Hot Water Heater Breaker???? - Electrical - Page 2 - DIY Chatroom Home Improvement Forum
Old 12-19-2008, 01:08 PM   #16
UAW SKILLED TRADES
Stubbie's Avatar
Rewards Points: 2,652
Originally Posted by Gigs View Post
The wire size of the circuit feeding it determines the breaker amps, not the water heater itself. Come on guys.
Nope not for a 240 volt water heater.... by your analysis a 4500 watt hot water heater less than 120 gallons would be serviced by 12 awg copper conductors and a 20 amp breaker. Not all equipment is subject to a breaker equaling the wire size ampacity. So you cannot make a blanket statement of that nature. In this case you need to know the characteristics of the load and the appliance type. If he was looking a 12 AWG romax and a 20 amp breaker he would think everything is fine, when it is not.
4500 watts at 240 volts is 18.75 amps so if he had 12 awg copper on an individual circuit under your analysis he would be fine but the appliance requires 25 amp conductors minimum and either 25 amp breaker or a 30 on 10 awg copper.
Old 12-19-2008, 01:35 PM   #17
Res Ipsa Loquitur
Originally Posted by thekctermite View Post
Then it is doing its job!
Hey KC, better watch out- You might recall the last time (in Nov) I made a statement like that the post went on forever!
Did you ever stop to think, then forget to start again?
handyman78 is offline   Reply With Quote
Old 12-19-2008, 03:44 PM   #18
Registered User
Termite's Avatar
Nah, no need for me to step lightly around that statement. If the breaker is tripping, it is reasonably safe to say it is doing its job.
Old 12-19-2008, 05:55 PM   #19
Electrical Contractor
jbfan's Avatar
Rewards Points: 552
Agreed! This info might have helped if it was stated in the opening post!
Old 12-19-2008, 06:53 PM   #20
Originally Posted by Bigbobdallas View Post
says it is hot
Loose connection at breaker?
How hot?
"Burned in 30 seconds by 54C, 5 sec. @ 60C, 1 second @ 71C."
No burn in 8 hrs. at 43C.
Less than 40C probably feels cool to the touch.
Anyone know the rise-above-ambient for a breaker carrying rated current? I doubt it is 24C.
Old 12-20-2008, 08:31 AM   #21
Rewards Points: 2,350
How hot?
Don't know right off hand. But I do know that any breaker carrying at or near its rated current will heat up significantly. Most breakers are 40 C, meaning they will maintain their thermal trip characteristics til that point, I think...
I have seen breakers in outdoor enclosures go way over their rated capacity because it was below freezing outside. There was a 20 A breaker with 32 A continuous, without tripping. I changed it for a new one, and almost the same thing. At any rate we had to reduce the load.
Old 12-20-2008, 08:56 AM   #22
I'll have to e-mail Square D or Cutler Hammer and ask, if they'll talk to me at all.
20 A squared = 400, 32 A squared ~1000, so this breaker had 2.5x the normal temp-rise-above-ambient for the thermal part, without tripping.
The NEC must know about this (?) and probably takes it into account. I guess they figure the wire is also colder, so the insulation is still below max temp.
Maybe the local codes for Alaska tweak these numbers a little.
Another way to figure this is max 30mV across closed, good contacts at rated current. At 30A this would be about 1w, and that won't heat something as large as a breaker.
For the thermal trip part they may have a 10w resistor in there. I'll have to take one apart sometime.
And so I did take one apart and found a mysterious component in it, which measured "zero" ohms on my meter.
10w at 20A is 25 mΩ, so I'll have to find some other way to measure this supposed resistor.
Rev A
Below 36C probably feels cool to the touch
no burn @42C
burned in:
30 seconds @ 54C,
5 sec. @ 60C,
1 second @ 71C.
