How To Tell If My Neutral Is Bonded To My Ground? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 07-06-2012, 12:19 AM   #16
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Originally Posted by simanco View Post
The grounding electrode is under the new meter box. You should be able to see it in the attached picture.
I can't see any copper coming into the panel but there is so much copper in that corner it could still be hiding from me. Is it possible to ground the panel via all that metal conduit shown in the picture?
Jim
Thank You, that is an allowed point of earth grounding. If you have metal water pipes you should have a grounding electrode conductor running to those also .. to within 5' of where the main line enters the house. Local codes sometimes require it to be closer than 5'. The key is the main line must be underground for at least 10' after leaving the house in order to be a required electrode. If it isn't then your not required to have a water pipe bond.
Old 07-06-2012, 12:21 AM   #17
Rewards Points: 83
No metal water pipes, so I don't have to worry about that one.
Thanks,
Jim
simanco is offline   Reply With Quote
Old 07-06-2012, 12:24 AM   #18
UAW SKILLED TRADES
Stubbie's Avatar
Then your good ... some others may have some questions but IMO your fine.
Old 07-21-2012, 02:09 PM   #19
Rewards Points: 83
Hey all,
I just pushed aside the bundle of wires over one of my bus bars and found the little item in the attached picture. My guess is that's the bonding strap that bonds the neutral and grounding bars. It is definitely running under the plastic strip that runs between the bars.
It's loose and I think it should be tightened down. Am I correct?
Thanks,
Jim
Old 07-21-2012, 02:38 PM   #20
Rewards Points: 1,542
Yes it should be tightened down. While you are at it, you might as well tighten down all the other screws and set screws holding wires in place. Flip off each breaker before tightening the screw(s) on it. (An experienced person should tighten the big lugs holding the fat service wires in place.)
3 Wire Set Up . . . Neutral Wire Tied to Ground Wires irishMonster Electrical 14 10-21-2010 08:20 AM
240 volt load/appliance and ground vs neutral kgize Electrical 7 04-22-2010 11:40 PM
Ground question. mystery guest Electrical 5 07-24-2008 12:47 PM
Nuetral from feeder cable to main panel question? TW Lucas Electrical 14 05-08-2008 11:33 AM
Hot Tub Install--Grounding Rod Question statgeek_rob Electrical 16 09-15-2007 02:59 AM