Old 05-12-2011, 05:53 PM   #16
Learning by Doing
Leah Frances's Avatar
Manufacturers love to require 'dedicated circuits'. The NEC does not use the term. The NEC talks about "Individual branch circuits" defined as "a branch circuit that supplies only one utilization equipment." In english: A circuit with ONLY ONE appliance plugged into it...ever.
Some inspectors will require that individual branch circuits run to refrigerators have only a single receptacle. This is not specified in the NEC.
The NEC 210.21(B)(1) requires that IF a single rec is used then is must be rated not less than the individual branch circuit rating.
So, with ONE rec on a 15Amp circuit you MUST use a 15 Amp rec.
with ONE rec on a 20Amp circuit you MUST use a 20 Amp rec.
Putting a duplex rec on an 'Individual Branch circuit' does not invalidate it as an 'Individual Branch Circuit". Plugging more than one thing into that duplex rec does.
If I could only remember to THINK about what I was doing before I did it.
Leah Frances is offline   Reply With Quote
The Following 2 Users Say Thank You to Leah Frances For This Useful Post:
davido30093 (05-12-2011), nap (05-12-2011)
Old 05-12-2011, 06:00 PM   #17
Learning by Doing
In my opinion: Manufacturers require so-called 'dedicated circuits' to limit their potential liability when people improperly use high-draw items. Also, in theory, to potentially limit their warranty coverage (BTW, I've never had that problem).... "Oh, your treadmill broke? Did you have it on a 'dedicated circuit'? No. Then we won't warranty it"
Old 05-12-2011, 06:16 PM   #18
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
all right. Have you been studying or did you snark that from somewhere else.
Old 05-12-2011, 06:16 PM   #19
Rewards Points: 83
I am going to have to agree with Leah, the biggest reason for the "dedicated circuit" requirement is to rule out interference to or from other equipment on the same circuit. I would doubt it is necessary to have a dedicated circuit for a treadmill. Just don't plug in other sensitive or power hungry equipment into the same circuit.
That being said your best bet for a dedicated 20amp circuit would be a window A/C unit. You are looking for a plug with a t shape on one side, probably just under a window. Which works out good because who doesn't want to workout in front of a window?
linuxrunner is offline   Reply With Quote
Old 05-12-2011, 06:17 PM   #20
Electrical Contractor
kbsparky's Avatar
Section 210.21(B)(1) allows a 20 Amp single receptacle on a 15 Amp circuit.
20 Amp outlet is not less than 15 Amp circuit ...
This is the same section that allows a single 50 Amp outlet (range) on a 40 Amp circuit.
-KB
Old 05-12-2011, 06:18 PM   #21
Learning by Doing
I've been studying. Mullin's Electrical 2008 NEC edition.
Old 05-12-2011, 06:27 PM   #22
nap
You talking to me?
nap's Avatar
ya did good except the thing kpsparky caught. If you re-read the section, you will realize why:
that states the recep cannot be rated for less than the circuit. They are concerned that you do not overload the recep. The circuit will take care of itself and trip if overloaded. The recep will heat up and...
well, we don't want to go there.
Old 05-12-2011, 06:30 PM   #23
Learning by Doing
NOPE. That is TABLE 210.21(B)(3).
Allows 40 or 50 Amp rec on a 40 amp circuit.
Old 05-12-2011, 06:33 PM   #24
Learning by Doing
Thanks for the complement and I still think I've got Sparky on the 40 or 50 Amp recs on 40 Amp circuits. As per the table.
Old 05-12-2011, 06:43 PM   #25
kbsparky's Avatar
Look again, Leah. Table 210.21(B)(3) is for circuits that have two or more receptacles. I stand by my original post.
-KB
Old 05-12-2011, 06:53 PM   #26
Learning by Doing
YEah, so I'm looking at that.
I'll get back at'cha. I'm not sure I'm right, right. Because, I'm no pro. Just trying to learn.
Old 05-12-2011, 06:55 PM   #27
kbsparky's Avatar
Leah, to maintain our electrical licenses, we are required to have 5 hours of continuing education per year. One of the things that was discussed in detail at one of those courses was this very topic.
Maybe you'd like to attend one such course with us sometime? You'd be surprised at what you might learn .... (of course, they ain't cheap)
-KB
Old 05-12-2011, 08:17 PM   #28
Learning by Doing
Ah, education for education's sake. Sounds awesome. So this is REALLY bugging me and I've got to wrap my mind around it. I totally acknowledge that I both
a) lack the education and experience to be a pro; and
b) am smart enough to admit it
In what situations would you put a SINGLE 40 or 50 rec on a 40amp circuit? what section of the code controls this?
Just had a tiny bit of a family emergency, but I'm not dropping out because I'm not interested. Just busy.
Old 05-12-2011, 08:44 PM   #29
kbsparky's Avatar
...In what situations would you put a SINGLE 40 or 50 rec on a 40amp circuit? ....
I already mentioned this: An electric RANGE. Many of them use a 50 Amp NEMA14-50 receptacle, wired with #8/3 romex, on a 40 Amp breaker.
FWIW, I've never seen any receptacle rated at 40 Amps. The NEMA configuration chart goes from 30 to 50.
-KB
Old 05-12-2011, 09:00 PM   #30
nap
You talking to me?
nap's Avatar
what do ya mean they aren't cheap? Mine are free!! but I only have to take one each time Michigan accepts a new code cycle.
Need a wiring diagram Mooreski Electrical 47 02-01-2015 03:07 PM
open circuit unknown location / voltage leakage fishmanflats Electrical 4 12-23-2009 09:04 PM
Home Theater Dedicated Circuit rjschwar Electrical 20 12-16-2009 12:42 PM
Changing a 3 way circuit...using recessed lighting box as a junction box? Oxymoron Electrical 1 12-07-2009 06:46 PM
Circuit out but circuit breaker didn't trip PaulenAndrew Electrical 17 08-16-2008 08:38 AM