With the aid of some rum & coke, the internal resistor of a Square D Q0 breaker comes in at 4.4 mΩ. 20A through this gives ~2w to heat up their bimetallic mechanism. 2w dissipated in a plastic case with a surface area as big as a breaker can't get very warm.
I don't know why the breaker you mentioned was hot at rated current, based on what I measured.
Old 12-20-2008, 09:17 AM   #23
DIYer
That was not what I was saying.
I just said the wire size determines the maximum breaker size. If you disagree with this then we have bigger problems.
Gigs is offline   Reply With Quote
Old 12-20-2008, 09:31 AM   #24
UAW SKILLED TRADES
Stubbie's Avatar
I certainly disagree if your saying this is always the case.
Old 12-20-2008, 10:45 AM   #25
Registered User
Termite's Avatar
Your methodology is 100% backwards and in conflict with basic electrical system design practices. Wire size is determined by the breaker ampacity. The ampacity of the specific circuit is determined for you by code or by the appliance manufacturer's requirements, and you pull the correct size of wire accordingly.
Old 12-20-2008, 11:09 AM   #26
DIYer
If you were pulling a new run then it might seem backward to say that the wire dictates the maximum breaker ampacity, but we are talking about an existing run in this thread.
It's just two different ways to say the same thing:
  • Breaker ampacity determines minimum wire size
  • (Smallest) wire size determines maximum breaker ampacity.
Old 12-20-2008, 11:28 AM   #27
UAW SKILLED TRADES
Stubbie's Avatar
I realize we are all bored here but wire size does not dictate breaker size in all cases. In this case we are serving a hot water tank...storage type.... so if the existing branch circuit breaker conductors are 12 awg copper then the maximum breaker is 20 amps. So I would agree that looking at an existing run of lets say 12/2 awg romax serving a hot water tank then 12 awg copper would dictate a maximum 20 amp circuit breaker.
What I am saying is that this is not always the case for maximum circuit breaker depending on what equipment or appliance the branch circuit serves exiting run or not. A 20 amp breaker on 12 awg copper romax is not necessarrily the maximum breaker size. I could put it on a 30 amp breaker.
Old 12-20-2008, 12:18 PM   #28
kbsparky's Avatar
... A 20 amp breaker on 12 awg copper romax is not necessarrily the maximum breaker size. I could put it on a 30 amp breaker....
In some cases, yes. Like with an A/C unit or other motor load.
In the case of a water heater (which is the topic of this thread), then no you are not allowed to use a 30 Amp breaker on a #12 wire.
For those who are lurking here, let's point out that a 4500 watts for a water heater circuit is considered to be a continuous load and as such has to be figured with a 125% multiplier. 18.75Amps x 125% = 23.43 Amps.
This translates to:
Minimum Circuit Ampacity = 25 Amps.
-- and --
Maximum overcurrent protection = 30 Amps.
Many new manufactured homes come equipped with a #10 wire connected to a 25 Amp breaker for a 4500 watt water heater.
Old 12-20-2008, 01:15 PM   #29
UAW SKILLED TRADES
Stubbie's Avatar
This translates to:
-- and --
Thanks for saving me the typing....that is exactly where I was going.
Old 12-21-2008, 06:54 PM   #30
Thanks All
Went and got me a new breaker and it is working great. Thanks for all the info. By the way it had a gas hot water heater and I ran a 220 from the main and put into a small breaker box and then put a 30 amp to the new Hot Water heater. But any how it is working OK now after two days.
Bigbobdallas is offline   Reply With Quote
Electric Water Heater GTSRider Plumbing 31 12-07-2008 11:30 AM
Installing a Tankless Water Heater infoiam Plumbing 4 11-10-2008 09:59 PM
Water Heater Troubles deadguydrew Plumbing 9 10-19-2008 09:30 AM
Water source from fridge from water heater? dankreboot Plumbing 11 07-12-2008 10:08 PM
"sticky" gas water heater thermostat homer12 Appliances 8 01-25-2008 04:36 PM