Old 03-11-2012, 06:23 PM   #1
Identifying a circuit type, with an orange wire
I am trying to replace a rocker switch that runs my Panasonic bathroom exhaust fan with a programmable switch that allows me to run the thing automatically several times a day to help suck moisture out of the condo (it's a 1962 condo with concrete walls, aluminum windows, and no central air).
I initially bought a GE SunSmart Timer but it requires a neutral, which I don't think I have. I understand there are some other switches like Intermatic ones that don't require neutrals.
I don't think I have a neutral because the condo is old and I don't see a white wire in the box, but what's strange is that I do see an unconnected orange wire in there. Does anybody know what that could be? Image is attached. Essentially there are 2 blues, 1 red, 1 black, and 1 orange (unconnected) in there. The only thing I can find about orange wires is something called a "high leg delta" circuit, which seems reasonable because it's supposedly used to control fans and lights off the same circuit, which is exactly what's going on here (one can light, one heat lamp, and one fan).
Any ideas?
mikeindustries is offline   Reply With Quote
Old 03-11-2012, 06:36 PM   #2
Licensed electrician
I don't see a neutral in your box. I suspect the orange is another switch controlled hot, maybe for a night light in the fan.
The orange is not part of a high leg delta. Three phase service in a residence is not needed.
Since you have a conduit system you should be able to pull a neutral to the box.
mikeindustries (03-11-2012)
Old 03-11-2012, 07:15 PM   #3
UAW SKILLED TRADES
Stubbie's Avatar
Are you in the USA? Just asking to be sure ...
As Jim said the wire colors indicate you have a conduit system. One switch appears to be a two switch combination device and the other is a single pole switch.
Unless the combination device has a receptacle (I can't tell) and a switch I would suspect there is no neutral in the box which is also confirmed by the fact there are no white wires.
High leg delta is a three phase system where the B phase is identified with orange marking as the high leg and cannot be used for 120 volt branch circuits. The orange wire shown is simply a wire meant to be used for a hot wire or switched hot in the branch circuit.
If the orange originates in the fan/light box and is unused you could use it to pull a neutral to the switch box
" One nice thing about the NEC articles ... you have lots of choices"
Stubbie
The Following User Says Thank You to Stubbie For This Useful Post:
Old 03-11-2012, 10:23 PM   #4
Thanks guys. Yep, I'm in the U.S. I have no idea why it was wired the way it was, with no neutral at the switch, so it seems like the path of least resistance would be to just buy an Intermatic timer that doesn't require a neutral. I think they use batteries to keep a bit of power going to the timer. I could probably pull wire to this location pretty easily since it's a few feet away from the circuit breaker but there is another location which needs a timer as well and it's quite a bit further away.
Agree? Simplest to just get a different switch?
Old 03-11-2012, 10:37 PM   #5
The neutral you need should be in the box with the utilization equipment. It should be an easy pull down to the switch box.
Old 03-12-2012, 07:35 AM   #6
hammerlane is offline   Reply With Quote
Old 03-12-2012, 07:41 AM   #7
Like STubbie said if that unused orange wire at the switch location is also at the fan location, wire nut the orange at the fan location to the neutral at the fan location. Now you have a neutral at the switch location.
The elctricity does not care what color insulation is over the neutral conductor but maybe wrap some white tape around the orange insulation at the switch location and fan location
Old 03-12-2012, 09:43 AM   #8
Licensed Pro
The electricity might not care, but you are advocating the OP to commit a code violation. Use the orange wire to pull in a neutral (white). If the possibility exists that the "orange" leg might be used in the future, pull in the white AND a wire of any color other than green, grey, or white.
The Following User Says Thank You to HouseHelper For This Useful Post:
Jim Port (03-12-2012)
Old 03-12-2012, 10:58 AM   #9
Good idea.
Hey at least I suggested taping the ends of the orange wire with some whit tape. Gimme credit for that. SO would be 1/2 a code violation.
Old 03-12-2012, 11:23 AM   #10
UAW SKILLED TRADES
Stubbie's Avatar
Absoultely, there are many times I have sacrificed a wire being used to pull another wire. You just have to be sure to pull in its replacement .....
Stubbie
breakers with multi wire branch circuit (shared neutral) corman Electrical 0 09-11-2011 12:52 AM
ceiling fan wicked97 Electrical 4 08-21-2011 09:12 AM
Mixed Wire Gauges off of a 20A Circuit jfhanson4 Electrical 4 04-20-2011 07:46 PM
Black/White/Orange wire...what to do with orange Wingingit Electrical 9 06-23-2009 01:10 PM
ground wire in mc circuit woodturner Electrical 10 08-07-2008 12:34 PM