How To Determine Wire Size? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-06-2010, 11:18 AM   #1
Just call me Andrew
Rewards Points: 1,020
How to determine wire size?
A couple NEC questions....
How do you determine what size EGC is needed? I know it can be smaller than the Current Carrying Conductors, but is there a chart somewhere?
I knew this at some point (and it should be added to the "national electric code" sticky). Which columns are used for NM-B and THWN in conduit?
THHN and THWN are in different columns, but most wire is rated for both...
Andrew
secutanudu is offline   Reply With Quote
Old 10-06-2010, 01:49 PM   #2
nap
You talking to me?
nap's Avatar
Rewards Points: 6,290
yes, there is. It is in the NEC along with all the rest of the numbers.
table 250.122
100 am/ #8
200 amp/ #6
400 amp/ #3
NM is limited to the 60 rated column unless you are calculating derating. Then you can use the 90 column for the calculations BUT the final ampacity still cannot exceed the 60 rating.
it depends if you are using it as THHN or THWN but (without a long explanation as to why) just stick with the 75 rating for either.
the right one. For most uses, that would be 310.16.
The Following User Says Thank You to nap For This Useful Post:
secutanudu (10-06-2010)
Old 10-06-2010, 03:43 PM   #3
Licensed electrician
Rewards Points: 1,872
If you are using the wire in a wet environment you would use the 60 degree column. Dry locations you can use the 75 degree column.
Old 10-06-2010, 07:36 PM   #4
nap
You talking to me?
nap's Avatar
actually, THWN is rated for 75 and THHN is rated for 90. There is no 60 rating to be concerned with at all. (for thwn or thhn)
Old 10-06-2010, 08:35 PM   #5
Just call me Andrew
Maybe a mod could add this to the NEC sticky...
Andrew
Size and type of entrance wire for 200A? Beemer533 Electrical 7 03-15-2010 10:54 PM
HALP! Master/Remote Dimmer troubles! Confuserated Electrical 9 02-12-2010 03:30 PM
Size of Wire & type of wire agman Electrical 6 11-10-2009 08:13 PM
What size wire do I have? 737Pilot Electrical 4 10-09-2008 09:47 PM
Wire size and Breaker size for remodel ?? Skydmark1 Electrical 12 12-15-2007 05:00 PM