Old 06-06-2012, 09:31 PM   #1
DBW
hot/ground reversed
I have an outlet that shows "correct" on a 3 prong tester, but goes to "hot/grd reverse" as soon as I plug anything in. Other lamps on the same circuit are working. I replaced the breaker and checked for loose wires in the box, but no change. Do I have to start rewiring?
DBW is offline   Reply With Quote
Old 06-06-2012, 09:40 PM   #2
Is thr ground attached to the box as well as the outlet? Are the side "posts" brass and silver screws ,screwed down to the outlet?
IntexInspector is offline   Reply With Quote
Old 06-06-2012, 09:46 PM   #3
DBW
Ground to box....no. The outlet is new, brass(hot) and silver(neut) screws are tight. (wires attached via push-in)
Old 06-06-2012, 09:46 PM   #4
Licensed Electrical Cont.
Speedy Petey's Avatar
Rewards Points: 1,822
This is a classic open or compromised neutral somewhere on the circuit. Logic tells us it is after or at the last working receptacle. Finding that receptacle is the trick.
Are the wires stuck in the back holes of the receptacles? This is a well known failure point.
Speedy Petey is online now   Reply With Quote
Old 06-06-2012, 09:53 PM   #5
DBW
Thanks Speedy, I'll start checking all outlets on this circuit. yes, outlets are all push-in from '85. Compromised neutral means loose or touching a hot? Also, does it matter that my breaker box uses the same grounding bar for neutrals?
Old 06-06-2012, 10:36 PM   #6
Yup, that itself is a dead giveaway.
No, as in loose or not making contact, as in open.
Nope, perfectly normal.
Old 06-06-2012, 10:41 PM   #7
DBW
Great info, thanks again! I'll follow-up when I find the solution.
Old 06-06-2012, 10:59 PM   #8
joed's Avatar
Rewards Points: 11,556
It hasn't been said so I will say it, move the wires to the screws. If there are no screws then replace the receptacles with ones that have screws.
Old 06-07-2012, 06:56 AM   #9
Licensed Electrician
k_buz's Avatar
Rewards Points: 2,006
Make sure you unplug all the electrionics on this circuit and they tend to let some smoke out in these situation. (Although I suppose its probably too late at this point)
Old 06-07-2012, 03:12 PM   #10
DBW
Yes, I did. Three light fixtures were wired on this circuit so I disconnected them. When wired to another line, all were ok.
Old 08-18-2012, 05:01 PM   #11
DBW
hot/ground reversed follow-up
Finally a follow-up. Speedy Petey said it at the beginning of this thread....
a compromised neutral. One note on the 3 prong tester, it fooled me at first.
It showed correct on the tester until I flipped on a ceiling light that was
hardwired on this circuit.
Many thanks for everyone's input.
hot/ground reversed-bad_outlet.jpg
Old 08-18-2012, 05:52 PM   #12
k_buz's Avatar
Feels good when you find the problem doesn't it?
Old 08-18-2012, 06:32 PM   #13
DBW
Yes it does!
Old 08-18-2012, 08:54 PM   #14
Electrical Contractor
kbsparky's Avatar
Hope you didn't back-stab the replacement receptacle!
-KB
Old 08-18-2012, 09:04 PM   #15
E2 Electrician
stickboy1375's Avatar
Rewards Points: 2,970
Eh, i feel differently about this, but whatever...
Light Switch Reversed.. Up is Off.. down is on caseynshan Electrical 11 07-12-2014 07:10 PM
Can't Find Reversed Polarity On A Circuit SirMissedALot Electrical 16 09-08-2011 06:50 PM
GFCI tester shows hot/ground reversed, then not reversed bw777 Electrical 7 02-04-2011 10:16 AM
hot / neu wiring reversed, getting a shock PIGEONS Electrical 2 11-07-2010 06:43 PM
pos/neu reversed help please mtstreicher Electrical 11 12-10-2009 02:17 PM