inspector says, can't paint wire?
My friend is selling his house and the inspector is giving him grief about romex he painted to match the room. he claims the wire must "breath"...
Now I have seen countless numbers of houses with painted romex, I don't know if its upto code or not, what do you think?
elementx440 is offline   Reply With Quote
Old 03-16-2007, 06:35 PM   #2
joed's Avatar
Rewards Points: 13,276
Is this a home inspector or an electrical inspector? I bet it's a home inspector. Ask him to quote a code reference number.
Old 03-16-2007, 06:38 PM   #3
Rewards Points: 150
I'm pretty sure it's the general home inspector... not electrical.
Old 03-16-2007, 07:11 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,968
More mumbo jumbo from wannabe professionals.
Breath??? I would LOVE to laugh right in that guy's face!
Old 03-16-2007, 07:19 PM   #5
Rewards Points: 150
yeah, breath? doesn't copper + air = oxidation????
the only thing I could THINK he means is that the paint might react with the insulation?
Will it be anywhere in code that you CAN paint wire? Where can I look at this?
Old 03-16-2007, 07:44 PM   #6
Lic. Builder/GC/Remodeler
AtlanticWBConst.'s Avatar
That's a new one. Unfortunately our electrician is on vacation this week in Florida and not answering phone calls.
I understand the concept about wiring insulation & heat...but I can't seem to find anything about this being a valid point, and in all these years in the building industry...I have never heard of this. I even checked on the General cable Industries website and found no references:
http://www.generalcable.com/GeneralCable/
If this is fact...then it's real piece of valuable trivia knowledge.....
- Build Well -
Old 03-16-2007, 07:47 PM   #7
Electrician
Rewards Points: 800
I know of no code against painting wire.
My concern would be have romex exposed. Where is this romex that it is painted? Romex is for use in concealed walls.
darren is offline   Reply With Quote
Old 03-16-2007, 07:48 PM   #8
Ok,....thanks Speedy P....You just answered this wackiness and confirmed my original suspicions...
- Build Well -
Old 03-16-2007, 07:49 PM   #9
It's right up there with making sure you have the "Plywood stretcher".....on every job site...
- Build Well -
Old 03-16-2007, 08:17 PM   #10
Not true Darren. NM cabe CAN most certainly be used exposed.
334.15 Exposed Work
In exposed work, except as provided in 300.11(A), cable shall be installed as specified in 334.15(A) through (C).
(A) To Follow Surface Cable shall closely follow the surface of the building finish or of running boards.
(B) Protection from Physical Damage Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC rigid nonmetallic conduit, or other approved means extending at least 150 mm (6 in.) above the floor.
Where Type NMC cable is installed in shallow chases in masonry, concrete, or adobe, the cable shall be protected against nails or screws by a steel plate at least 1.59 mm ( 1/ 16 in.) thick and covered with plaster, adobe, or similar finish.
(C) In Unfinished Basements Where cable is run at angles with joists in unfinished basements, it shall be permissible to secure cables not smaller than two 6 AWG or three 8 AWG conductors directly to the lower edges of the joists. Smaller cables shall be run either through bored holes in joists or on running boards. NM cable used on a wall of an unfinished basement shall be permitted to be installed in a listed conduit or tubing. Conduit or tubing shall utilize a nonmetallic bushing or adapter at the point the cable enters the raceway. Metal conduit and tubings and metal outlet boxes shall be grounded.
Old 03-17-2007, 07:18 AM   #11
he could be siting 110.12 (C), but he would be wrong, as the outer insulation is not internal to the equipment.
Master Electrician
jwhite is offline   Reply With Quote
Old 03-17-2007, 08:25 PM   #12
Petey,you must have had some of the same experiences with HI's that I have.
halibrand is offline   Reply With Quote
Old 03-18-2007, 10:12 AM   #13
Diesel Fitter
Rewards Points: 150
this is what I looked like when I first heard this one
this was the inspector
this was my painter
this was his helper
mikemy6 is offline   Reply With Quote
Old 03-18-2007, 10:55 AM   #14
Diesel Fitter
Rewards Points: 150
Hey Atlantic
I must of had 1 of your ex guys helping me on a job cause when I told him I duct stretcher in my truck he said (Yeah real funny) so I let him bang on that thing while I ate my lunch. Being the nice guy I am ( or maybe it was the cursing he was doing) I got it for him showed him how to use it.
Paint coming off of siding ciera Painting 5 07-01-2007 05:22 PM
Old house, new light fixture, too many wires Persephonee Electrical 3 01-15-2007 08:58 AM
my painter did not fallow the contract jaskoo Painting 17 11-19-2006 01:21 PM
exterior paint question sherlock Painting 5 07-05-2006 07:31 AM