Hot Tub Disconnect Panel - Electrical - DIY Chatroom Home Improvement Forum
Old 04-04-2012, 06:02 PM   #1
Hot Tub disconnect panel
Hi,
I am ready to wire my new hot tub. The salesman told me I did not need to purchase a dissconnect panel. The reason was the house main panel was in line of sight to the hot tub and only 12 feet from Hot tub foundation. Thus, the the house panel itself is considered the dissconnect panel. Of course, it would be connected to a 50 amp GFCI breaker. Does this sound correct?
bigedy is offline   Reply With Quote
Old 04-04-2012, 06:51 PM   #2
Rewards Points: 204
Please get someone who knows how to safely install your tub. The salesman is not an electrician and it looks as if his information is not correct.
Or you need to get a close look at article 680 of the NEC.
680.12 Maintenance Disconnecting Means. One or more
means to simultaneously disconnect all ungrounded conductors
shall be provided for all utilization equipment other
than lighting. Each means shall be readily accessible and
within sight from its equipment and shall be located at least
1.5 m (5 ft) horizontally from the inside walls of a pool,
spa, or hot tub unless separated from the open water by a
permanently installed barrier that provides a 1.5 m (5 ft)
reach path or greater. This horizontal distance is to be measured
from the waterís edge along the shortest path required
to reach the disconnect.
Here is what you need. It is a self contained disconnect and required convenience receptacle. About $100.00.
Old 04-04-2012, 06:57 PM   #3
Thanks... I will get an electrician and disconnect box.
Old 04-04-2012, 07:12 PM   #4
Master Electrician
Rewards Points: 3,918
That disconnect does not contain a receptacle. That is a dead front GFCI which trips the relay power to the hot tub upon a fault.
brric is offline   Reply With Quote
The Following User Says Thank You to brric For This Useful Post:
J. V. (04-05-2012)
Old 04-04-2012, 07:28 PM   #5
Thanks for input. This will be dedicated to the hot tub. My contracter will run conduit from disconnect to hot tub. He plans on buring it 18 inched. I thought the disconnect was needed and now it is confirmed. I will let them do all the wiring... I just want to be informed. I was very concerned about the salesman telling me I did not need a disconnect panel. It did not sound correct. What else was he wrong about
Old 04-04-2012, 07:52 PM   #6
A "Handy Husband"
rjniles's Avatar
Rewards Points: 4,226
You hired a contractor between 7:02 PM and 8:28 PM? WOW!
Coastal South Carolina
rjniles is offline   Reply With Quote
Old 04-04-2012, 08:03 PM   #7
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
actually 7:57 and 8:28
Old 04-04-2012, 08:03 PM   #8
Well I have three bids on the table to redo my back yard....including hot tub and all said they have licenced electricians to do work. Now when we talk about the detailed electrical, thanks to all, I am informed. I will ask them about the Connecter Box.. if they tell me what the salesman did... they will not get the job.
Old 04-05-2012, 09:46 AM   #9
Rewards Points: 204
Thanks for the help. I saw the test/reset buttons and assumed. The receptacle is required, so I will remember to not use that picture again.
Old 04-06-2012, 02:56 AM   #10
Electrical Contractor
kbsparky's Avatar
IF that house panel is indeed only 12 feet away, you may not need another $100 disconnect box. The salesman may in fact, be correct.
Is the panel box outside, or is the tub outside, and the panel inside? Just a couple of clarifications here.
As for the receptacle integral with the disconnect box, that is an item of convenience. You can have a nearby receptacle qualify as the required receptacle, provided distance and GFCI protection are within guidelines.
-KB
Alabama Sub Panel KHman Electrical 14 04-10-2012 10:35 AM
Old House Rewire finnimus Electrical 15 05-13-2011 10:39 PM
100A Fuse Panel Replacement Charlie1101 Electrical 4 07-25-2009 02:22 PM
Subpanel installation in outbuilding fls Electrical 19 03-16-2008 02:19 PM
breaker panel question chadvavra Electrical 11 08-10-2007 09:20 AM