Old 06-06-2012, 03:57 AM   #1
Hot Tub Wiring Question
Hello everyone I have moved on to my next project and I have a few quick questions.
Just to put it out there right away I have a certified electrican helping me on this project to look over final hook up and verify I did everything right before turing on.
I am buying a hot tub that requires 240V/50Amps. I know I need the 4 wires in THHN or THWN run through my conduit that is 1". Okay all that is good.
What wire size do I need to run for each color? I am thinking the two Hot (blacks) need to be min #8 or possibly #6. But I am most unsure about the common and the ground sizes? Can they be smaller since they are not carrying the load?
Stranded Wire or Solid Wire??? I do have some 90 degree gradual curves where I am pulling wire.
Also does my double beaker at my main panel box need to be GFCI or just the one (50Amp) in the spa pack located on the outside of the house.
I wouldn't think they would both be GFCI but I want to check before I buy the product.
My run is going to be no more than 50' feet. Thank you all
ryan5068 is offline   Reply With Quote
Old 06-06-2012, 05:21 AM   #2
Licensed electrician
Two #6 blacks are good, a #6 white and a green. The instructions may call for a full size ground, otherwise a #10.
They need to be THWN if used outside. They will be stranded.
The GFI protection can be inside or outside.
Old 06-06-2012, 05:27 AM   #3
Electrician
Your pipe is a wet location so the wire rating has to have a w in it. #8 thwn copper for two hots and #10 thwn copper for green and white. The 8 will only come in stranded. You might as well get the 10 in stranded, too, but it doesn't matter electrically. Only one gfci per circuit, do not put them in series. If the main panel is less than 50' and in sight of the spa, you should not need a disconnect ( spa pack/breaker) closer to the spa. Local codes may vary. You would then run the pipe directly up into the spa with no splices or boxes. Your one gfci breaker would be in the main box.
Glennsparky is offline   Reply With Quote
Old 06-06-2012, 06:08 AM   #4
Electrician
Jim typed quicker than me. He's right that the instructions may call for a bigger ground wire. And the inspecter will probably require the white wire be no smaller than the green. But, the white never carries much power. Sometimes just the electronics are 120 volts. Maybe also a motor or two. If the white ever had more than a dozen noncontinuous amps on it, it'd blow my mind. The 50 amps you quoted is the minimum circuit ampacity. Which means your spa is designed to pull less than 40 amps and the spa company already multiplied by 125% for what you read in the manual or on the nameplate. Check to make sure. If that's true, #8 wire is plenty for less than 70 feet of wire one way.
Old 06-06-2012, 12:03 PM   #5
J. V.'s Avatar
Glenn. You cannot derate the neutral in this circuit. The neutral must be the same size as the two hots.
Old 06-06-2012, 12:10 PM   #6
Electrician
Hi J.V., please explain.
Old 06-06-2012, 05:18 PM   #7
E2 Electrician
stickboy1375's Avatar
Most of this was just mass confusion... do you really think the OP understood any of this?
stickboy1375 is online now   Reply With Quote
Old 06-06-2012, 05:21 PM   #8
E2 Electrician
I've wired a lot of hot tubs, and I'm betting on it requiring 4 #6awg conductors... The hot tub companies, are really hard up for a full size equipment ground.
Old 06-06-2012, 05:36 PM   #9
Semi-Pro Electro-Geek
There is no code provision which would allow the use of a reduced-sized neutral on this circuit - especially not one rated for less than the OCPD ampacity! The conductor ampacity and OCPD rating must jive, regardless of how light the load is.
I'm just curious now: is there ANY circumstance outside welders and motor/hvac loads where #10 wire could be used on a 50A breaker? I don't think so.
mpoulton is offline   Reply With Quote
Old 06-06-2012, 05:36 PM   #10
Code05's Avatar
Heck, I cannot really understand it and I twist wires for a living.
Code05 is offline   Reply With Quote
Old 06-06-2012, 05:40 PM   #11
E2 Electrician
Me too, it was a long trip to nowhere.
Old 06-06-2012, 05:52 PM   #12
E2 Electrician
210.19(a) (3) exception no. 1
The Following User Says Thank You to stickboy1375 For This Useful Post:
mpoulton (06-06-2012)
Old 06-06-2012, 08:35 PM   #13
J. V.'s Avatar
Here you go.
Derating the neutral is not allowed in this circumstance as mpoulton has explained above.
Derating neutrals are permitted in some applications. Not in this one.
Old 06-07-2012, 04:18 PM   #14
Electrician
The run between the main panel box and what Ryan calls the spa pack is a feeder. Read 215.2(A)(1) Exception No. 2 and 215.2(A)(2).
Old 06-07-2012, 05:03 PM   #15
E2 Electrician
Yes, but 99% of Hot tub manufactures still spec out the minimum size conductors you can use...
Question about AFCI and Ontario code as well as some other general wiring queries drunken0monkey Electrical 5 06-15-2010 10:49 AM
Yet another subpanel wiring question Chris_M Electrical 6 06-10-2010 06:12 PM
mini split Wiring question??? mjebril HVAC 5 08-02-2009 07:31 PM
Attic wiring question everyman Electrical 4 07-07-2009 10:47 AM
Trane Heat Pump tstat replacement with Honeywell prog - wiring question sep23 HVAC 2 10-20-2006 10:10 PM