How Long To Trip? Type NC 20A - Electrical - DIY Chatroom Home Improvement Forum
Old 06-27-2010, 05:11 PM   #1
Rewards Points: 97
how long to trip? type NC 20A
does anyone know how quickly (or slowly) a 20 amp FPE type NC breaker will trip when loaded to 22 AMP heating load??
i guess the right answer will be to find the "trip curve" (or characteristics) of this breaker but i could not find anything on the web
i had a kitchen circuit loaded at 22 amp (resistive) (of course, unintentionally) for about 10 minutes, the breaker did not trip. is this normal?
add: i used an amp meter to measure the current draw for each of the 2 appliances that were plugged in in steady-state; the actual total was 22.1
(for those who dislike FPE , telling me to change the panel at this point will not help-- that may come later)
drgkjd is offline   Reply With Quote
Old 06-27-2010, 05:25 PM   #2
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,992
A 20A breaker may never trip at 22A.
Old 06-27-2010, 05:38 PM   #3
Electrician
Rewards Points: 802
It's a Federal Pacific breaker so you probably could load it up to 222A and it wouldn't trip.
darren is offline   Reply With Quote
Old 06-27-2010, 08:25 PM   #4
Licensed electrician
Rewards Points: 1,876
Using the trip curve for a Square D breaker loaded at 100% to 125%, the time to trip was up to several hours.
Old 06-27-2010, 10:31 PM   #5
Rewards Points: 97
thanks....this should not be much different than i would guess. so it seems that 10% over-current can be handled easily for 10 mins and would not cause the breaker to trip in that short a time.
Originally Posted by Jim Port View Post
Using the trip curve for a Square D breaker loaded at 22 amps the time to trip was several hours. It might have even been more than that IIRC.
Old 06-27-2010, 10:40 PM   #6
Rewards Points: 97
hmmmm...interesting....now i got to dig up a comparable trip curve and understand what is the usual overload for quick trip--- other than of course a complete short.
thanks
Old 06-27-2010, 10:44 PM   #7
I loaded up a bunch of C-9 Christmas light strings on a 20a circuit
I think I had 15-16 straings on the circuit
Usually they take 175w each....so at least 1625w on the circuit
I went inside...sat down & started calc'ing the load on the circuit
Realized I had too much....looked out & they were off, breaker had kicked off...maybe 15 minutes Max
The Following User Says Thank You to Scuba_Dave For This Useful Post:
drgkjd (06-28-2010)
Old 06-27-2010, 10:53 PM   #8
" Euro " electrician
frenchelectrican's Avatar
The trip setting will affect by tempture as well like what Pete say 20 amp breaker may not trip at 22 A which I have ran into from time to time and ditto with European verison the same olé story.
but if the breaker box is in basement which I know typically more cooler than on first floor or on very warm spot it may not trip very fast with mild overload at all.
Merci,
Marc
Old 06-28-2010, 03:15 AM   #9
Here is a trip curve for the 15 amp.
http://static.schneider-electric.us/...kers/730-2.pdf
As you can see it can hold 100-125% load for a long time.
Old 06-28-2010, 10:16 PM   #10
Rewards Points: 97
thanks for posting the curve. i am pretty sure the fpe is very similar and at 10% overload it my not trip for several 1000s of second and unlikely in 10 min.
Old 06-28-2010, 10:18 PM   #11
Rewards Points: 97
yes, the panel is in the basement....and as i see on the trip curve posted by jim, 10 min is too short for a 10% overload, specially in the cool basement (about 68deg there).
thanks
Merci,
Marc
Circuit breaker Type Q vs QP orange Electrical 6 12-15-2010 03:35 PM
Breaking up a long/continuous wall tigereye Interior Decorating 4 03-08-2009 03:43 PM
screw type bulbs. mpj111 Electrical 5 01-27-2009 03:27 PM
Need help with Type T and TL fuses? Fotoguy Electrical 6 03-04-2008 01:08 PM
Type L Or M Copper Pipe bobo Plumbing 1 11-20-2005 07:53 PM