Forums | Home Repair | Home Improvement | Painting | Interior Decorating | Remodeling | Landscaping
Old 02-25-2014, 06:06 PM   #1
Share |
Hot Wires Even After Breaker Removal
Hello,
Does anyone know of a wiring configuration with a central air conditioning unit where there would remain AC power in the wires to a breaker AFTER that switch was turned OFF and REMOVED? Here is the rest of the story...
I was doing some work in my panel and moving a few breakers around. My (geothermal) air conditioning system has two 40 amp double-pole breakers. When I turned off and removed one of the breakers, the attached wires were still HOT! Only turning off the other double-pole breaker defeated all power in the four involved wires. The same is true visa versa. I also noticed that these two breakers have no neutral wires inside the main panel, but do have ground.
Wow, good that I am obsessive about double-checking for power with my AC sensor! So, I am rather confused as to why there would be such a configuration. The air conditioning system was recently installed and has worked flawlessly even through it's first maintenance inspection, so I can only assume that this is the correct wiring (in series?).
Peace,
Dr. Z.
Zeigh is offline   Reply With Quote
Old 02-25-2014, 06:27 PM   #2
Licensed Electrician
k_buz's Avatar
It would help if you post the make and model of the unit.
It's obvious the wires are interconnected somewhere. It is possible that the unit required an 80A circuit and they illegally paralleled two 40A breakers to accomplish this.
When a government creates a subsidy for these green energies, the hacks come out of the woodwork. Was a permit pulled for this system?
The Following 2 Users Say Thank You to k_buz For This Useful Post:
gregzoll (02-26-2014), mpoulton (02-26-2014)
Old 02-25-2014, 07:08 PM   #3
If you used a non- contact voltage detector, you are picking up induced voltage from the live circuit.
bobelectric is offline   Reply With Quote
Old 02-25-2014, 07:41 PM   #4
What type of meter were you utilizing?
What was the voltage measured? As noted above it is possible you had phantom/ghost voltage.
http://support.fluke.com/find-sales/...105317_A_w.pdf
Know A Little is online now   Reply With Quote
Old 02-26-2014, 09:37 AM   #5
UPDATE:
I was finally able to contact the technician who installed my geothermal air conditioning system and discovered that the wiring is correct (as well as to code). The WaterFurnace equipment handles this electric feed configuration internally.
Once again, here is a reminder to all in double-checking for the presence of electricity even though the power was shut off and/or the breaker pulled. I am not a professional electrician, but have done many rewiring projects in various homes over the years and this is the first time I have been presented with this kind of situation. Another person may have logically assumed that there was no way power could still be flowing in a removed breaker/wires and gotten all their hair standing on end!
Be safe (and obsessive with that AC sensor),
Dr. Z.
Old 02-26-2014, 10:21 AM   #6
Retired from the grind
gregzoll's Avatar
So the lesson is to not answer anyone's question about what equipment you were using to test for voltage, nor reply if there was improper wiring. Just something that all of us that have been around playing with electricity for a long time, something that we already know.
: Now listen, Cadet. I've got a job for you. See this button?
: Don't touch it! It's the History Eraser button, you fool!
: So what'll happen?
: That's just it. We don't know. Maybe something bad, maybe something good. I guess we'll never know, 'cause you're going to guard it. You won't touch it, will you?
Old 02-26-2014, 10:36 AM   #7
k_buz's Avatar
Originally Posted by Zeigh
UPDATE: I was finally able to contact the technician who installed my geothermal air conditioning system and discovered that the wiring is correct (as well as to code). The WaterFurnace equipment handles this electric feed configuration internally.
And you are going to believe that is normal that one circuit to backfeed to another. It is not normal.
The Following 3 Users Say Thank You to k_buz For This Useful Post:
gregzoll (02-26-2014), jbfan (02-26-2014), mpoulton (02-26-2014)
Old 02-26-2014, 10:36 AM   #8
It apparently matters to some, so here is the requested information:
- Fluke 2AC/90-1000V VoltAlert AC Non-Contact Voltage Tester
- Fluke T5-1000 Voltage/Continuity/Current Tester
- WaterFurnace 5 Series, model 500A11 (correctly wired)
Like with many lessons of life, they are often reminders of how best to navigate the journey. If you don't need the information, great. Maybe someone else does and it can save them allot of trouble. Isn't that what an online forum is all about?
Peace,
Dr. Z.
Old 02-26-2014, 10:42 AM   #9
k_buz's Avatar
If you truly measured voltage with the T5, you really need to get someone else out there to verify the wiring is correct. You keep stating the wiring is correct, but you are taking the word of the installer.
gregzoll (02-26-2014), mpoulton (02-26-2014), Msradell (02-26-2014)
Old 02-26-2014, 10:46 AM   #10
Wow, tough crowd...
http://www.waterfurnace.com/literatu...s/IM2500AN.pdf
Old 02-26-2014, 10:59 AM   #11
What does that tell us? There is no way back-feeding a circuit is correct, and your pdf is nowhere pertinent to that.
Anti-wingnut is online now   Reply With Quote
The Following 3 Users Say Thank You to Anti-wingnut For This Useful Post:
Old 02-26-2014, 11:07 AM   #12
Hey, I'm not young enough to know everything (Tibetan proverb), which is why I am here. Assuming that everyone is here to help, doesn't the diagram on page 47 of the PDF show the configuration debated?
Old 02-26-2014, 11:17 AM   #13
Shows no connection between the parallel circuits
The Following User Says Thank You to Anti-wingnut For This Useful Post:
Old 02-26-2014, 11:40 AM   #14
The schematic in the lower right hand corner of page 47 is interesting...
IslandGuy is offline   Reply With Quote
The Following 2 Users Say Thank You to IslandGuy For This Useful Post:
Old 02-26-2014, 11:44 AM   #15
But that's not applicable. That's for Canada where instead of two parallel 30A (or whatever) circuits, they require a single disconnect of 60A. The OP was clear that this is a two circuit system, so that detail is not used.
Are lug's code compliant on this DIY 175A breaker panel? Needed for 10KW PV system superduper Electrical 23 09-09-2012 12:13 PM
Two Wires on Breaker Perry401 Electrical 9 05-18-2011 04:44 PM
GFCI Breaker Tripping Spa Light eaposition Electrical 21 09-08-2010 09:57 PM
Breaker box wiring question(s) janralix Electrical 6 08-29-2010 10:13 PM
Breaker Tripping Jeridmar6 Electrical 15 07-10-2010 08:20 PM