Old 09-27-2012, 10:23 PM   #1
how deep should PVC conduit be in slab?
OK in preparation for the kitchen island - I'm cutting a channel into the slab to run electric (about 2' from the wall)- I cut down about 2.5" and about 3.5" wide in the concrete - I rented a power chisel. To go deeper seems to really be a challenge- Can I lay the PVC in and cover with concrete from here? What determines the depth that it needs to be? I can't see weight being an issue- Once the concrete hardens around the PVC and the floor gets installed.....thoughts? suggestions?
skinut2234 is offline   Reply With Quote
Old 09-27-2012, 10:37 PM   #2
Licensed Electrician
jrclen's Avatar
The National Electric Code determines this. Table 300.5 note 2 requires the conduit to be surrounded by 2" of concrete. What size conduit are you using?
John
jrclen is offline   Reply With Quote
Old 09-27-2012, 10:45 PM   #3
3/4" PVC Conduit
Old 09-27-2012, 10:49 PM   #4
Lic Electrical Inspector
electures's Avatar
The NEC does not require the conduit to be surrounded by 2" of concrete. It can be laid on the soil and concreted over.
All responses based on the 2011 NEC.
If you live in New Jersey click
. All other states click
Please check with local, county and state officials as laws may vary.
Sizing motors
. Online motor calculator
. Online calculators
electures is offline   Reply With Quote
Old 09-27-2012, 11:05 PM   #5
It needs to be covered by 2" of concrete
Gac66610 is offline   Reply With Quote
Old 09-27-2012, 11:13 PM   #6
Semi-Pro Electro-Geek
The standard approach to solving this problem is to cut all the way through the slab with a saw, and lay the conduit under the slab. It is easier than making a shallower channel. Chiseling a channel through concrete is REALLY HARD as you discovered, but making two sawcuts through the slab a few inches apart is really easy. You still need a rotohammer or small jackhammer to break up and remove the pieces, but it's about a 30 minute job with the right tools, rather than all day with a rotohammer trying to chisel 3" deep groove in the slab.
mpoulton is offline   Reply With Quote
The Following User Says Thank You to mpoulton For This Useful Post:
AndyGump (09-28-2012)
Old 09-27-2012, 11:14 PM   #7
electures's Avatar
No. Since it is under the building it can be 0" deep. It is covered by the thickness of the slab.
Sizing motors
Old 09-27-2012, 11:49 PM   #8
Licensed electrician
Could you cite the NEC rule for this?
The Following 2 Users Say Thank You to Jim Port For This Useful Post:
electures (09-28-2012), mpoulton (09-28-2012)
Old 09-28-2012, 07:11 AM   #9
Table 300.5, Notes
Old 09-28-2012, 07:57 AM   #10
electures's Avatar
Table 300.5, Notes
If you are refering to Note 2, it states;
2. Raceways approved for burial only where concrete encased shall require concrete envelope not less than 50 mm (2 in.) thick.
PVC does not require concrete encasement and is "Listed for direct burial without concrete encasement", therefore Note 2 does not apply. Refering to Table 300.5, Row 3, labeled "Under a building", Column 3, the required depth is 0". The OP just needs to break through the slab and lay the PVC on top of the dirt. Then concrete over the pipe. Done.
Sizing motors
The Following User Says Thank You to electures For This Useful Post:
Code05 (09-28-2012)
Old 09-28-2012, 08:19 AM   #11
Code05's Avatar
300.5, Note 2 is referring to conduit like EB20 - not PVC 40 or 80.
Code05 is offline   Reply With Quote
Old 09-28-2012, 09:01 AM   #12
let me clarify- I don't know how thick the slab is- It's not a new house- it's an existing house built in the mid 70's in NJ. I was going with the channel since after chiseling down 2" or so- It's getting really hard to go any deeper and I thought by going down 2" and then laying the PVC in the slab- I could cover it back up with high strength concrete. Won't that keep the PVC well secured?
Old 09-28-2012, 09:30 AM   #13
jrclen's Avatar
Can you cite something on this? I really would like to know. I have laid PVC in concrete channels cut in slabs and was required to cover the conduit with 2" of concrete. Evidently some slabs are not allowed to be cut through. But that's completely out of my field so I may well be wrong about this.
John
Old 09-28-2012, 10:28 AM   #14
That would be tensioned concrete. They have steel cables running through them keeping tension on the concrete. If one gets cut, the concrete can lose some of its strength.
herdfan is offline   Reply With Quote
The Following User Says Thank You to herdfan For This Useful Post:
jrclen (09-28-2012)
Old 09-28-2012, 12:13 PM   #15
So you (a long with others) are saying that PVC can not be used in concrete?
I read Notes 2, and 5, both say minimum of 2" concrete, so how would a slab be any different?
Building Floating Deck over ground and Concrete slab jagnew Building & Construction 2 05-27-2012 01:10 PM
Pier on slab cer2012 Building & Construction 0 04-16-2012 09:52 PM
Slab leak or not? loveyolife Plumbing 11 04-01-2012 02:25 AM
What conduit should I use? mulltron Electrical 6 07-12-2011 02:34 AM
Extending Concrete Patio Slab bobo Building & Construction 6 04-17-2008 01:17 PM