Old 08-11-2012, 01:50 PM   #1
I'm sure that this has been asked before:
I apologize in advance.
I have a 1957 ranch. The outside service and the breaker box have been updated, also all wiring and outlets in the remodeled kitchen & baths.
However, the rest of the house (bedrooms, living room, dining room) have the original wiring running to the outlets from the new breaker box. The outlets themselves have been replaced with new 3-prong outlets.
I'm selling the house.
The home inspector just included this in his report:
REPRESENTATIVE DEVICES
Mostly 2-wire (ungrounded) wiring and receptacle outlets noted on main level. This is typical of this age house, however, new wiring may be required to accommodate some modern appliances. Most of the 3 prong outlets on the upper level are not grounded. I recommend having grounded for proper design function. Ungrounded 3 prong outlets are considered a hazard.
Can both these items be fixed by replacing the outlets or is it necessary to actually run new wires to the breaker box?
TIA
fragonardium is offline   Reply With Quote
Old 08-11-2012, 02:00 PM   #2
Electrical Contractor
Replace the 3 prong receptacles with 2 prong type.
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
The Following User Says Thank You to jbfan For This Useful Post:
gregzoll (08-11-2012)
Old 08-11-2012, 02:25 PM   #3
A "Handy Husband"
rjniles's Avatar
Or identify the first receptacle on each circuit and install a GFCI. Then connect down stream receptacles to the load terminals of yhe GFCI.
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 08-11-2012, 02:26 PM   #4
"So I Re-Wired It"
MisterZ's Avatar
exactly. they cannot complain if a 2-wire is connected to a non-ground 2-prong recepticle.
im guesing the outlet boxes are metal. if the metal boxes are clamped to armored cable or BX type wire, this will connect ground from the box to the panel.
if this is your case you can add a ground clip or screw to the metal boxes, then pigtail copper to the recepticle ground.
Knowledge is Power, but 240v can Keel You!!
MisterZ is offline   Reply With Quote
Old 08-11-2012, 05:08 PM   #5
E2 Electrician
stickboy1375's Avatar
Not all BX is suitable for use as en equipment grounding conductor.
The Following 4 Users Say Thank You to stickboy1375 For This Useful Post:
kevinp22 (08-11-2012), MisterZ (08-11-2012), mpoulton (08-11-2012), rjniles (08-11-2012)
2x in a row ive asked for some help and gotten blown off jpc Tiling, ceramics, marble 3 02-16-2011 12:35 PM
Plywood thickness: asked for 1/2" plywood; hardware delivered 7/16 (.437) thickness) lazzlazz Flooring 7 03-31-2010 12:25 PM
asked in appliances & it was suggested,,, yes.itsconcrete HVAC 16 11-16-2008 07:58 AM