How Does A Double Pole Circuit Breaker Trip? - Electrical - DIY Chatroom Home Improvement Forum
Old 07-09-2008, 12:13 PM   #1
On my electrical service panel, the "MAIN" breaker is a double pole breaker and each side is marked "100 Amps." Does that mean that when the total amperage exceed 100 one side it will trip, or if the total of both sides exceed 100 amps it will trip? So do can all my appliances together draw up to 200 amps, or just 100 amps? Also, I recently bought a new electric range. I need a double pole breaker because it uses 240 volts, and the total consumption of the range should not exceed 40 amps. Should I get a double pole breaker with 20 amps marked on each side (the whole thing is marked 20 amp double pole breaker) or should I get one with 40 amps marked on each side (the whole thing is marked 40 amp double pole breaker)?
shadowx360 is offline   Reply With Quote
Old 07-09-2008, 01:54 PM   #2
If current exceeds 100A through either leg of the 220V line, both sides will trip together.
So, you can draw up to 100A on each side, and that current can be a combination of 110V appliances on one leg, or 220V appliance on both legs.
Both poles of a double pole breaker will always trip together if current through either leg exceeds the rating.
For your range, if the specs are 40A at 220V, you need a 40 Amp double-pole breaker.
Hope this helps
FW
fw2007 is offline   Reply With Quote
Old 07-09-2008, 02:44 PM   #3
Licensed Electrician
jrclen's Avatar
Rewards Points: 514
A double pole breaker is the same as two single pole breakers connected together. So your 100amp 2 pole is 2 100 amp breakers side by side. If either side conducts more than 100 amps the entire unit will trip or open. Both sides will shut off together
That breaker can supply 100 amps of current at 240 volts. It can supply 200 amps of current at 120 volts. Or any combination of the two as long as neither one exceeds 100 amps.
If your range requires a 40 amp 240 volt circuit, then each side of the 2 pole breaker will be 40 amps.
A home type electrical service consists of 2 legs of power at opposite polarity. Between the 2 legs there is 240 volts of electricity. Between each leg and the service neutral conductor, there is 120 volts of electricity.
If you have any questions, just ask away.
John
jrclen is offline   Reply With Quote
Double pole CH breaker ?? James Con Electrical 7 07-09-2008 11:41 PM
Three way light switches and double pole breaker ShawnColes Electrical 6 04-15-2008 08:25 PM
Novice Replacing 60 amp double pole breaker Ayreonna Electrical 40 02-19-2008 01:26 AM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM
Problem with circuit breaker. HELP! spartanic Electrical 2 10-28-2007 03:09 PM