 circuit out to a detached building.
You can run a MWBC (Multi Wire Branch Circuit) which would effectively give you 2 20 amp circuits if you run 12/3 (with ground) cable. Protected by 20a DP breaker. This eliminates the need for a ground rod and sub panel.
Under no circumstance can you run what is known as "Romex" or "NM Cable" underground or anywhere outside. You can use it in the garage under some circumstances depending on how you run it and what your local code is. Even in conduit outside it is considered wet location. Big no-no.
seansy59 is offline   Reply With Quote
The Following 3 Users Say Thank You to seansy59 For This Useful Post:
jbfan (04-02-2013), JSJ (04-03-2013), SquishyBall (04-02-2013)
Old 04-02-2013, 02:50 PM   #14
Master Electrician
Rewards Points: 3,916
10-3, gotcha!!!
You must run a grounding conductor to the garage, four wires, hot, hot, neutral, ground.
brric is online now   Reply With Quote
Old 04-03-2013, 07:33 AM   #15
JSJ
Thanx seansy59, the check is in the mail buddy!!!lol Thanx for taking the time to give me a such a great and detailed answer. I didn't know I couldn't run romex underground even if it was in conduit. I also thought I could get away with earth grnding my com bus in the new garage box.
proper way to install TWO breaker boxes. Cinci Joe Electrical 1 04-27-2011 09:18 PM
Heat Pump trips breaker gt1935 HVAC 2 03-26-2011 10:06 PM
240V/30A outlet install with 1/2" 2 pole breaker neal0713 Electrical 5 02-03-2011 10:35 AM
GFCI Breaker Tripping Spa Light eaposition Electrical 21 09-08-2010 09:57 PM
Breaker problem jdhar Electrical 11 06-10-2009 01:18 AM