How To Connect 1/0 Aluminum To 70A Breaker? - Electrical - DIY Chatroom Home Improvement Forum
Old 10-09-2012, 04:49 PM   #1
How to Connect 1/0 Aluminum to 70A Breaker?
How do you connect a 1/0 aluminum feeder cable to a Homeline - HOM270 breaker? The SPEC sheet for the HOM270 shows this breaker is designed for #8-2 AWG... so is there an adapter available that allows a 1/0 to connect to this breaker?
In case you're wondering... the reason I'm connecting a 1/0 to a 70 amp breaker is to compensate for the voltage drop which occurs on a 250 ft. feeder (between the service panel at the house) to the outbuilding sub-panel.
CMA = K x I x L x 2/7.2 = 21.2 x 70 x 250 x 2 / 7.2 = 103,056 CMA... and a 1/0 is 105,600... so this is the proper cable to get 70 amps to a sub-panel 250 feet away. I considered using copper, but due to budgeting issues, aluminum was the only realistic choice at this time.
Thanks for your help!
infoseek is offline   Reply With Quote
Old 10-09-2012, 05:44 PM   #2
Master Electrician
Easy answer is that you don't connect it to that breaker.
Sarcasm is my friend
I'm here to learn too, i do mostly commercial/industrial/new construction and this place is a great way to pick up tips on residential from some good electrical minds. Excuse the spelling, my phone has a mind of it's own.
andrew79 is offline   Reply With Quote
Old 10-09-2012, 05:55 PM   #3
Semi-Pro Electro-Geek
Rewards Points: 2,970
You connect a smaller conductor to the breaker, and then use appropriate connectors (like split bolts) to transition to the larger conductor. You can do the transition inside the panel, so you only need a foot or so of smaller wire.
I am a lawyer, but not your lawyer. And who cares anyways? We're here to talk construction. This is DIY advice, not legal advice.
mpoulton is offline   Reply With Quote
Old 10-09-2012, 07:42 PM   #4
Think I may have figured out the problem... I was using 7.2 in my calculation because an electrician told me this is the number he always uses when calculating CMA. But upon reading an article online I see that Max Voltage Drop is dependent on the circuit voltage (which in my case is 240v) and the max allowable voltage drop (Ed) is 5%... which equals 12v for a 240v feeder circuit. Therefore by code I am allowed to use a 100A breaker on a 1/0 feeder circuit which is 250 feet in length.
CMA = K x I x L x 2 / Max Ed
21.2 x 100 x 250 x 2 / 12 = 88,333 CMA = 1/0
The problem (having to use a 70A breaker) is eliminated because a 100A breaker will accept wire from #4 to 2/0... and I have a 1/0 cable!
That is... unless I'm supposed to be taking 5% of 120v (6v) which changes everything.
So this Max Ed is truly the key.
Does anyone know if I'm supposed to take 5% of 120v or 5% of 240v?
Thanks for your feedback!
Old 10-09-2012, 07:46 PM   #5
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
There is no code in the NEC limiting voltage drop to less than any percent.
The Following User Says Thank You to k_buz For This Useful Post:
stickboy1375 (10-10-2012)
Old 10-09-2012, 10:11 PM   #6
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
I admire your interest in learning the calculations ... it is beneficial to know how it is done .. BTW you use 240 volts not 120. Also there is much to know to provide a code compliant installation ... it is more than just running the correct size wire.
In the future try this ......
http://www.electrician2.com/calculat...alculator.html
Added new breaker, no garage lights now. lum1nes Electrical 8 08-04-2012 07:50 PM
breaker keeps tripping RMCarner Electrical 29 07-22-2012 09:53 AM
Separate 110 and 220 receptacles on 2-pole 220 V Square D GFI breaker sunrise Electrical 1 05-13-2012 07:27 PM
Wiring Size Calculations for New Service CorinthWest Electrical 7 12-07-2010 11:36 AM
Circuit breaker panel - Advice needed justtired Electrical 15 12-13-2007 05:55 AM