How To Fix Double Tap At Circuit Breaker - Electrical - DIY Chatroom Home Improvement Forum
Old 05-07-2010, 06:56 PM   #1
How to fix Double tap at Circuit Breaker
Is it acceptable to take the two blacks to a wire nut, a pigtail from the wire nut to the breaker? Is this OK by latest code?
xraydido is offline   Reply With Quote
Old 05-07-2010, 06:59 PM   #2
retired elect/hvac/plumb
plummen's Avatar
Location: south east of omaha/The island of misfit contractors
Rewards Points: 2,020
as long as its done inside of the panel and done neatly ive never had a problem
plummen is offline   Reply With Quote
Old 05-07-2010, 07:42 PM   #3
joed's Avatar
Rewards Points: 13,340
It is also OK on some brands of breakers to put two wires under one screw(double tap).
Old 05-07-2010, 08:31 PM   #4
Inspector/Instructor
codeone's Avatar
Yes this would be code compliant. As noted by another poster some breakers are listed for 2 wires. Two are Square D Homeline and Square D QO breakers.
codeone is offline   Reply With Quote
The Following User Says Thank You to codeone For This Useful Post:
GCRandle (06-12-2010)
Old 05-07-2010, 09:15 PM   #5
Electrician
Rewards Points: 802
hey joed this came up in a different topic not to long ago. Do you know where or if it says in the CEC that we are not allowed to make joints in the panel., the closet I came to an answer was 12-3032.
darren is offline   Reply With Quote
Old 05-07-2010, 10:47 PM   #6
joed's Avatar
I only have an Ontario 1998 code book.
12-3032 would be the section that requires the divider for the mains from the branch circuits.
12-3034 states that enclosures for over current devices, controllers and externally operated switches shall not be used as junction boxes, troughs or raceways for conductors feeding through to other apparatus
Old 05-08-2010, 09:44 AM   #7
Sparkaholic
Rewards Points: 150
Send a message via Yahoo to sparks1up
[/QUOTE]12-3034 states that enclosures for over current devices, controllers and externally operated switches shall not be used as junction boxes, troughs or raceways for conductors feeding through to other apparatus[/QUOTE]
Don't misinterpret that to mean you can't make a splice in the panel! It is perfectly acceptable to splice 2 wires together in a panel so long as you are terminating them on a breaker.
What is NOT ok is to make a splice that is coming and going through the panel but not connected to a breaker. That would be using the panel as a raceway or a junction box!
sparks1up is offline   Reply With Quote
Old 05-08-2010, 01:55 PM   #8
Electrician
Rewards Points: 802
I know in the USA it is fine but i have heard from more then one source that they are not allowed in panels. Remember were talking about CEC not the NEC.
Old 05-08-2010, 02:15 PM   #9
I've been retired since 1995 and things may have changed in that time, but before that time, connections within the panel were considered to be the best place to make these connections.
The only other choice would be to terminate the two cables in a junction box and then run a feed to the panel! In all my years, I have never seen this done!
As previously noted, circuits that do not terminate in the panel are not allowed and should be joined in an external junction box!
Old 05-08-2010, 02:36 PM   #10
Sparkaholic
Rewards Points: 150
Read this quote posted by the OP out of his CEC handbook
Originally Posted by 12-3034 states that enclosures for over current devices, controllers and externally operated switches shall not be used as junction boxes, troughs or raceways for conductors [B
feeding through to other apparatus[/B]
It clearly says "for conductors feeding through to other apparatus"! That means you can't pass through the panel. If you are splicing to go to a breaker you are NOT passing through you are terminating.
20A Circuit Breaker, 30A dryer, is it OK? ninghai Electrical 36 01-03-2010 03:11 PM
Replacing a circuit breaker tertius Electrical 9 09-24-2009 08:17 PM
Circuit out but circuit breaker didn't trip PaulenAndrew Electrical 17 08-16-2008 08:38 AM
Dead circuit - Breaker not tripped Anne Electrical 2 08-09-2008 03:29 PM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM