How Much Current Draw - Electrical - DIY Chatroom Home Improvement Forum
Old 12-10-2006, 08:41 PM   #1
How much current draw
I understand I can run 20amps on a 12 guage wire but I have a cable that is 12/3, ie, red, white, black, green. So my question is, can I run 20amp on both the red and black?
I'm confused because I would think the return white wire would still only be rated for 20amps total but if the other two ran 20 then that would put a 40amp load on the white wire.
What am I misunderstanding?
drhowarddrfine is offline   Reply With Quote
Old 12-10-2006, 09:07 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
Copied from my reply on the other forum:
It is actually the opposite. The white will only carry the imbalance of the two circuits of a multi-wire circuit.
For instance, if the black is carrying 10 amps, and the red is carrying 7 amps, the white is only carrying 3 amps.
Understand?
This is provided the multi-wire circuit is wired correctly. Meaning the two hots are on different "phases" in the panel.
Old 12-16-2006, 02:36 PM   #3
Rewards Points: 79
Speedy Petey is right about having the "hot" wires on 2 different phases in the panel. To check this, you should have 240 volts (or close to it) from black to red. If you have nothing from black to red, then both "hots" are from the same phase...and you would be overloading the neutral (white) wire, as you first mentioned. "Edison 3-Wire Circuit"...http://www.bobvila.com/BBS/3_wire-El...l-1-T1593.html
sootybuttercup is offline   Reply With Quote
This doesnt seem right. JoulesWinfield Electrical 27 07-26-2009 07:40 PM
Current trends: Cast Iron or Stainless Steel sink? Fat b Remodeling 4 05-04-2007 07:09 PM
Current through my A/V components HELP! aperionguru Electrical 1 03-14-2007 04:42 AM
Am I Crazy? AC Current Less than 110 kahuna44 Electrical 8 03-02-2007 10:25 AM
Time Current Curves allenroad Electrical 1 03-19-2005 07:24 PM