How Are Stove Amperages Calculated? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-07-2013, 12:58 PM   #1
Rewards Points: 83
How are stove amperages calculated?
Hello all,
How do stove manufacturers calculate the amperage ratings for their stoves?
I ask because our stove calls for - and has been on for 30 years - a 50 amp circuit.
The problem is that I did a calculation by adding up the wattage of all the oven and surface elements and that indicates it should be on a 70 amp circuit.
I don't understand. Can someone enlighten me?
(2) 2600w surface elements = 5200w
(2) 1500w surface elements = 3000w
One large oven at 5800w
One small oven at 3000w
A total of 17000w at 240v is 70.1amps when I do the math.
Jim
simanco is offline   Reply With Quote
Old 10-07-2013, 01:12 PM   #2
joed's Avatar
Rewards Points: 11,592
It is based on the fact that all the elements are not likely to be on FULL at the same time.
The Following User Says Thank You to joed For This Useful Post:
Know A Little (10-07-2013)
Old 10-07-2013, 01:41 PM   #3
nec allows demand factors for ranges and other cooking appliances, for just the reason joed mentions above. check 220.55
itsnotrequired is offline   Reply With Quote
Old 10-07-2013, 08:50 PM   #4
Rewards Points: 83
And commercial ranges would fall under another section of the NEC? I went poking around and a Garland commercial electric range with nearly the same kW rating as our old Kenmore calls for the full breaker capacity.
The reasoning would be that in a commercial environment, it would be more likely for all the heaters to be on full at the same time?
Thanks,
Jim
Old 10-07-2013, 09:01 PM   #5
Rewards Points: 774
Thanks,
Jim
And operate for a longer period of time.
Know A Little is offline   Reply With Quote
Old 10-08-2013, 05:33 AM   #6
Electrical Contractor
kbsparky's Avatar
Thanks,
Jim
Not likely unless you want to burn all the food to a crisp.
-KB
Old 10-08-2013, 05:33 AM   #7
Philly Master's Avatar
Rewards Points: 516
Hello all,
Jim
there is a tag on the oven ... with the wattage ..usually in the front ..
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
The Following 2 Users Say Thank You to Philly Master For This Useful Post:
J. V. (10-08-2013), plummen (10-08-2013)
Old 10-08-2013, 05:58 AM   #8
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
A total of 17000w at 240v is 70.1amps when I do the math. Can someone enlighten me?
Jim
This is sort of on the line if you were to add all the breakers up in your electrical panel.
Most likely to be much higher than your main breaker rating. Mine is 500
wirenut1110 is offline   Reply With Quote
Old 10-08-2013, 07:28 AM   #9
Rewards Points: 774
My point was commercial stoves operate for long periods of time, while in a residential application it is a cook and done
Old 10-08-2013, 07:33 AM   #10
Rewards Points: 510
I own a restaurant and our equipment is turned on at 10:30 am-1:30 am 7 days a week and the meter just goes "cha ching cha ching"
The Following User Says Thank You to wirenut1110 For This Useful Post:
Know A Little (10-08-2013)
Old 10-08-2013, 08:17 AM   #11
Rewards Points: 718
even if the oven was at 100% load, a 50 amp breaker at 70 amp will take few minutes before tripping. Pretty sure the oven has some type of limiting current also, it can deactivate some heater. If you put your your surface element at high they will stop after few minutes because they will overheat, so there a not a continuous load, same thing for the oven.
carmusic is offline   Reply With Quote
Old 10-08-2013, 09:17 AM   #12
Rewards Points: 774
A 50 amp molded case circuit breaker will handle 70 amps a 40% overload for a LONG TIME, may not trip for hours, depending on adjacent circuit breakers and the ambient at the panel. A typical molded case residential style circuit breaker will handle 300% overload for 35-80 seconds, on average not verifying the Time Current Curve for any particular circuit breaker based strictly on experience.
Old 10-08-2013, 09:37 AM   #13
yep, breakers can carry overloads for a damn long time. it is a misconception that a, say, 20 amp breaker will trip right at 20 amps. it could very well carry 22 amps indefinitely and never trip.
of course, one should never knowingly overload a circuit breaker. it is bad practice and prohibited by code.
Old 10-08-2013, 11:05 AM   #14
Rewards Points: 58
Hello all,
Jim
Taking this a step further.
Imagine the size of the service for an apartment building if they used the 50 amp load for every apartment or condo.
In this example, the NEC is assuming all of the ranges will never be on at the same time.
Its called derating. Derating allows the engineer or contractor to be able to install in a practical manner while installing for safety.
J. V. is online now   Reply With Quote
The Following User Says Thank You to J. V. For This Useful Post:
Old 10-08-2013, 11:34 AM   #15
and the derates for large buildings are insane. the oven/range load for a 41 unit apartment is 25 kw plus 3/4 kw for each additional range or about 56 kw TOTAL, even though there may be more than 330 kw of connected load. the assumption is that no more than 10 or so units will be using the equipment at the same time. there is no scientific method to determining these derates, it is all based on past experience.
but yeah, if everyone in the building turned their ovens on at the same time, likely some breakers will start popping!
The Following User Says Thank You to itsnotrequired For This Useful Post:
J. V. (10-09-2013)
Heat for a basement with Pellt Stove on Main Floor magnum44 HVAC 1 11-20-2011 09:55 AM
Do you have a Wood/Pellet Stove Insert with a Raised GRANITE Hearth? gmoom Remodeling 1 01-24-2011 05:54 PM
Wood burning stove trim not flush against chimney Fortitude Appliances 1 11-11-2010 10:28 PM
Wood Stove, and Furnace hot water system shendog HVAC 7 10-04-2010 10:30 PM
Three electricans said it was impossible! Tom Electrical 35 04-29-2006 06:06 PM