Old 12-07-2012, 07:51 PM   #16
Lic Electrical Inspector
electures's Avatar
How do I connect a ground wire to the water pipe?
This type of meter requires the jumper.
This type of meter does not require a jumper because removal will not interupt the bonding path.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 12-07-2012, 08:04 PM   #17
Originally Posted by Quackerjack View Post
Thanks. But if the ground is connected on the city side of the meter, what difference would it make if the meter were ever removed?
With the grounding electrode conductor properly clamped to the city side of the meter, problems with neighboring houses' electrical systems won't affect removal of your meter. But a ground fault to a water pipe upstairs in your house could electrocute someone disconnecting the meter if there was no bonding jumper around the meter..
The disadvantages of crab apple trees. In summer, the apples are too sour to pick and eat. In winter the birds come and leave dropping all over the place.
The Following User Says Thank You to AllanJ For This Useful Post:
electures (12-07-2012)
Old 12-07-2012, 08:12 PM   #18
TTW
TTW's Avatar
""" This type of meter does not require a jumper because removal will not interupt the bonding path. """
Uh, that last meter happens to be the one in my basement, it's a photo I posted earlier today. There are two unions there. If you unscrew the 2 unions and pull out the meter assembly the only thing connecting the piping is air. Last I knew air is not a good conductor.
#1 - If you don't know what you're doing - get a licensed electrician!
#2 - If you follow my advice and something bad happens see # 1
Electricity bites hard, and it could be the last thing you feel... Good Luck!
TTW is offline   Reply With Quote
Old 12-08-2012, 12:14 PM   #19
electures's Avatar
The meter is removed by taking apart the unions on either side of the meter. Not the connections (which may be soldered) above and below the meter yoke. Removal of the meter does not interupt the grounding electrode path. Removal of the yoke will interupt the GEC path. I have the same yoke.
I should clarify that if the connections for the yoke are soldered, I do not require the bonding jumper because the fittings cannot easilly be disassembled. If the fitttings for the yolk are not soldered then I require the bonding jumper. Either way removal of the water meter will not break the GEC path.
Here is a better picture of the yoke;
Removal of this meter will not interupt the GEC path and if the yoke connections are soldered, no jumper is required.
Sizing motors
Tags
ground wire, water pipe
What’s the best way to remove pipe from T Jaylyn Plumbing 2 02-03-2011 02:05 AM
Basement drain pipe "pit" ground water fix. alecmcmahon General Discussion 13 12-01-2010 06:42 AM
Kitchen Sink Moved - new kitchen sleepysmurf Plumbing 1 08-10-2010 07:38 AM
A blocked water line causing water to loose heat? Snav Plumbing 6 05-07-2010 03:18 PM
hooking up dryer....bronx ny code SURFBUG Appliances 6 10-14-2008 10:41 PM