-   -   how to wire an electric heater (http://www.diychatroom.com/f18/how-wire-electric-heater-20285/)
murray59 04-24-2008 12:15 PM
Okay, I bought a Dimplex EF621C electric heater. It just has two grey wires at the back and a ground screw. It says it is 2kW maximum load and can be hooked up 240 or 208 volt supply. It's the 240/208 part that's got me confused. I plan to run a 14/2 to the electrical box and hook each wire to either side of a double 20amp breaker and have no neutral. That's 240v right? Am I on the right track? What's the 208v about?
LawnGuyLandSparky 04-24-2008 12:42 PM
240 is what you get between 2 legs of a single phase, typically residential utility distribution 120/240 volt transformer.
208 is what you'll most likely see between 2 phases of a 3 phase, typically commercial distribution 120/208 volt transformer.
slakker 04-24-2008 12:51 PM
One thing I'd do is to install a 2 toggle thermostat as well... some thermostats only switch one leg of the circuit....
Speedy Petey 04-24-2008 12:59 PM
It says it is 2kW maximum load and can be hooked up 240 or 208 volt supply......
What you have very wrong is that you CANNOT use 14/2 on a 20A breaker, especially for a 2Kw heater.
You need to use 12/2.
murray59 04-24-2008 01:43 PM
Okay, I'll run 12/2.
When I install the breaker does it click in accross two buss bars or one space over so it's on one buss bar?
murray59 04-24-2008 01:45 PM
This heater has a built in thermostat for a circuit that provides up to 1000w and it also has a delay timer that, when activated, boosts it up to 2000w.
J. V. 04-25-2008 11:37 AM
Install the breaker like the other single pole breakers in the panel. Make sure you get the right one for your panel. 20 AMP.
CowboyAndy 04-25-2008 11:48 AM
That should be DOUBLE pole breaker... it's a 240v heater...
J. V. 04-26-2008 11:21 AM
Right Cowboy.