Hide/Cover Sconce Light Fixture hole
Want to remove electrical sconces on bedroom walls. Would prefer not to cover the holes or hide with pictures. Can these holes be patched? Can wires be removed? Is this a fire hazard?
In order to patch up the holes you will have to remove the boxes. If you remove the boxes, you have to pull back the wires to the next box or install a box in which to terminate the wires.
It's not a fire hazard to have unconnected wires as long as they have wire nuts on them. |
Welcome to the Forum.
Tell us about your bedroom sconces. Are they wired with Romex type wire? If you don't know how to tell the difference then you may be safer by calling an Electrician? |
you can get decorative blanks to fit the boxes as well, or get whites and paint them to match the room.
or buy nicer sconces and just install them instead. :)
If these sconces are wired in the "switch leg" fashion (power goes to switch first, then a switch leg is run to the sconces) all you need to do is disconnect the wire in the switch box. Then you can patch the holes, burying the box is fine.
Some will say that even if the lights were wired in the "switch loop" fashion (power goes to the light box first, then a switch loop runs over to the switch) you can just cap the wires off and then bury the box because there is no connection inside of the box. |
Energized ends of a cable cannot be buried in the wall.
Edited: There is a lot of discussion on this topic, it goes both ways. Here is an example: http://www.electriciantalk.com/f2/hack-12483/ The main reason why you can't bury a junction box isn't a safety issue, it's in case the splices ever came loose, it's easier to troubleshoot when you can actually find the box. When abandoning wires and capping them off, there is nothing to come loose. I don't think the thread starter should have this issue anyway since I am guessing the sconces are fed with a switch leg and he could just disconnect the wires inside of the switch box and abandon them properly. |
If it is still energized I would think this would apply.
314.29 Boxes, Conduit Bodies, and Handhole Enclosures to Be Accessible. Boxes, conduit bodies, and handhole enclosures shall be installed so that the wiring contained in them can be rendered accessible without removing any part of the building or, in underground circuits, without excavating sidewalks, paving, earth, or other substance that is to be used to establish the finished grade. |
If the conductors have been de-energized and removed from the box I would agree that it could be abandoned and covered over. |
This most applicable article is 300.15 IMO. Depends how you read it. I agree with you, but many will not. |
This topic is completely up in the air, different people see it in different ways.
One can say that if you pull a cable out of a box and tape it off, it's legal to bury it in the wall live. 300.15 wouldn't cover this since the wire isn't being spliced, terminated, etc. I linked to one thread where they were discussing that and there are many others. |
Here is 300.15 which I also agree would apply. Blue by me for emphasis.
300.15 Boxes, Conduit Bodies, or Fittings —Where Required. A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring. Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed. Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables,[COLOR="rgb(65, 105, 225)"] a box or conduit body shall be installed at each conductor [/COLOR]splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (L). |
| All times are GMT -4. The time now is 04:57 PM. |