How To Figure Load On A Circuit - Electrical - DIY Chatroom Home Improvement Forum
Old 05-15-2013, 11:32 AM   #1
Rewards Points: 664
How to figure load on a circuit
This forum is great, but I need to have some ready information I can apply immediately. I recently asked if I could add a sump pump to a 20 amp circuit that already had a garbage disposal and a dishwasher on it. How do I go about figuring that out? Do I just add up the amps written on the dishwasher and garbage disposal and see if they exceed 20? The garbage disposal certainly is not used continually, although it could be used simultaneously with the dishwasher and sump pump. Isnít that a factor?
Yes, I know code may govern certain things, but I like to know the math involved here. Thank you for any help to my understanding.
crescere is offline   Reply With Quote
Old 05-15-2013, 11:38 AM   #2
Licensed electrician
Rewards Points: 1,758
In your case the appliances already in place are typically dedicated or the instructions call for an individual circuit. Even if the appliance only draws 1 amp but the instructions called for an individual circuit it could not be shared.
There are also different rules depending on whether the equipment is cord and plug connected or hard-wired.
Old 05-15-2013, 11:43 AM   #3
JOATMON
ddawg16's Avatar
Rewards Points: 1,958
Jim covered it pretty good.
Basically, your will most likely have issues if your try that. The problem is that the chances of needing the sump pump are directly related to the probability that the dishwasher is going and your wife wants to run the disposal.....and water is filling up fast in the sump....
A sump pump should really have it's own ckt.
Old 05-15-2013, 12:13 PM   #4
Rewards Points: 664
Yes, I understand that over all, but what math did you or the code writers do to get there? How is it done?
What if I took away the garbage disposal? How does the math change? Thank you for your time.
Old 05-15-2013, 12:30 PM   #5
Electrical Contractor
Philly Master's Avatar
Rewards Points: 516
For now look at,the name plates of all the 3 appliances...what do you have in watts or amps..
Philadelphia Master Electrician-Generac Dealer
Philly Master is offline   Reply With Quote
Old 05-15-2013, 04:39 PM   #6
Rewards Points: 664
I am not at the house now, and when I am I do not have a fancy internet phone to post here. Again, I assume I just add up the amps to see if they exceed 20? Or is there some other maximum like 80%? The thing is though that the garbage disposal is certainly intermittent. No one leaves theirs on for more than a few minutes.
Old 05-15-2013, 05:47 PM   #7
Rewards Points: 150
you have three motors so find the largest motor and it is figured at %125 then add the other two motors.
usair is offline   Reply With Quote
Old 05-15-2013, 05:50 PM   #8
DIY staff
Rewards Points: 7,174
Can your breaker box use mini twin breakers? If it can you have and option----
Old 05-15-2013, 05:53 PM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,226
Where did you pull that formula from? The circuits he wants to share are dedicated for their existing use and cannot be shared regardless of the load
Coastal South Carolina
rjniles is offline   Reply With Quote
The Following User Says Thank You to rjniles For This Useful Post:
Jim Port (05-15-2013)
Old 05-15-2013, 06:16 PM   #10
Rewards Points: 150
430.53 Several Motors or Loads on One Branch Circuit.
Two or more motors or one or more motors and other loads shall be permitted to be connected to the same branch circuit under conditions specified in 430.53(D) and in 430.53(A), (B), or (C).
now where did you pull yours from?
Old 05-15-2013, 06:17 PM   #11
JW
mm11's Avatar
Rewards Points: 620
430.24- Several Motors or Motor(s) and Other Loads
usair paraphrased this section
mm11 is offline   Reply With Quote
Old 05-15-2013, 06:28 PM   #12
Remodel and New Build GC
MTN REMODEL LLC's Avatar
Rewards Points: 3,348
That's just begging for a good response
MTN REMODEL LLC is offline   Reply With Quote
Old 05-15-2013, 06:41 PM   #13
Rewards Points: 744
You still can't share a DEDICATED circuit.
..And it's in section 210....
Seattle2k is offline   Reply With Quote
The Following User Says Thank You to Seattle2k For This Useful Post:
rjniles (05-15-2013)
Old 05-15-2013, 07:04 PM   #14
Isn't the OP really asking here what's safe.... (I know code tells us what is safe... and I know safe is a subjective /relative opinion)
But I don't think any one of his loads is continuous (over 3 hours). A dishwasher at probably 10A (when drying), a GD at maybe 2A (and momentary) and a sump at 3-4-5A (intermittant) seems well under 20.
Not saying what to do.... just saying
Old 05-15-2013, 07:04 PM   #15
Rewards Points: 516
430 does not apply here ...
The Following User Says Thank You to Philly Master For This Useful Post:
Garage light circuit issue Uncle Ben Electrical 15 03-02-2012 01:00 PM
Dispute: Oven malfunction after h/w guys used the circuit rational Appliances 18 05-17-2011 10:37 PM
Just for fun Andy in ATL Electrical 56 10-20-2009 09:33 AM
Can this circuit handle the load seahawk2000 Electrical 8 01-05-2009 08:12 PM