Old 11-23-2012, 05:17 PM   #1
How do I know if my load center is single phase?
Finishing the basement and I need some more circuits. My load center is a square-d homc30uc. Best I've been able to tell is that this puppy will not accept tandem breakers. I figured no problem I'm put in a sub panel while it's all open. The sub panel I purchased does however accept tandem breakers. I was thinking about purchasing some of these for the sub panel just to leave a little bit of breathing room.
However on the instructions it indicated that my load center must be single phase. How can I determine this?
nateo is offline   Reply With Quote
Old 11-23-2012, 05:43 PM   #2
If this is a residential service you almost certainly have single phase. You can tell by the service drop at the weather head. Single phase will have two hot conductors and a neutral. Three phase would add an additional hot conductor.
teamo is offline   Reply With Quote
Old 11-23-2012, 05:48 PM   #3
It would be a big help if you went back and added where you live to your profile!
In the US it's rare to ever see 3 phase in anything but an industrial setting.
Old 11-23-2012, 05:48 PM   #4
Missouri Bound's Avatar
Since that is a residential panel it would be very unlikely for it to be other than single phase. As teamo suggested look at the service drop. If it's underground you can pull the cover off the panel.
Do you want it your way or the right way?
Old 11-23-2012, 08:55 PM   #5
JOATMON
ddawg16's Avatar
Look at the wire coming into your house....if you have 3 wires up there...chances are it's single phase.
As the other guys have noted....3 phase is really rare for residental....
Some people do get confused when talking about 120 vs 240....some seem to think that 240 Vac is 2 phase....mainly because the 2 120Vac phases are 180 deg our of phase with each other.
Common Sense is like Deodorant. Those that need it the most don't use it.
My
and
Old 11-24-2012, 07:39 AM   #6
Perhaps we might ask, what difference would it make whether the upstream panel is single phase or 3 phase?
Would it just be an all inclusive cover all sentence to avoid having the high leg of a 120/240 volt delta 3 phase
system fed into the single phase subpanel by mistake?
It's not common but apartments in a commercial building (such as apartments above a store) can have two
phases of a 3 phase symmetric neutral (wye) system fed into a standard single phase panel. The outward
appearance would be that of a single phase panel. The voltage would be 208 volts hot leg to hot leg and
120 volts hot leg to neutral.
Single wide double breakers take power from just one leg or phase so it would not make a difference whether
they were used in a 3 phase panel or system.
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
Old 11-24-2012, 10:31 AM   #7
Electrical Contractor
Since this is a homeline panel, it is a single phase, but like Allan said, why does it matter?
Yes I am a Pirate, 200 years too late. "Jimmy Buffett"
Old 11-24-2012, 12:45 PM   #8
Look at how many hots are connected to the panel. 2 = single phase, 3 = 3 phase.
Single phase...
3 phase...
Billy_Bob is offline   Reply With Quote
The Following User Says Thank You to Billy_Bob For This Useful Post:
Kpack (11-24-2012)
Old 11-24-2012, 12:50 PM   #9
Single phase service from electric company. 1 transformer on pole and 3 wires coming to building...
3 phase service from the electric company. 3 transformers on pole and 4 wires coming to building...
Old 11-24-2012, 08:17 PM   #10
And if you have 4 or 5 hot wires, it could be two-phase. If you live on Cape Cod, you may see this type of installation in many older hardware stores, used to run old motors. There are also industrial systems with as many as 20 phases!
neo565 is offline   Reply With Quote
Old 11-24-2012, 08:55 PM   #11
Do any power companies deliver 2 phase or 20 phase, or are these sources synthesized on site from a 3 phase
or even a single phase service?
Old 11-24-2012, 08:59 PM   #12
Billy Bob....is that some of your work? If so....
Very nice job.
Old 11-24-2012, 09:57 PM   #13
Power Gen/RS Engineer
Umm.....what???
Number of cables does not equal number of phases. US, Canada, Bangkok. 20 phases makes zero sense.
As Dave Chappelle once said, "I tried to tell him that it was a bad idea but I was high!"
The very existence of flamethrowers proves that some time, somewhere, someone said to themselves,"You know, I want to set those people over there on fire, but I'm just not close enough to get the job done." - George Carlin
BigJimmy is offline   Reply With Quote
Old 11-25-2012, 12:54 AM   #14
" Euro " electrician
frenchelectrican's Avatar
Originally Posted by AllanJ View Post
Do any power companies deliver 2 phase or 20 phase, or are these sources synthesized on site from a 3 phase or even a single phase service?
The old school true 2 phase service is pretty much gone the only way you can get 2 phase power is run a scott-tee transfomer set up this is the closest you can get to the 2 phase supply set up but not widesperead useally found on older elevatour motor which it is common.
20 Phases ?? the answer is NO more like mulit conductor per phase so with very large service drop so it can spread the load over more conductors the last large service I have done 3600 amp yeah not a misprint a European veison of 3500 amp service which they will take 18 yeah .,, 18 conductors per phase.
Merci,
Marc
Old 11-25-2012, 01:28 PM   #15
Very nice job.
Not quite! My work is more messy.
Also I'll start it out looking somewhat nice, then need to add in something I forgot, then there goes the "nice looking" panel!
(I just grabbed those images off google.com / Images.)
Need Square D Load Center cover? dejola Electrical 6 11-05-2012 07:52 PM
Expanding load center capacity in barn mn1247 Electrical 8 09-13-2011 09:24 AM
Help 30 amp Load center for my HID lights and miscellaneous Mont@n@ Electrical 9 03-06-2010 12:49 PM
Flush mount an outdoor load center? wmldwilly Electrical 1 04-29-2009 08:17 PM
Load center vs. bottom fed Panel Board. Ugh. wmldwilly Electrical 8 04-23-2009 08:48 PM