How To Ground A Detached Shed Subpanel ? - Electrical - DIY Chatroom Home Improvement Forum
Old 08-13-2009, 02:36 PM   #1
Rewards Points: 1,062
Question
how to ground a detached shed subpanel ?
to which i am running 50 A from the main panel ? the conduit is buried.
Old 08-13-2009, 03:11 PM   #2
Shed must have 4 wire feed
Neutral & grounds seperated in the sub-panel
Neutral not bonded to the panel
1 or 2 (8') ground rods must be run from the ground buss
If 2 rods they must be at least 6' apart
I used some left-over #4 wire - may not need something that big
Old 08-13-2009, 03:14 PM   #3
Question
does the ground wire coming out of the subpanel need to go outside under the foundation, i.e. not be exposed outside, or can it come outside the shed through a wall and then go under ground, i.e. a piece will be exposed (with conduit, i guess) ? also, how deep does the rod need to be buried ?
Old 08-13-2009, 03:20 PM   #4
My ground wire goes thru the wall & is protected by conduit until underground
Ground rods are 8' long & must be installed 8' deep if possible
Old 08-13-2009, 03:42 PM   #5
does the rod need to be buried horizontal or vertical and, if vertical, how deep should the upper end have to be below grade ?
Old 08-13-2009, 03:58 PM   #6
Electrical Contractor
wirenut1110's Avatar
Rewards Points: 510
Send a message via AIM to wirenut1110
You should drive them straight down but if you encounter rock, you can drive them at an angle not to exceed 45 deg or bury them in a trench at least 30".
They need to be flush with or below the ground level.
Best to use #6, if you use #8 it needs to be protected from physical damage.
wirenut1110 is offline   Reply With Quote
Old 08-13-2009, 04:13 PM   #7
thanks y'all. i think i've got what i need
A few slightly different questions on subpanel wiring. Chris Dopp Electrical 8 06-26-2009 09:45 PM
Detached shed/shop rewire gtmatt Electrical 7 05-24-2008 09:40 AM
running wire to a detached shed subpanel amakarevic Electrical 9 03-27-2008 05:15 PM
Subpanel to Shed - Check my plan NateHanson Electrical 9 04-26-2007 09:56 PM
Subpanel feeder questions Silhanek Electrical 4 03-22-2007 06:30 PM