Ok, so I'm trying to get ready for my new hot tub to arrive. The model specs says that its a 50 amp but where I bought it from recommended running a 60 amp setup.
As of now, I'm looking at doing a 60 amp double pole breaker at the service panel and 6/3 THHN (not Romex) in the inside to the 60 AMP GFCI panel on mounted on the outside of the wall.
Now at the GFCI panel I'll obviously have the grounds and neutrals separated.
For the questions.
Can I just run 6/3 THHN from the GFCI panel through conduit and avoid the need for a insulated ground wire or will I still need a THHN with the insulated ground?
I also have a ~100' run from the service panel to the hot tub. Is the drop going to be significant enough to trip the GFCI? Should I look at 4/3 instead?
70' - From the service panel to the GFCI panel
25' - From service panel to hot tub
TIA!
doublejz is offline   Reply With Quote
Old 06-13-2012, 10:36 PM   #2
Code05's Avatar
Rewards Points: 1,104
What is 6/3 THHN?
Code05 is offline   Reply With Quote
Old 06-13-2012, 10:46 PM   #3
DIY Expert
Rewards Points: 73
http://www.lowes.com/pd_377313-226-1...hhn&facetInfo=
Old 06-13-2012, 11:16 PM   #4
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
That IS romex. You can use that to the gfi panel, but you cannot use that to the tub.
Old 06-13-2012, 11:32 PM   #5
DIY Expert
Rewards Points: 73
Oh so what wire do i need from the gfi panel to the tub? I guess I should stay away from romex all together as its only rated to like 55 amps I think. Also, aslong as its rated THHN and in conduit I'm good right. I'd only need THWN if it was out of conduit and buried, right?
I'm still worried about the overall length of the run, trying to figure out how to shorten the run.
Old 06-13-2012, 11:38 PM   #6
k_buz's Avatar
You are going to need to run a conduit from the GFI panel to the tub. That is the only way I know of to get an insulated ground to the tub. Inside the conduit, you will need to run individual conductors. Most THHN that you buy is dual rated THHN/THWN. The "W" is the important part. You need that "W" to be able to run those conductors underground in pipe.
If the tub's specs call for a 50A circuit, that that is what you must run. You don't have the option of putting the tub on a 60A breaker.
Old 06-13-2012, 11:45 PM   #7
DIY Expert
Rewards Points: 73
Ok thanks. Do you think that 100' is too long for #6 wire?
Old 06-13-2012, 11:48 PM   #8
k_buz's Avatar
I don't
Old 06-14-2012, 05:28 AM   #9
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,034
K Buz,
The picture & link he shows is THHN. (Unless he has changed it after you posted)
OP,
You need THWN wire(wet rated) and according to the Cerro web side the wire you show is dual rated THHN/THWN. You need 4 runs of the wire, 2 hots, a neutral and an insulated ground. You need red or black for the hots, white for the neutral and green for the ground.
Coastal South Carolina
Old 06-14-2012, 06:42 AM   #10
Rewards Points: 720
If it's going to be #6, then it can't all be black. You will need white #6 for the neutral and green #10 for the ground. They can't be taped to change the color at that size.
Mark
busman is offline   Reply With Quote
Old 06-14-2012, 06:51 AM   #11
k_buz's Avatar
My apologies. That looks like a coil of 6-3 and the OP was stating he was using 6-3. The packaging also confused me. I see THHN on coils/spools, not in "bags".
Old 06-14-2012, 06:53 AM   #12
k_buz's Avatar
If you are piping the inside of your house from the panel to the GFI panel, you can use #8's for a 50A circuit provided the tub's specs don't specifically require #6's.
Old 06-14-2012, 06:58 AM   #13
A "Handy Husband"
rjniles's Avatar
Mark
The manufacturer or the AHJ may require the ground to be the same sjze as the other conductors.
Old 06-14-2012, 08:12 AM   #14
Rewards Points: 720
I'm just working to the NEC. I've never seen a Hot Tub with instructions that require larger sized EGC.
Mark
Old 06-14-2012, 10:21 AM   #15
DIY Expert
Rewards Points: 73
I was trying to avoid piping it inside the house if possible. Also, backing up to where I stated that where I bought the tub told me to run 60 amp instead of 50. I got the installation guide for the tub and it appears there is 3 configurations that can be used. I'm curious what they mean about minor circuit board modification will nee to be made though, sounds like more $$ for the electrician when it gets inspected.
Attic wiring - ceiling lighting uses 14/2 cable without ground darlingm Electrical 3 11-29-2011 10:01 AM
Backyard wiring questions MikeInDetroit Electrical 1 11-02-2011 10:46 AM
Cloth Wiring - Replace? JessicaGus Electrical 9 09-23-2009 07:45 PM
Replacing wiring in middle of run, ungrounded lighting circuit alexz Electrical 3 07-05-2007 09:53 PM
Knob & Tube wiring - How concerned should we be? hotdiggitydog Electrical 6 04-11-2006 08:52 PM