how many lights in a circuit as per code
It is my intention to place 24 pot lights around
the perimeter of the house. 24 lights of 50 watts, having of total of 1200 watts. 1200 watts divided by 120 volts gives me 10 amps. I have placed a new breaker of 15 amps. Wich lead me to think that I will be OK. The question that I have is: How many lights I am allowed asper code in one circuit. IT is 12 lights ONLY???? PLEASE REPLY..thanks |
#2 |
You talking to me?
what country?
If the US, there is no limit by quantity. It is determined by load, or more correctly, possible load. If the max wattage listed on the lights is 50 watt or 60 watt, you are fine. If they will accept a 75 or even a 100 watt, you need to have fewer lights or a bigger (amperage) circuit. figure 80% of the breaker as max load. Lights, although they are not considered to be a continuous load generally, calculating them as if they were gives you a margin of safety in the calculations. Last edited by nap; 10-03-2010 at 01:25 AM. |
#3 |
Wire Chewer
In Canada it's 12 items per circuit.
#4 |
You talking to me?
how many lights in a circuit as per code |
#5 |
Wire Chewer
#6 |
You talking to me?
I know. I was just picking on ya RS. That 12 count thing is a strange limitation to me. I just cannot justify the rule.
#7 |
Electrician
Nap the rule does not make any sense to me either but it does stop people from overloading there circuits.
The 12 items on the circuit does have an exemption that most people do not know about. If you know the connected load you can put more then 12 items on a circuit as long as you don't go above 80% of the breaker. So if you have potlights that have a max bulb of 50W(.42A) you could put 28 on a 15A circuit. Your question about the christmas lights would be the plug counts as one outlet and you can put as many as the circuit can handle. A 4 light vanity in your bathroom would be 1 outlet. An outlet is described as a point in wiring installation at which current is taken to supply utilization equipment. Last edited by darren; 10-02-2010 at 11:46 PM. |
#8 |
The limit of 12 is in the Canadian code code. However if it is lights only the limit can be exceeded if you use the max wattage of the fixture and keep it under 80% (1440 watts). It must be only lights. There can be even on receptacle or you are limited to 12.
Do not PM with questions that can be asked in a forum. I will not respond. |
#9 | ||
You talking to me?
how many lights in a circuit as per codeQuote:
actually the limit of 12 is not a bad idea for receps although I tend to limit it to less than that even if it is my design and choice. Quote:
![]() it really was a joke for RS. |
#10 | |
" Euro " electrician
Now to OP this what I useally do and yeah I am electrician as well. What I do is take the max wattage rating of each can luminaire and add them up to see how far I can go to load up the circuit so if the can have 120 watts like example then I can go 12 cans on this circuit that is max on 15 amp circuit { I know I can load it up to max of 1800 watts but I rather leave a little margin there } so you have to plan it ahead a little. Merci. Marc |
#11 | |
You talking to me?
thanks. |
| Display Modes | |
| Can I use lights and outlets on same circuit? | heyd | Electrical | 4 | 08-24-2010 01:05 PM |
| Code question on extending existing 120v circuit | radiercks | Electrical | 15 | 11-14-2009 06:29 PM |
| Outdoor lights on Kitchen Light Circuit | WaldenL | Electrical | 5 | 08-28-2009 02:16 PM |
| Lights in same joist space with water pipes - Code violation? | jweller | Electrical | 2 | 03-15-2009 02:02 PM |
| Adding lights to a circuit.. Pl check circuit | aw44 | Electrical | 4 | 08-27-2008 03:09 PM |