Go Back   DIY Chatroom Home Improvement Forum > Home Improvement > Electrical

CLICK HERE AND JOIN OUR COMMUNITY TODAY...IT'S FREE!

Reply
 
Thread Tools Search this Thread Display Modes
Old 03-07-2012, 07:06 PM   #1
AHJ
Newbie
 
Join Date: Mar 2012
Posts: 13
Rewards Points: 10
Default

Inductive heating


I have always understood that the way Inductive heating is limited by two ways, One, 120 volt single phase circuit, induction is reduced by the grounded conductor, by bringing the unbalanced load back.
Two, 120/208 Volt three phase or single phase, by having two phases or more in the same conduit this cancels out the induction?
So with that said, I have a two tub panel, 120/208 volt three phase system. I nippled into a contactor control cabinet for refrigeration that the panel feeds. I used two, 2" nipples, in the top nipple I ran my load conductors (switch legs)
and in the second conduit I ran all of my Line conductors. My load consists of Door heat, anti sweat heaters, fans for dual temp cases and lights.
Question, My inspector hit my on the way that I grouped my conductors, his argument is, Need to run my Hots, and the switch leg for that hot in the same raceway to prevent Inductive heating?
Only place I have seen this in is 300.3 (B) but I don't think this is the code that the inspector is talking about, curious to know where this information is.

AHJ is offline   Reply With Quote
Old 03-08-2012, 09:09 AM   #2
Craftsman
 
Join Date: Nov 2008
Location: Kentucky
Posts: 66
Rewards Points: 75
Default

Inductive heating


300.5 (i)

Superrick is offline   Reply With Quote
Old 03-08-2012, 02:12 PM   #3
Member
 
Join Date: Jul 2008
Location: NW of D.C.
Posts: 5,990
Rewards Points: 2,000
Default

Inductive heating


It's further limited by using a twisted pair. The mag field from each wire tends to cancel.
Yoyizit is offline   Reply With Quote
Old 03-17-2012, 10:15 AM   #4
AHJ
Newbie
 
Join Date: Mar 2012
Posts: 13
Rewards Points: 10
Default

Inductive heating


Ok, what is the difference between my installation, or setting a junction box above ceiling for a pull box, conductors in, and out? Besides i used chase nipples, so technically its not conduit. I personally think the inspector is full of it, but I did change it only because he is Authority Having Jurisdiction.
AHJ is offline   Reply With Quote
Old 03-17-2012, 11:33 AM   #5
JOATMON
 
ddawg16's Avatar
 
Join Date: Aug 2011
Location: S. California
Posts: 7,487
Rewards Points: 2,316
Default

Inductive heating


mmmmm......I think you guys are using the wrong term.....

At 60 Hz for straight runs....the amount of 'inductive heating' from the wires due to magnetic field produced is so small that I don't think you can measure it....sorry...but your getting a lot of misinformation.

About the only heating in the wire your going to get is from the temp rise due to high currents. This is the reason for fill specs for conduit...

Allow me to give you a little science lesson....

When current is passing through a wire, a magnetic field is generated around the wire. Think left hand rule...wrap your hand around the wire with your thumb pointing in the direction of the current flow....your fingers show the direction of the magnetic field. When that wire is next to another wire, you do get some mutual inductance into the other wire....on long runs you will get some induced voltage into the other wire...but no current....in other words...if you measure it with a high impeadance meter, you might measure 50 Vac..but grab it with your hand and the voltage would drop to almost nothing.

In order to get any heating from inductance you need a magnetic load....like iron....wrap the wire around an iron rod...pass current through it...now you can get some heating....wrap the same wire around something non-magnetic....no heating....if you do get some heating...it's only because of the resistance of the copper....hence, resistive heating. A good example is the inductive heating stove tops....you have to use the special pots on them...

If inductive heating was such as issue then there would be a lot of comercial installations with issues....for example....some of those 1000 HP motors that we run power to where each leg is in it's own conduit....no neut cond in the conduit to cancel the 'inductive heating'.

Regarding the 'twisting' of the wires....that is used to reduce noise coupling. The twist actually puts the wires at a 90 deg angle to each other which helps to eliminate noise....does nothing for 60 Hz....more applicable to high freq....like your Ethernet cable.
__________________
"The dream is free but the hustle is sold separately."

My 2-Story Addition Build in Progress Link ... My Garage Build Link and My Jeep Build Link

Last edited by ddawg16; 03-17-2012 at 11:35 AM.
ddawg16 is offline   Reply With Quote
Reply


Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
What is a good efficient heating system for cold climates? reveriereptile HVAC 7 02-08-2012 08:26 PM
Electric baseboard heating virago Electrical 8 05-18-2011 11:36 AM
Radiant floor heating questions secutanudu HVAC 35 03-08-2010 01:04 PM
Hydrokientix Heating System Not Heating damonl73 HVAC 11 12-18-2009 05:12 PM
Electrical consumption of baseboard heater CowboyAndy Electrical 7 03-24-2008 07:27 PM




Top of Page | View New Posts