Inside The Breaker Pannel - Electrical - DIY Chatroom Home Improvement Forum
Old 02-07-2004, 11:03 PM   #1
Guest
Guest
Posts: n/a
Inside the breaker pannel
Are grd and nuetral connected to each other in the breaker pannel?
Old 02-08-2004, 03:26 AM   #2
No. Should be a lug bar for each. I've seen some where the grounds all tie into one thing.. but not too often.
hatchet is offline   Reply With Quote
Old 02-08-2004, 01:03 PM   #3
Contractor
Old way, yes. New way, no. :confused:
Teetorbilt is offline   Reply With Quote
Old 02-08-2004, 10:09 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,824
In the main panel in the house the neutrals and grounds go to the same bar(s). The neutral bar is bonded to the panel case by either a strap or screw.
After the first overcurrent device(main breaker) the grounds and neutrals must be kept isolated. As in the case of a sub-panel.
Separate structures off the same service have different rules.
Speedy Petey is online now   Reply With Quote
Old 02-08-2004, 10:15 PM   #5
Question on wiring a ceiling fixture
I am installing a ceiling fixture and the box in the ceiling has 4 wires, a white, a black and a red and a ground. The light has two wall switches to control it. My fixture only has three wires, a white and a black and a ground.
When installing it, where do I connect the red wire?
Cregan is offline   Reply With Quote
Old 02-08-2004, 10:23 PM   #6
Cregan, I answered on your other post so we don't hijack this thread.
Old 02-17-2004, 09:44 PM   #7
Guest
Guest
Posts: n/a
Listen to Speedy.
Old 12-19-2006, 10:16 PM   #8
Rewards Points: 33
So in my new Square D QO 200a 40 circuit panels, there are 4 bars on the neutral circuit. So what you're saying is just connect all the grounds and neutrals to those bars anywhere?
I was originally under the impression that the grounds and neutrals were on seperate bars and those bars were connected or "bonded".
One more question -- I'm installing two 200a QO panels. Do I run two SE's from the meter and treat each of these panels as a main panel?
Thanks,
David
Patriot_RAM is offline   Reply With Quote
Old 12-20-2006, 12:09 PM   #9
joed's Avatar
Rewards Points: 11,560
If this panel is your main panel and first place of disconnect after the meter then yes you can connect the grounds and neutrals in the same bus bars. Only one neutral per screw is permitted.
Old 12-26-2006, 09:14 PM   #10
remodeling pro
Just leave the red wire capped off like it was . It is fairly common to wire this way to ceiling boxes. The red wire would become a switch leg to control the fan separate from the lights if a ceiling fan was hung there.
I assummed the red wire was not connected originally or you would have known what it was connected to.
troubleseeker is offline   Reply With Quote
Old 12-26-2006, 09:23 PM   #11
Seeker, you do realize you are replying to an almost 3 year old post, which was also originally a duplicate, don't you?
Old 12-29-2006, 10:50 PM   #12
Rewards Points: 33
Look at the bright side -- at least the original question was eventually answered.
I have one more question. If these two 200a panels are both wired directly from the meter base, do you bond the neutral/ground as if they are both main panels, or do you treat one as a sub.
I think I know the answer, but want to be sure. Also -- what meter base do you guys recommend for this application?
Thanks,
David
Old 12-29-2006, 11:14 PM   #13
The two 200 amp panels are BOTH treated as main panels. Both bonded, and "grounded".
A standard 320 amp meter base is typically used. You can get double lugs for both the line and load sides if you are also doing a parallel lateral.
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 06:55 AM
Zinsco breaker boxes and breakers. evosounds Electrical 3 07-29-2007 07:08 PM
Outdoor breaker panel questions lhoney2 Electrical 12 07-19-2007 06:44 PM
Breaker Buzz SkipI Electrical 2 07-13-2007 08:48 PM
Breaker keeps being thrown (solution?) JH7800 Electrical 4 06-28-2006 04:55 PM