How To Wire Seperate Oven/range With One Feed And Different Breaker Size - Electrical - DIY Chatroom Home Improvement Forum
Old 10-29-2012, 06:58 PM   #1
how to wire seperate oven/range with one feed and different breaker size
im doing a minor facelift to my kitchen and went with a seperate oven and countertop range set up.what im trying to figure out is how do i wire the oven and range with different size amp breakers. the one feed there now has a 40amp in it cause it was for my original oven. the ge range is showing a 40amp breaker size but the oven is calling for a 20amp ,according to the online specs. this is on the main floor but the basement is completely finish or else i would have just run another feed.any thoughts? thanks
raaaidvw is offline   Reply With Quote
Old 10-29-2012, 07:03 PM   #2
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,214
You can 't, run another 20 amp circuit. BTW unless you existing circuit is 4 wire, it slso needs yo be replaced.
Coastal South Carolina
Old 10-29-2012, 07:07 PM   #3
it is a 4 wire (red,black,white,bare) can i not use the 40 for the range then wire in a small breaker panel for the 20?
Old 10-29-2012, 07:28 PM   #4
A "Handy Husband"
rjniles's Avatar
Yes you can install a small 4 space sub panel but where would you put it and meet accessability requirements?
Old 10-29-2012, 07:54 PM   #5
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
A little correction to RJ's statements. Even if the feed is 3 wire to the existing range, you can still use it. You cannot use it, however, for a small subpanel.
The sub panel idea won't work anyway. You will still be overloading the circuit. 40 Amps is 40 Amps no matter if it is being supplied by a main panel or a sub panel.
Old 10-29-2012, 09:36 PM   #6
i got a new plan but wanted to pass it by you guys to make sure it will fly. i managed to open up a small section of drywall in the basement and pulled the line that fed the stove through and into the basement. the wire is 6/3 ,so 4 wires including the bare. the breaker at my main panel are 2x 40amp obviously for the 240.now im thinking of changing out the breakers to 50amps and then running a sub panel in the laundry room where i pulled the wire through and run 2 seperate 6/3 lines to feed the 20amp oven and the 40 amp range.will that work and any other suggestions? thanks
Old 10-29-2012, 09:42 PM   #7
k_buz's Avatar
Maybe, maybe not. We would need to know the KW rating of each of the appliances.
Old 10-29-2012, 09:54 PM   #8
the oven is showing 3.8kw@240,2.8kw@208v and the range is 7.7kw@240,5.8kw@208v.
Old 10-29-2012, 09:57 PM   #9
k_buz's Avatar
If you were in the US you would be OK, however, I now notice that you are in the great white north. I will defer this question to one of our Canadian posters.
The Following User Says Thank You to k_buz For This Useful Post:
raaaidvw (10-29-2012)
Old 10-29-2012, 10:04 PM   #10
what makes it ok in the U.S. is it the amp x volt=watts theory. i did the math and it looked like the wattage of the appliances does not exceed the wattage the circuit can safely handle.does that make sense? i thing i should be at 80% iunder its max load .
Old 10-29-2012, 10:08 PM   #11
Electrical Contractor
kbsparky's Avatar
In the US you could simply splice all the lines together at a junction box, and connect it to a 50 Amp breaker. No further breaker needed.
I do not know if the CEC allows this or not.
-KB
Old 10-29-2012, 10:28 PM   #12
k_buz's Avatar
While that may be legal according to the NEC, most of those appliances will spec a certain circuit size.
Old 10-29-2012, 10:42 PM   #13
but what if they require different amp sizes like what im dealing with? i could see if both appliances used the same amp breaker.
Old 10-29-2012, 10:56 PM   #14
kbsparky's Avatar
Tap conductor rules allow for a 20 Amp oven to be connected to a 50 Amp feeder without any further overcurrent protection.
See NEC section 210.19(A)(3) Exception No. 1
I am not sure if the CEC has a similar ruling.
-KB
Old 10-29-2012, 10:59 PM   #15
k_buz's Avatar
True, but if the manufacturer specs "connect to a dedicated 20A 240V circuit" you cannot do what you are proposing.