An HVAC Electrical ? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-13-2008, 03:43 PM   #1
An HVAC electrical ?
Ok, I am just looking for ballpark figures as I know I can't get an exact answer since I don't have a brand of HVAC yet. But I am curious as to how much amperage a 5 ton unit will use with the air handler and condenser.
Thanks.
737Pilot is offline   Reply With Quote
Old 10-13-2008, 04:02 PM   #2
DIY
Rewards Points: 150
My 2 ton HP system pulls about 9 amps total on second stage heat, a bit less on second stage cooling. Those are real numbers at the sub panel feed line with an amp clamp.
gp_wa is offline   Reply With Quote
Old 10-13-2008, 04:10 PM   #3
DIY'r
ScottR's Avatar
~25A @ 240V running load .. This is a generator sizing guide, but lists approximate loads for AC units (PDF!) http://www2.sea.siemens.com/NR/rdonl...zing_guide.pdf
ScottR is offline   Reply With Quote
Old 10-13-2008, 11:36 PM   #4
Idiot Emeritus
Rewards Points: 1,492
I'd say around 25 to 30 amps.
When you get the unit, or at least its spec's, it'll most likely list a 'minimum circuit ampacity', or MCA. This determines the wire size.
It will also list a maximum fuse or breaker size. This listing is almost always over the current rating of the wire. HVAC, motors, and welders are some of the few instances where a breaker can be rated higher than the wire. Unfortunately, a lot of inspectors don't know this, and have to be led through the codebook.
Most likely, it'll need either an 8/2 or 10/2. Two hots plus a ground, no neutral.
Rob
micromind is offline   Reply With Quote
Old 10-14-2008, 08:00 AM   #5
An old Tradesmen
Rewards Points: 8,234
13 SEER, Less then 40 amps combined.
The average 5 ton 13 SEER OD unit will need a 8/2 with ground.
10/2 would not meet min circuit requirements of outdoor unit.
Old 10-14-2008, 12:24 PM   #6
Rewards Points: 246
Those readings sound awful low to me. And if you mean "heat strips" for second stage heat it definitely is wrong. 9 amps.
I would check it with another clamp.
When you get your new unit, it will have all the requirements on the name plate. And if you know what you are getting, you can always get the specs in advance from the supplier.
low-voltage and electrical wiring sharing same stud space jheavner Electrical 21 10-06-2011 11:16 AM
History of HVAC Industry Brands winkydink HVAC 8 03-25-2011 07:28 AM
Electrical or HVAC? Redeyejedi General DIY Discussions 1 04-08-2008 04:18 PM
new 3 ton hvac Payne units. No cool air comes out when fan, compressor,thermostat run runbikeengr HVAC 10 04-10-2007 05:59 PM
So lost - electrical requirements please help lapsis9 HVAC 4 12-20-2006 08:09 PM