#1 |
industrial motor circuit
Hey guys, i'm trying to make sure my companies air compressor circuit is up to code. The NEC is a little confusing to me on this topic. we currently have a 300hp compressor supplied by a 600amp molded case circuit breaker. line of sight is an issue. my question is, according to NEC, do i need a CB at start of circuit sized to protect feeder conductors, a CB sized for motor FLA (for branch-circuit and short-circuit protection) and then a Disconnect at the motor for line of sight? also does the disconnect have to be fused or not? thanks for the help.
#2 |
What is the voltage? Or just post all the nameplate data on the motor.
#3 |
480v, 3ph, FLA 349amps
#4 |
Scott, Sorry I forgot you and your post.
1) Breaker - Motor FLA x 2.50 = 872 amps. Table 430.50 This is the maximum allowable breaker current for a squirrel cage motor using a regular inverse time breaker. The existing breaker is okay. 2) Conductors - Motor FLA x 1.25 = 436 amp. Use article 310.15B to find conductor size. What size wire do you have? Yes, you need a breaker sized as above to protect the motor and a non-fused disconnect at the motor if it is not in sight of the breaker. 430.107 This is one instance where the breaker size can exceed the wire amp rating. Note: These calculations are not engineered to your application. This is for exercise and nothing more. Consult the NEC and the engineering dept for specifics. Last edited by J. V.; 09-13-2012 at 01:54 PM. |
#5 | |
Lic Electrical Inspector
industrial motor circuitQuote:
361 x 125% = 451.25A. The ITCB is 361 x 250% = 902.5A I like your note.
All responses based on the 2011 NEC. If you live in New Jersey click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . All other states click To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Please check with local, county and state officials as laws may vary. Sizing motors To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online motor calculator To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . Online calculators To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. . |
#6 | |
#7 |
Nameplate amps are 349. That is what I used. Must I use the NEC current?
#8 | |
#9 |
Idiot Emeritus
You need only one circuit protection. It can be a breaker or fuses. You can have more than one, but it's dumb.
430.28 covers feeder taps and location of the protection. Basically it says that you can have conductors tapped from a larger source if they land in a protective device under two conditions. 1) If the source is 1000% or less than the rating of the tapped conductors, they can be not longer than 10' from the tap to the protective device. 2) If the source is 300% or less than the rating of the tapped conductors, they can be not longer than 25'. There's an exception about buildings 35' high or higher, but I doubt if it applies here. In my experience, a 600 amp breaker is ok for a 300HP motor operating at 480 volts. If the breaker is in in compliance with 1) or 2) above, then the motor feeders are protected. If needed, a non-fused disconnect can be installed closer to the motor. Or a fused one, but there's no reason for the fuses. Rob |
#10 |
Thanks guys, the info helped. Appreciate your responses.
#11 |
6ea 4/0 THHN CONDUCTORS
#12 |
Idiot Emeritus
Per the NEC, two parallel (6 wires) of 3/0 copper would be the minimum if there are 3 wires in two conduits. If all 6 are in the same conduit, 4/0 copper is the minimum.
Rob |
#13 |
JOATMON
300HP? And your starting this across the line without a VFD or softstart?
That is a lot of HP to run just off a contactor....
Common Sense is like Deodorant. Those that need it the most don't use it. My To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. ... To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. and To view links or images in signatures your post count must be 10 or greater. You currently have 0 posts. |
#14 | |
I disagree. The motor brach circuit conductors have to be sized at 125% of the motor FLA using Table 430.250. 361 x 125% = 451.25A 700 KCMIL THHN CU (rated 460A) per conductor if three are used. 250 KCMIL THHN CU x 2 per phase if two sets of paralleled (6 conductors in one conduit). 250 KCMIL THHN CU are rated 290A x 2 = 580A x 80% = 464A
#15 |
The local utility probabely has restrictions on the size of motor started by across the line starters. I think around here it is 150HP.
| Display Modes | |
| Industrial Window Shade | dcase84 | Interior Decorating | 5 | 09-04-2012 11:41 PM |
| Flat Industrial Roof | timsb | Roofing/Siding | 4 | 06-05-2012 12:37 PM |
| two industrial ceiling fans on one switch | arusillon | Electrical | 4 | 01-17-2012 05:57 PM |
| Tiling on industrial steel | don57 | General Discussion | 3 | 10-18-2010 11:26 PM |
| Industrial Designer | johall | Introductions | 2 | 05-08-2009 01:54 AM |