Old 08-25-2011, 09:24 AM   #16
Code05's Avatar
Rewards Points: 1,104
Originally Posted by brric View Post
Panel will require a main if there are more than six breakers.
Good catch, I thought garage was attached when I said MLO.
Code05 is offline   Reply With Quote
Old 08-25-2011, 09:28 AM   #17
Code05's Avatar
Originally Posted by dw1256 View Post
I think this is my last question. There are also some other wires that run out from the basement to the garage that power lights on side of the garage and the roof. They do not get any power from the load center, but they do run through the panel as if it were a junction box. Any idea if that is not allowed?
Thanks again. You have been very helpful.
If this garage is detached, now you got a problem here. More than 1 supply to a building.
Old 08-25-2011, 11:26 AM   #18
Originally Posted by Code05 View Post
You have a code book, it would be easier to explain.
I will see if I have a link.
I have access to the 2008 National Electric Code book.
dw1256 is offline   Reply With Quote
Old 08-25-2011, 11:29 AM   #19
Code05's Avatar
Go look at table 310.16.
Old 08-25-2011, 11:33 AM   #20
The reason for this is because there are 3 way switches between the house and garage for certain lights. Is that not allowed?
Old 08-25-2011, 11:44 AM   #21
Code05's Avatar
Only if the switches are fed from the garage or the wire feeding the lights does not enter the garage.
The Following User Says Thank You to Code05 For This Useful Post:
frenchelectrican (08-25-2011)
Old 08-25-2011, 12:37 PM   #22
Let's say I rewired them so that they were using power from the garage. They can still be controlled by switches in the house, correct? Also, now that I have to use a panel with a main breaker due to the amount of breakers used, can I still make connections inside of this panel to wire the 3-ways?
Old 08-25-2011, 12:49 PM   #23
" Euro " electrician
frenchelectrican's Avatar
Oui you can with three way switch however there will be a sticky item may come up is you will have no netural connection at the house side due some case you may want to change to timer but with convental three way switch you are fine but just make sure you do NOT steal house's netural conductor at all if you have electrionic timer.
{ note : my SOP is have seperated switch box or have two gang swtich box with divder in there so you know you can not get it mixed up at all }
Merci,
Marc
Old 08-25-2011, 12:50 PM   #24
Code05's Avatar
Hmmm. An argument could be made that the wire feed for the lights could be okay in addition to the feeder.
225.30(D) Different Characteristics. Additional feeders or
branch circuits shall be permitted for different voltages,
frequencies, or phases or for different uses, such as control
of outside lighting from multiple locations.
225.31 Disconnecting Means. Means shall be provided
for disconnecting all ungrounded conductors that supply or
pass through the building or structure.
225.33 Maximum Number of Disconnects.
(A) General. The disconnecting means for each supply
permitted by 225.30 shall consist of not more than six
switches or six circuit breakers mounted in a single enclosure,
in a group of separate enclosures, or in or on a switch-board.
There shall be no more than six disconnects per
supply grouped in any one location.
225.37 Identification. Where a building or structure has
any combination of feeders, branch circuits, or services
passing through it or supplying it, a permanent plaque or
directory shall be installed at each feeder and branch-circuit
disconnect location denoting all other services, feeders, or
branch circuits supplying that building or structure or passing
through that building or structure and the area served by
each.
225.38 Disconnect Construction. Disconnecting means
shall meet the requirements of 225.38(A) through (D).
Exception: For garages and outbuildings on residential
property, snap switches or 3-way or 4-way snap switches shall
be permitted as the disconnecting means.
Old 08-25-2011, 02:05 PM   #25
Rewards Points: 1,588
I didn't think a breaker box could be used as a junction box for splicing wires that pass through and are not being protected for overload?
bob22 is offline   Reply With Quote
Old 08-25-2011, 02:08 PM   #26
Code05's Avatar
312.8 Switch and Overcurrent Device Enclosures with
Splices, Taps, and Feed-Through Conductors. The wiring
space of enclosures for switches or overcurrent devices
shall be permitted for conductors feeding through, spliced,
or tapping off to other enclosures, switches, or overcurrent
devices where all of the following conditions are met:
(1) The total of all conductors installed at any cross section
of the wiring space does not exceed 40 percent of the
cross-sectional area of that space.
(2) The total area of all conductors, splices, and taps installed
at any cross section of the wiring space does not
exceed 75 percent of the cross-sectional area of that
space.
(3) A warning label is applied to the enclosure that identifies
the closest disconnecting means for any feedthrough
conductors
bob22 (08-25-2011)
Copper to Black Pipe Gas Connection dwolek HVAC 1 03-15-2010 05:02 PM
Copper hood - Looking for input steve1234 General DIY Discussions 13 01-04-2010 01:34 PM
Screen/Storm Door Handle Height Steven Z. General DIY Discussions 2 11-22-2009 04:38 PM
copper strap around copper pipe? analogmusicman Plumbing 3 06-04-2008 10:55 AM
Debate - Pex vs Copper sandy2982 Plumbing 13 04-10-2008 10:47 PM